120 volt termination

Hi everyone - Can someone help me clarify what this means:

Never install a switch receptacle fully inside of a room where both the top and bottom of the duplex is controlled by a switch.

1 Like

switched-split-receptacle-wiring-diagram
The diagram answers your question.
Welcome to the forum Alice. have fun and enjoy.

3 Likes

I believe it means to not use one switch to control both the top terminal and the bottom terminal of a single receptacle separately.

Or, you can ask Ben at Ben@InterNACHI.org.

3 Likes

The issue with switching the entire receptacle is that it no longer counts towards the 6’/12’ receptacle wall spacing rule so an additional receptacle may be required adjacent to the switched receptacle. It’s just easier to switch only half of the device.

6 Likes

That makes sense, the house I inspected today had both top & bottom switched, but it was built in 1981, evidently before the rule was put in place.

Thanks, Rob!

That’s correct, this was a code change to the 2008 edition of the NEC. {210.52(2)}

I thought this code changed in the '90s. Thanks for the info.