# AFCI test button. Hit it or Not

**URL:** <https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459>\
**Category:** Misc. Discussion\
**Created:** [November 30, 2022, 2:01pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459 "2022-11-30T14:01:31Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![hwoosley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/hwoosley/32/207873_2.png) [@hwoosley](https://forum.nachi.org/u/hwoosley)\
**Post date:** [November 30, 2022, 2:01pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/1 "2022-11-30T14:01:31Z")

</div>

I am confused with testing of AFCIs. While in school they said to not hit the test button due to home owners having computers and such plugged in and it may mess up the work they have on their computer. Everything I read says to hit the test button. What do we do? I will test the outlet for defects but does the test button need to be checked?

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [November 30, 2022, 2:13pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/2 "2022-11-30T14:13:07Z")

</div>

You can on vacant homes. I don’t do it on occuied homes and put it as a limitation in the report.

---

<div class="post-metadata">

**Author:** ![hwoosley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/hwoosley/32/207873_2.png) [@hwoosley](https://forum.nachi.org/u/hwoosley)\
**Post date:** [November 30, 2022, 2:31pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/3 "2022-11-30T14:31:58Z")

</div>

Thank you! That was my thought but then I was second guessing myself!

---

<div class="post-metadata">

**Author:** ![lhenderson2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lhenderson2/32/58205_2.png) [@lhenderson2](https://forum.nachi.org/u/lhenderson2)\
**Post date:** [November 30, 2022, 2:38pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/4 "2022-11-30T14:38:08Z")

</div>

Ditto Ryan.  
I had a first generation AFCI explode. It was like a little blow torch in the panel. Makes a good story now, but at the time, it was pretty exciting.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [November 30, 2022, 2:41pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/5 "2022-11-30T14:41:04Z")

</div>

> [@ruecker](#):
>
> I don’t do it on occuied homes and put it as a limitation in the report.

Same for me with some GFCI’s (especially when a freezer is involved 😄 )

---

<div class="post-metadata">

**Author:** ![hwoosley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/hwoosley/32/207873_2.png) [@hwoosley](https://forum.nachi.org/u/hwoosley)\
**Post date:** [November 30, 2022, 3:08pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/6 "2022-11-30T15:08:38Z")

</div>

Thanks, that makes a great point too!

---

<div class="post-metadata">

**Author:** ![mburfitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mburfitt/32/266036_2.png) [@mburfitt](https://forum.nachi.org/u/mburfitt)\
**Post date:** [November 30, 2022, 4:34pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/7 "2022-11-30T16:34:32Z")

</div>

Everyone who is selling a home should have all their personal stuff put away, including electronics. I usually take a peek before testing the bedrooms just as a courtesy but given how often we lose power current homeowners should not be bothered by it. Besides, isn’t testing GFCI/AFCI breakers a part of the InterNACHI SOP?

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [November 30, 2022, 5:53pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/9 "2022-11-30T17:53:15Z")

</div>

I always ask, and 99.9% get a “no problem” or a “just a moment”. Then I press the button.

---

<div class="post-metadata">

**Author:** ![kleonard](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kleonard/32/170953_2.png) [@kleonard](https://forum.nachi.org/u/kleonard)\
**Post date:** [November 30, 2022, 7:03pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/10 "2022-11-30T19:03:23Z")

</div>

I’ve always tested them all and through the years have found quite a few that wouldn’t trip, but to each their own, as inspectors we each should stay within our comfort zone.

On a side note, I do inform all LAs in emails sent when the inspection is scheduled that I’ll be testing AFCI & GFCI devises.

---

<div class="post-metadata">

**Author:** ![mfellman](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mfellman/32/369692_2.png) [@mfellman](https://forum.nachi.org/u/mfellman)\
**Post date:** [November 30, 2022, 7:10pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/11 "2022-11-30T19:10:12Z")

</div>

> [@mburfitt](#):
>
> Everyone who is selling a home should have all their personal stuff put away, including electronics.

So, to sell a house a person should live like a caveman?

---

<div class="post-metadata">

**Author:** ![hwoosley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/hwoosley/32/207873_2.png) [@hwoosley](https://forum.nachi.org/u/hwoosley)\
**Post date:** [November 30, 2022, 7:25pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/12 "2022-11-30T19:25:42Z")

</div>

Thank you!

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [November 30, 2022, 7:37pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/13 "2022-11-30T19:37:35Z")

</div>

> [@hwoosley](#):
>
> I am confused with testing of AFCIs. While in school they said to not hit the test button due to home owners having computers and such plugged in and it may mess up the work they have on their computer

Afternoon, Heather.  
Hope to find you well.

As for testing of AFCI breakers or AFCI devices. Follow the manufacturer’s’ recommendations. Nothing trumps manufactures’ recommendations.  
As well, you can protect yourself by putting memo in your PIA by requesting homeowners list if the home is continually monitored by an insurance company. Ask them to lists what not to test in terms of AFCI, Fire Alarms, and other safety items incase the home is monitored by an insurance provider.  
As well, you can ask the venders agent if it is OK to test AFCI devices.

