Please clarify for me if 1/0 copper is suitable for a 200 amp breaker.  
My understanding is 150, max 175 for SEC.

Thanks, seems undersized, looks to me like a 150 amp breaker should be installed.

![267714 079 (Small).JPG](https://global.discourse-cdn.com/internachi/original/3X/c/6/c6c24a2f5590d6bd55a2655687c2de362d119141.jpeg)

![267714 079 (Small).JPG](https://global.discourse-cdn.com/internachi/original/3X/c/6/c6c24a2f5590d6bd55a2655687c2de362d119141.jpeg)

![267714 080 (Small).JPG](https://global.discourse-cdn.com/internachi/original/3X/1/1/11d7b0bfdc9385a8cf7d11c7c8574ccaa290dacd.jpeg)

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [April 10, 2014, 4:36pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/2 "2014-04-10T16:36:40Z")

</div>

> [@dmacy](#):
>
> Please clarify for me if 1/0 copper is suitable for a 200 amp breaker.  
> My understanding is 150, max 175 for SEC.
> 
> Thanks, seems undersized, looks to me like a 150 amp breaker should be installed.

You’re correct. The max for 1/0 is 150 amp.

200 amp requires 3/0 (copper).

---

<div class="post-metadata">

**Author:** ![dmacy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dmacy/32/1466_2.png) [@dmacy](https://forum.nachi.org/u/dmacy)\
**Post date:** [April 10, 2014, 4:43pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/3 "2014-04-10T16:43:44Z")

</div>

> [@ccurrins](#):
>
> You’re correct. The max for 1/0 is 150 amp.
> 
> 200 amp requires 3/0 (copper).

Thanks, I wanted to make sure and I appreciate the feedback.

---

<div class="post-metadata">

**Author:** ![jwicklander](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jwicklander/32/57038_2.png) [@jwicklander](https://forum.nachi.org/u/jwicklander)\
**Post date:** [April 10, 2014, 4:54pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/4 "2014-04-10T16:54:07Z")

</div>

Technically the NEC states 2/0 copper is required. However, your local may require 3/0 copper.

Jeff

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [April 10, 2014, 4:55pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/5 "2014-04-10T16:55:15Z")

</div>

David according to NEC 2008. No! also according InterNachi training. No!  
Looks like we all got to you at the same time.😉

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [April 10, 2014, 5:12pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/6 "2014-04-10T17:12:09Z")

</div>

> [@jwicklander](#):
>
> Technically the NEC states 2/0 copper is required. However, your local may require 3/0 copper.
> 
> Jeff

That’s correct. With NEC 2/0 co is minimum. Some of my locals have been requiring 3/0. Either way what David has is undersized. 🙂

---

<div class="post-metadata">

**Author:** ![Martin\_Brooke](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@Martin\_Brooke](https://forum.nachi.org/u/Martin_Brooke)\
**Post date:** [April 10, 2014, 8:11pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/7 "2014-04-10T20:11:13Z")

</div>

1/0 copper is not suitable for a 200 amp main. NEC table 310.15 B 7 lets you use it for 175 amps not 200. A 200 amp service would need 2/0 copper or 4/0 aluminum.

Hope this helps:

Table 310.15(B)(7) Conductor Types and Sizes for  
120/240-Volt, 3-Wire, Single-Phase Dwelling Services and  
Feeders. Conductor Types RHH, RHW, RHW-2, THHN,  
THHW, THW, THW-2, THWN, THWN-2, XHHW,  
XHHW-2, SE, USE, USE-2  
Conductor (AWG or kcmil)  
Service or Feeder  
Rating (Amperes) Copper  
Aluminum or  
Copper-Clad  
Aluminum

(Amps are first, the copper wire size then aluminum)

100 4 2  
110 3 1  
125 2 1/0  
150 1 2/0  
175 1/0 3/0  
200 2/0 4/0  
225 3/0 250  
250 4/0 300  
300 250 350  
350 350 500  
400 400 600

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [April 10, 2014, 8:16pm UTC](https://forum.nachi.org/t/1-0-copper-sec/86000/8 "2014-04-10T20:16:25Z")

</div>

According to NEC Table 310.15(B)(7) #1/0 copper is good for 175 amps. Your close up photo is of the neutral are the ungrounded conductors also #1/0? The neutral is permitted to be smaller.