I for got to check brand of panel and I could not determine how many amps this panel is. This is for a condo built in 2000 in the state of Florida. I used phone app but still learning it. Any help would be appreciated. I have not done a ton of inspections and am still prone to “rookie” mistakes. If I could get help today that would be great. Thank you all in advance!! Doug
they look like square d breakers although it is a little hard to blow the picture up and tell. if i had to guess the total amps i’d say 150 but hard to say without determining the size of the feeder. i’m still new too though. someone will be along soon to verify.
It’s a Square D panel.
Go outside and find the meters and main disconnect, likely grouped together on one side of the building or the other.
The panel is a Square D type QO. You would need to find the OCPD that is ahead of the feeder to determine the panel capacity in amperes.
Yep, SquareD panel. Some condos in my area have the main disconnect in a locked electrical room. Sometimes on older buildings the “ELECTRIC ROOM” sign(s) have been painted over. I document those findings when that is the case. Don’t “guess” document what you find.
That helps. Some here said that too. Need a few more to confirm. Bugged there are no main breakers. Never saw one like this.
A few more what?
There is likely a main at a different location, such as:
Very common in condos and apartments. The service disconnect is adjacent to the meter in a remote location. Typically this is called a sub-panel. Since it’s lacking the service disconnect it is not a service.
Like people said above, the best thing to do to determine capacity is to track down the electrical disconnect which is probably at the meter bank, often outside.
If you have more pictures than what you’re showing, you might see if you can read what the information label (above where they label the circuits) on the inside of the door says. That label gives a lot of helpful information about the electrical panel manufacturer, the model number and the overall amperage rating for the enclosure.
In cases when I can’t find the main disconnect for the panel (big property, can’t find, don’t have access to meter area, etc.), I then use the panel amperage rating given on the label.
Also, in general, I find that when I go to properties, I’d rather have more pictures than less.
Nice question. Keep up the good work.
Morning, Douglas. Pleasure to meet you.
The sub/remote panel appears to be manufactured by Square D.
The manufacturer’s label, inside the panel door will rate the maximum ampacity. (Right hand side in this case)
The main disconnect, main breaker, is likely located in/on the metering equipment inclosure.
Electrical: Observation.
Square-D sub/remote panel.
12 OCPD’s.
7 empty spaces.
Unknown closure ampacity.
No adverse conditions observed the day of the inspection. PS: I did not pay attention to the circuits and terminations.
Remember to include if GFCI and AFCI were available and functional.
If you cannot find the feeder OCPD to determine the feeder size you cannot accurately determine the panels maximum ampacity. You could use a combination of the panel rating and the size of the feeder conductors to make an educated guess as the ampacity.
Using only the panel rating may be a problem because the panel rating can be higher than the feeder ampacity. The same holds true for the opposite observation, using only the conductor size to determine the ampacity since in condo and apartment buildings long runs of feeder conductors may be oversized to compensate for voltage drop.
As an example if you knew that the feeder was relatively short and likely not oversized for voltage drop then the conductor size alone may be enough to tell you the feeder ampacity. So making an educated guess by looking at the second photo. If you had a 125 amp panel rating and a #1 aluminum (rated at 100 amps) feeder you could have a 100 amp maximum ampacity for the panel.
When the feeder conductors are smaller (lower amp rating) than the panel rating you cannot use the panel rating to determine the overall maximum ampacity of the panel.