2 circuits to one receptacle?
Not true
How about if both are on the same phase .
Regardless it is wrong .
An electrician would have no trouble figuring out this instantly.
Hmmm, I stand corrected. I guess that wouldn’t trip the circuit/s would it?
There’s still the problem that it tripped when Mike connected them up to the receptacle which may indicate they are on opposite phase. Keep us updated, this is an interesting one, glad you didn’t get bit badly.
I see two circuits to one outlet now and then in my area. Usually on a switch controlled outlet so if the power trips on one, the light plugged into the other will still work. Tabs on the outlets are usually cut. As for not tripping , like stated above if they are the same phase it will not trip as there is no difference in potential. We’ll Chalk this one up to a DYIer getting lucky and forgetting to cut the tabs and it just happened to be two circuits, same phase…
I am fairly confident that you got zapped by the return current on the neutral. That outlet is sharing the neutral with that other circuit that you found later (a multi-wire branch circuit, MWBC, that another poster referred to). Please do a google search on how MWBCs work. It’s confusing at first, but you’ll figure it out. These circuits were originally wired wrong in this instance. The two breakers feeding this circuit should have been connected by a breaker tie, that way when you kill power to one, you kill power to both, and the neutral current won’t zap you.
that’s kind of where I was heading. The main breaker never tripped, but the GFCI tripped.
That makes sense.
My good friend and former employee is a Master Electrician. He’s stumped as well. Either I didn’t explain it right, or I am mistaken about the broken tab.
Both breakers are on the same phase
If the hots did not feed through to other devices or if only one did, abandoned one in the box and install the GFCI.
If they go to feed other devices you could bypass the outlet for that circuit.
That’s how I see it. Connect the non-switch controlled hot to GFI and switch controlled to the correct outlet (light, heater, fan). Or cap and abandoned hot that is not needed.
Thanx guys. Slap myself on the forehead. That 's too easy.
Tomorrow I shall call and give my electrician buddy a lesson.
I am curious…
Why are you doing electrical work?
You are not qualified.
You are not licensed.
You do not have the proper experience.
You have no insurance or bond for such work.
It is illegal.
You are putting yourself, your client and the rest of the community at risk for safety and legal issues. Not to mention it is a conflict of interest for you to do so. It also invalidates your company slogan that is at the bottom of your posts.
You are mistaken
Actually, finding the answer and completing the work validates the slogan, thanks for the HELPFUL brothers here
Actually, it is for you:
§29-3B-8. Effect of noncompliance with article; failure to obtain license.
Any person, firm, corporation or employee thereof, or any representative, member or officer of such firm or corporation, individually, entering upon or engaging in the business of performing any electrical work as defined in this article, without obtaining the required license or otherwise complying with this article, is for the first offense guilty of a misdemeanor, and, upon conviction thereof, shall be fined not less than one hundred dollars, nor more than five hundred dollars. For a second and each subsequent offense, the penalty and punishment is a fine of not less than five hundred dollars nor more than one thousand dollars. Each day during which such electrical work is performed without the required license or while in noncompliance with any of the provisions of this article, after official notice that such work is unlawful, is a separate offense.
Be careful with your insurance: it won’t pay off if you are doing work you are not licensed for.
You are mistaken. Again. Read the entire article. Here’s the link.
http://www.legis.state.wv.us/wvcode/ChapterEntire.cfm?chap=29&art=3B
The law states that an electrical license is not required for:
  1. A person working on their own property.
  2. Doing maintenance work as an employee.
  3. Appliance installer.
  4. Electrical work performed on public facilities while employed by the public utility.
  5. Government workers doing electrical work on government property.
Please help me understand how you can perform electrical work while not exempt from any of the above.
May I ask who you are? Do just troll message boards and harass members? Living on the opposite side of the country from Mike I really don’t see your point.
My sentiments exactly, Chris. Thanks.
And just in case it would happen to be Mr. Hansen’s business, or really a concern, in order to fall into these categories you have to charge for this service. Performing work for a relative, or neighbor, or just to be kind, as long as you don’t charge for it, is okay.
If you’re out of the city limits you won’t need a permit.
That being said, I can still do electrical work, and have a Master Electrician sign off on it, and everything would be legal.
Maybe Mr Hansen wants to do electrical work in WV, and since I am putting the structure, the entire community, and my insurance in danger by installing a GFCI outlet, he’s worried there will be nothing left here after the entire state burns to a crisp because I got the hot and neutral crossed in dim light, or because I was not qualified to connect black to black and white to white.
Each his own.
Now you are changing your story. You stated you did jobs for sellers getting their homes ready to sell. You do those for free?
A master electrician cannot sign off on any work. An electrical inspector is the only one who has the authorization to sign off permits. Being a home inspector you should know this.
Mike, I originally asked why you did this work without being licensed. I didn’t ask you to justify it, because you can’t. The law in WV is clear. You just choose not to follow it.
BTW, the code of ethics of this organization is an interesting read… it covers a lot of what we have been talking about.