AC Breaker Sizes Minimum


2014 York AC calls for a minimum of 23.7 amp minimum circuit ampacitiy and maximum overcurrent protection 40.

The panel legend shows the AC is on a 20 amp breaker. I believe you are supposed to round up not down. Is this being overkill/pedantic or should it be rounded to a 25 amp breaker minimum?

1 Like

I think Robert has a very good reputation. I believe he answers your question.

2 Likes

Thanks I was hoping he would chime in I’ll definitely read what he said

Good forum I read through most of it.

1 Like

The OCPD should be a minimum of 25 amps. Having said that it will probably run for a long time on the current 20 amp breaker. The nameplate current at 208 volts is 17.9+1.3=19.2 amps. Run that unit at the normal home voltage of 240 volts and the current will drop by the ratio of 208 to 240 volts so 208/240=.867 19.2*.867=16.6 amps. Put an ammeter on the circuit conductors when it running and it should read approximately 16.6 amps.

5 Likes

All of which is fine and well for an AC tech or an electrician BUT the manufacturers installation requirements trump all of that. I would write it up.

8 Likes

I agree. It’s wrong and needs to be corrected.

8 Likes

I thought so but wanted to be sure. Apparently 25 amp breakers don’t exist in the hvac vans

1 Like

Good point about the 25 amp circuit breaker. Although 25 amps is a standard size and are readily available it seems like many installers don’t use them (think hot water heaters). In this case a 2P-30 would be just fine.

2 Likes