Is there a code that explicitly prohibits this?

This is all I can find about the primary condensate drain in the IRC:

“M1411.3 Condensate disposal. Condensate from all cooling  
coils or evaporators shall be conveyed from the drain pan outlet  
to an approved place of disposal. Condensate shall not discharge  
into a street, alley or other areas where it would cause a  
nuisance.”

![050610 128.JPG](https://global.discourse-cdn.com/internachi/original/2X/9/92bc72428c8c90718d29b714b9bd6ffa6312c856.jpeg)

---

<div class="post-metadata">

**Author:** ![bkelly2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bkelly2/32/58257_2.png) [@bkelly2](https://forum.nachi.org/u/bkelly2)\
**Post date:** [May 7, 2010, 4:48am UTC](https://forum.nachi.org/t/ac-condensate-drain-into-plumbing-vent/49419/2 "2010-05-07T04:48:48Z")

</div>

What does your code book say about DWV lines Joe??

03 irc 1411.3 No direct connection to waste of vent pipe…UMC is similar

---

<div class="post-metadata">

**Author:** ![bkelly2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bkelly2/32/58257_2.png) [@bkelly2](https://forum.nachi.org/u/bkelly2)\
**Post date:** [May 7, 2010, 5:14am UTC](https://forum.nachi.org/t/ac-condensate-drain-into-plumbing-vent/49419/3 "2010-05-07T05:14:49Z")

</div>

Joe, the condensate line needs to have a trap that will not dry out if it is tied into the DWV system, or an air gap or a trap tail piece…

Also I believe the Condensates lines is not “Listed” in the code to make that connection into the DWV system…

And I can not tell from your picture but if that is any type of saddle connection is is prohibited in the DWV system…

[http://www.inspectapedia.com/aircond/aircond17c.htm](http://www.inspectapedia.com/aircond/aircond17c.htm)

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [May 7, 2010, 5:22am UTC](https://forum.nachi.org/t/ac-condensate-drain-into-plumbing-vent/49419/4 "2010-05-07T05:22:03Z")

</div>

> [@bkelly2](#):
>
> Joe, the condensate line needs to have a trap that will not dry out if it is tied into the DWV system, or an air gap or a trap tail piece…
> 
> Also I believe the Condensates lines is not “Listed” in the code to make that connection into the DWV system…
> 
> And I can not tell from your picture but if that is any type of saddle connection is is prohibited in the DWV system…

It did have a ptrap (but incorrectly had the cleanout downstream of the ptrap).

The vent simply had a hole cut into it and the c-drain was inserted into the hole. I know it’s not right, but can’t put my finger on anything to back me up.

I’m writing it up anyway.

---

<div class="post-metadata">

**Author:** ![bkelly2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bkelly2/32/58257_2.png) [@bkelly2](https://forum.nachi.org/u/bkelly2)\
**Post date:** [May 7, 2010, 5:38am UTC](https://forum.nachi.org/t/ac-condensate-drain-into-plumbing-vent/49419/5 "2010-05-07T05:38:09Z")

</div>

> [@jfunderburk](#):
>
> It did have a ptrap (but incorrectly had the cleanout downstream of the ptrap).
> 
> The vent simply had a hole cut into it and the c-drain was inserted into the hole. I know it’s not right, but can’t put my finger on anything to back me up.
> 
> I’m writing it up anyway.

If you look in the DWV section of the code, you can not have a saddle connection in the DWV system…

In a nutshell that is not an approved connection for the DWV system…

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [May 7, 2010, 5:42am UTC](https://forum.nachi.org/t/ac-condensate-drain-into-plumbing-vent/49419/6 "2010-05-07T05:42:25Z")

</div>

Thanks Brian. You’re a great help.

I’m trying to get done. Got 3 tomorrow and I’m bushed.