200 amp panel feeding 110 amp

I think what Simon is getting at is your use (or in this case misuse) of the word “service”. The garage panel is not the service, the 200 amp panel on the exterior of the structure where is service disconnect is located is the service. This is an area where a slight misuse of a word in a report can dramatically change what is actually installed in the house.

1 Like

Well said Robert.

Yep. There’s only one piece of service equipment at that house and it’s configured for 200 amps. The distribution panel on the interior is configured for 110 amps.

2 Likes

Robert Meierrmeier2Non-Member Guest

3

escanlan

1d

(post withdrawn by author, will be automatically deleted in 120 hours unless flagged)

rmeier2 Robert Meier

Non-Member Guest
December 3

Just curious as to why would someone would need mention anything other than the garage panel is 110 amps? Would you note every sub-panel in that way? For example what it the garage panel were 60 amps would you note it saying it’s less than the minimum required for a single family dwelling?

The way I see it is that this is a 200 amp service with a 110 amp garage sub-panel, there is not much more to report than that.

Visit Topic or reply to this email to respond.

In Reply To

\ 45x45 escanlan Emmanuel Scanlan, TREC# 7593 InterNACHI®️ CPI
December 3

As the OP wrote, and Larry explained, it appears to be a 200 Amp “service”. However the maximum current draw available with this configuration would only be the size of the exterior OCPD. “Technically” there is nothing wrong with the configuration as we see it and explained to us with the only is…

You will have to better phrase your question for it to be understood. Before you do carefully read my responses and you might then understand the answers.

Service is 200A

Subpanel: is protected at 110A

Thats what i would report.

The more you try to explain equals more opportunity to be wrong or misleading. Unless of course you are an electrician, and a good one at that.

How hard can it be :smiley: