I did Inspection at single family with at 70 amp in Florida what is the recommendation for this…Sorry is not mobile home is residential
Depends on who you ask. Min. recommended is 100 amps. Some insurance carriers in Florida will not write policies on homes with less than 100 amps.
Was the heat pump on it’s own breaker on an outside panel? I have seen some anemic interior panels with a 50 amp HVAC breaker next to the meter.
Are you referring to the exterior Main Panel, or the interior Sub-panel?
That is not a 70 amp panel. The 70 you see is feeding the bottom section of a split buss panel. Hard to tell the size of the SEC from the photo but probably a 100 amp service.
I agree with David its a split bus panel. And punch the guy from regional pest control in the face for covering the panel label which show that it’s a split bus.
That’s the meter box. You do not disconnect service by taking the meter off.
The two breakers highlighted below are your disconnects. The circled breaker turns off all the breakers below.
Yes but is not another one
I know but that’s the only two
So the 50 and the 70 are the amps for the house
Hello Jesus.
Was that meter attached to the exterior wall of the same building that the Cutler Hammer panel was inside of?
Did you look behind the wall that the meter was attached to to see if there was a second panel?
The main service disconnect in that backfed Cutler Hammer panel appears to be missing a fastener to keep it from accidentally being removed from the bus bar.
Adam
Jesus, maybe this will help you understand split buss panels and how to shut off electricity.
I’m not sure I agree with this. Why would there have to be another disconnect upstream of this panel? If there were another one, I would expect to see ground/neutrals separated in this panel (in most cases). Also, this panel is clearly older than the requirement for an exterior disconnect..
Mobile (manufactured) homes usually have a main service disconnect or electrical service disconnect at the exterior of the home where I live in Colorado. The photo of that meter on the wall does not resemble a manufactured home. There’s more to the story that we’re not getting from Jesus.
Agree with that part.
And I’m not sure it’s a “mobile” or manufactured home either.