1802 Q8 (sealed roof deck): what counts on the new form, and what to do when you can't see it

Q8 caused the most arguing in the earlier threads, so here is the new form’s own language in one place.

Option A (Sealed Roof Deck / SWR) lists these:

  • Fully adhered polymer-modified bitumen underlayment, ASTM D1970.
  • Tape over the roof deck seams: a self-adhering strip at least 3.75 in. wide (ASTM D1970), or AAMA 711 Level 3 flexible flashing tape.
  • A double layer of felt or synthetic with no tape: two layers of ASTM D226 Type II, D4869 Type III or IV, or D8257.
  • Spray foam along the rafter/deck intersections and all panel joints.
  • A separate box: “check here if entire roof deck underside covered.”

What doesn’t count: the form says standard underlayment or hot-mopped felts do not qualify.

If you can’t verify which one it is: B means no sealed roof deck. C, “Unknown or undetermined,” is a real answer on the form. Whichever you pick, write down what you relied on, such as photos, the permit, or an invoice.

Question for the group: how are you verifying double-layer or taped seams on a finished roof? Attic photos, permits, asking the homeowner for the roofer’s invoice? I’m curious what is actually holding up with the insurers.