# 200amp main breaker; wiring not updated

**URL:** <https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943>\
**Category:** Misc. Discussion\
**Created:** [July 24, 2024, 10:38pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943 "2024-07-24T22:38:29Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 24, 2024, 10:38pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/1 "2024-07-24T22:38:29Z")

</div>

Hello all,  
Recently had an inspection done on a flipped, 70 year old house in N FL. There was a 200amp main breaker in the box but the original wiring was for 100amps. My handyman noticed this, the plumber giving me a quote for a tankless water heater noticed this, the home inspector did not.

What do you guys think? Is this something that a home inspector should notice or does it fall outside what is expected?

To be clear, we’ve already purchased the home and corrected the electrical issue. I’m just curious what kind of expectations I should have with home inspectors going forward

Thanks in advance!

---

<div class="post-metadata">

**Author:** ![tglaze](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tglaze/32/362210_2.png) [@tglaze](https://forum.nachi.org/u/tglaze)\
**Post date:** [July 24, 2024, 10:50pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/2 "2024-07-24T22:50:07Z")

</div>

> [@adauner](#):
>
> My handyman noticed this, the plumber giving me a quote for a tankless water heater noticed this, the home inspector did not.

“Handyman” ? Please 🙄 Did the HI know or state anything about the system not being able to support additional systems? Most likely NO…

You’re reaching for faults.

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [July 24, 2024, 10:56pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/3 "2024-07-24T22:56:55Z")

</div>

> [@adauner](#):
>
> There was a 200amp main breaker in the box but the original wiring was for 100amps…

Do you mean the service entrance conductors were only rated for 100 amps? Or, can you be more specific when you say the “wiring was for 100 amps?” That statement on its own doesn’t really tell us much unfortunately.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [July 24, 2024, 11:17pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/4 "2024-07-24T23:17:24Z")

</div>

> [@adauner](#):
>
> and corrected the electrical issue.

Who made the corrections? You/DIY? Handyman? Licensed Electrician?  
What exactly did the “corrections” consist of?  
Be specific.

---

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 25, 2024, 12:49am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/5 "2024-07-25T00:49:26Z")

</div>

The electrician I hired said this  
“The existing service wires are undersized probably rated for only 100amp total. I’ll provide new exterior overhead service with new mast, and new grounding.  
Install new meter main on exterior of home, install new 200amp service cable from meter main, to interior panel.”

Think that should give you a good idea of what work was needed

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [July 25, 2024, 12:56am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/6 "2024-07-25T00:56:59Z")

</div>

> [@adauner](#):
>
> Think that should give you a good idea of what work was needed

Can you post some photos of the existing system?

---

<div class="post-metadata">

**Author:** ![jmilby](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmilby/32/57038_2.png) [@jmilby](https://forum.nachi.org/u/jmilby)\
**Post date:** [July 25, 2024, 2:07am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/7 "2024-07-25T02:07:00Z")

</div>

Sounds like an old 100 amp panel was replaced with a 200 and the old service conductors were left in place.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [July 25, 2024, 2:36am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/8 "2024-07-25T02:36:32Z")

</div>

> [@adauner](#):
>
> … **probably rated** for only 100amp

> [@jmilby](#):
>
> an old 100 amp panel was replaced with a 200 and the old service conductors were left in place.

Common practice in my area on older homes. PoCo says it’s okey-dokey as long as condition is good, (not deteriorated or damaged).  
(And yes, there are always exceptions).

Note: The Minnesota “Minimum Standard” for panels is 100 AMP Rated. Most every Meter is 200 AMP Rated. Service Drop are all over the place, but PoCo claims all are good Minimum 200 AMPS.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [July 25, 2024, 3:12am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/9 "2024-07-25T03:12:05Z")

</div>

> [@rmeier2](#):
>
> Can you post some photos of the existing system? .

I’d like to see what information the Inspection Report contains. Can’t really offer the OP an opinion without all the FACTS.

---

<div class="post-metadata">

**Author:** ![rbleich](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rbleich/32/423577_2.png) [@rbleich](https://forum.nachi.org/u/rbleich)\
**Post date:** [July 25, 2024, 3:22am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/10 "2024-07-25T03:22:34Z")

</div>

> [@adauner](#):
>
> There was a 200amp main breaker in the box but the original wiring was for 100amps…Is this something that a home inspector should notice or does it fall outside what is expected?

