![IMG_8101](https://global.discourse-cdn.com/internachi/original/4X/d/0/8/d081a02674f88695e81e486df67fa25dc2cc0b95.jpeg)Doing a new build inspection and came across this setup in the kitchen. I know AAVs are acceptable in Texas, but my question specifically is about its placement. I thought they had to be above the drain connection point to help provide adequate air flow and avoid potential backup overflows.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [September 29, 2026, 5:27pm UTC](https://forum.nachi.org/t/aav-placement-in-kitchen/271065/2 "2026-09-29T17:27:13Z")

</div>

> [@jmatthews10](#):
>
> ![IMG_8101](https://global.discourse-cdn.com/internachi/original/4X/d/0/8/d081a02674f88695e81e486df67fa25dc2cc0b95.jpeg)
> 
> Doing a new build inspection and came across this setup in the kitchen. I know AAVs are acceptable in Texas, but my question specifically is about its placement. I thought they had to be above the drain connection point to help provide adequate air flow and avoid potential backup overflows

Going from memory, I believe the AAV inlet must be positioned at least 4 inches above the horizontal drain pipe it serves. @mwilles will be along to help.

 ![000](https://global.discourse-cdn.com/internachi/original/4X/d/8/4/d841dab96a99f0372b4d2eb5ae722897f8aafb3f.jpeg)

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [September 29, 2026, 6:37pm UTC](https://forum.nachi.org/t/aav-placement-in-kitchen/271065/3 "2026-09-29T18:37:28Z")

</div>

> [@lkage](#):
>
> Going from memory, I believe the AAV inlet must be positioned at least 4 inches above the horizontal drain pipe it serves.

You are correct. there’s nothing wrong with the installation method used under the sink in this photograph.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [September 29, 2026, 6:38pm UTC](https://forum.nachi.org/t/aav-placement-in-kitchen/271065/4 "2026-09-29T18:38:56Z")

</div>

> [@jmatthews10](#):
>
> I thought they had to be above the drain connection point

It is. The AAV is venting the P-trap.