New 200 amp panel and the 200 amp breaker is not being used. The 100 amp breaker to the lower right is now the main breaker. First time I have ever seen this. How do I write this up?

1 Like

There’s nothing to write if the 100A breaker is properly installed. It needs to be secured in place. Identify the service as being 100A.

4 Likes

I agree with George, and I’ll add, if the 100 amp breaker is back-fed it needs to be secured (screwed) in place.

I found this one yesterday that wasn’t.

5 Likes

Image please.

1 Like

You write it up as a 100 amp service. There is nothing remarkable about using a 200 amp panel at less than its rating.

2 Likes