It sounds like you have a 100 amp service. The home inspector should have identified it as such as required by Florida standards. If they identified it as a 200amp service, you may have a claim against them.

> [@adauner](#):
>
> The electrician I hired said…_” **probably** rated for only 100amp”_

Your electrician doesn’t sound very sure of himself. The conductors are either rated for 100 amps or they’re not.

> [@adauner](#):
>
> I’m just curious what kind of expectations I should have with home inspectors going forward

[61-30.doc](https://forum.nachi.org/uploads/short-url/uN9n5DudgVcqmYniWAU2PcEmka1.doc) (170.5 KB)

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [July 25, 2024, 5:18am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/11 "2024-07-25T05:18:36Z")

</div>

> [@adauner](#):
>
> The electrician I hired said…_” **probably** rated for only 100amp”_

The electrician needs to identify the wire type and gauge: it’s printed on the wire. The power company makes the determination on the wires from the pole to the point of entry.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [July 25, 2024, 10:24am UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/12 "2024-07-25T10:24:06Z")

</div>

Photo please.

---

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 25, 2024, 1:14pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/13 "2024-07-25T13:14:52Z")

</div>

![Screenshot_25-7-2024_91418_app.spectora.com](https://global.discourse-cdn.com/internachi/original/4X/2/e/c/2ecde3fa65b63c7602dcab92312254a7865ed73b.jpeg)

From the inspection report

---

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 25, 2024, 1:15pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/14 "2024-07-25T13:15:44Z")

</div>

![Screenshot_25-7-2024_91526_app.spectora.com](https://global.discourse-cdn.com/internachi/original/4X/2/4/a/24ac27184e0e925163c4c4efcf42822a23e21cf9.jpeg)

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [July 25, 2024, 1:31pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/15 "2024-07-25T13:31:02Z")

</div>

That panel is a mess. What else did the inspector say about the condition of the panel?

---

<div class="post-metadata">

**Author:** ![megbert2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/megbert2/32/424064_2.png) [@megbert2](https://forum.nachi.org/u/megbert2)\
**Post date:** [July 25, 2024, 1:34pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/16 "2024-07-25T13:34:47Z")

</div>

Ditto Roberts question, that is a terrible looking “panel replacement” by the flippers. Also, did your electrician actually say “probably rated for 100amps”? That is a very ambiguous description from an electrician and could be a bit of a red flag about their skill.

---

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 25, 2024, 1:34pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/17 "2024-07-25T13:34:47Z")

</div>

![Screenshot_25-7-2024_9342_app.spectora.com](https://global.discourse-cdn.com/internachi/original/4X/b/d/5/bd53135c8aa8f356b0e1facb1cac279be5041228.jpeg)

Thats everything on the panel

---

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 25, 2024, 1:39pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/18 "2024-07-25T13:39:18Z")

</div>

> [@megbert2](#):
>
> Also, did your electrician actually say “probably rated for 100amps”? That is a very ambiguous description from an electrician and could be a bit of a red flag about their skill.

It was thru text; it might have just been easier to write that than to explain it. Either way we ended up using a different electrician because of pricing

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [July 25, 2024, 1:45pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/19 "2024-07-25T13:45:44Z")

</div>

I would take issue with the note saying that “this is generally an easy and inexpensive repair” regarding the lack of cable connectors. The entire panel or all of the cables would need to be removed, the proper NM cable connectors installed and then it would need to be rewired. That is by no means inexpensive. Also the panel is missing the MBJ (main bonding jumper) typically a green bonding screw. The service entrance cable does appear to be 100 amps but unless there is an overcurrent protection device on the outside of the house the 200 amp circuit breaker is the wrong size.

---

<div class="post-metadata">

**Author:** ![adauner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/adauner/32/250242_2.png) [@adauner](https://forum.nachi.org/u/adauner)\
**Post date:** [July 25, 2024, 1:49pm UTC](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943/20 "2024-07-25T13:49:00Z")

</div>

> [@jjonas](#):
>
> Who made the corrections? You/DIY? Handyman? Licensed Electrician?  
> What exactly did the “corrections” consist of?  
> Be specific.

![Screenshot_25-7-2024_94639_mail.yahoo.com](https://global.discourse-cdn.com/internachi/original/4X/c/7/3/c735ce35d508550c2d5bd1ac73ca9a3dd1275096.jpeg)  
This was the work that was done

[Next page](https://forum.nachi.org/t/200amp-main-breaker-wiring-not-updated/244943.md?page=2)