---

<div class="post-metadata">

**Author:** ![mburfitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mburfitt/32/266036_2.png) [@mburfitt](https://forum.nachi.org/u/mburfitt)\
**Post date:** [November 30, 2022, 7:48pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/14 "2022-11-30T19:48:57Z")

</div>

I think you know what I mean: nobody is going to leave expensive electronics or an important document open on the computer during an inspection or an open house, at least I have never seen it in the hundreds of homes I have been inside. Either way I doubt any homeowner will really care you flicked the power for a second: after all they are not surprised by your visit.

---

<div class="post-metadata">

**Author:** ![mfellman](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mfellman/32/369692_2.png) [@mfellman](https://forum.nachi.org/u/mfellman)\
**Post date:** [November 30, 2022, 8:19pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/15 "2022-11-30T20:19:00Z")

</div>

They shouldn’t but assuming they won’t/didn’t is a big assumption. There’s a reason the SOPs have an exclusion for occupied houses. Any one house it’s very unlikely to be a problem but like everything in this business, the numbers will catch up with you eventually.

---

<div class="post-metadata">

**Author:** ![ddagostino](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ddagostino/32/60136_2.png) [@ddagostino](https://forum.nachi.org/u/ddagostino)\
**Post date:** [November 30, 2022, 9:45pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/16 "2022-11-30T21:45:38Z")

</div>

> [@mburfitt](#):
>
> nobody is going to leave expensive electronics or an important document open on the computer during an inspection

Been at plenty of gigs where the sellers/occupants are working in their office, on PC’s, etc…  
Life goes on for homeowners, inspection or not.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [November 30, 2022, 10:14pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/17 "2022-11-30T22:14:20Z")

</div>

> [@mburfitt](#):
>
> expensive electronics

I inspect occupied homes all the time that have expensive Medical Devices that are plugged in and powered up, (usually in bedrooms), such as Oxygen Concentrators.  
Maybe $1,000+ is nothing to you, but I bet my clients would disagree! Their insurance definitely will not cover a device that the inspector fried!!

---

<div class="post-metadata">

**Author:** ![srechkin](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/srechkin/32/180448_2.png) [@srechkin](https://forum.nachi.org/u/srechkin)\
**Post date:** [November 30, 2022, 10:34pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/18 "2022-11-30T22:34:02Z")

</div>

Expensive medical devices necessary to sustain life, or such, should be plugged in and protected by UPS+generator. Power companies do lose power and do not guarantee your power will be on 24/7/365 and or there won’t be spikes in voltage when power does come back. Few years back I used to lose power at least 1s a month or so where I live. After much complaining, they have finally upgraded some of the infrastructure and pruned a lot of trees around the power lines.

---

<div class="post-metadata">

**Author:** ![mmasengale](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mmasengale/32/176219_2.png) [@mmasengale](https://forum.nachi.org/u/mmasengale)\
**Post date:** [December 1, 2022, 4:48pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/19 "2022-12-01T16:48:18Z")

</div>

Hello Heather -  
Nope. I never ever (repeat never & ever) turn on/turn off/test any breakers. I inspect for and report on their presence and absence only. I’ve been there, done that, and know what the results can be.  
Some will claim that testing these breakers is required by our SOP. This is not necessarily true as it is a confliction in the SOP. Which means you could go either way. It’s up to you.  
From the SOP:  
I. The inspector SHALL inspect:  
J.a representative number of switches, lighting fixtures and receptacles, including receptacles observed and deemed to be arc-fault circuit interrupter (AFCI)-protected using the AFCI test button, where possible;  
K. all ground-fault circuit interrupter receptacles and circuit breakers observed and deemed to be GFCIs using a GFCI tester, where possible

> Which is followed by…  
> IV. The inspector is NOT required to:

A. insert any tool, probe or device into the main panelboard, sub-panels, distribution panelboards, or electrical fixtures.  
D. operate or re-set over-current protection devices or overload devices.

With video cam in action - I WILL test accessible GFCI receptacles using their test button only, and confirm that all required (on-circuit) receptacles also shut-off. If I notice any devices plugged-in and reliant on any on-circuit receptacles (phones w/answer machine, devices operating on a timer), I will not test at all.

Whether you choose to test or not to test - A healthy disclaimer or warning in your report limitations is advisable.

Looks like you may be new to the biz. Welcome to the industry!  
If you need any help with the limitation narratives, holler.

---

<div class="post-metadata">

**Author:** ![mmasengale](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mmasengale/32/176219_2.png) [@mmasengale](https://forum.nachi.org/u/mmasengale)\
**Post date:** [December 1, 2022, 5:01pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/20 "2022-12-01T17:01:43Z")

</div>

> [@mburfitt](#):
>
> Everyone who is selling a home should have all their personal stuff put away, including electronics.

Now ‘that’s’ a delightful fantasy!

---

<div class="post-metadata">

**Author:** ![lhenderson2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lhenderson2/32/58205_2.png) [@lhenderson2](https://forum.nachi.org/u/lhenderson2)\
**Post date:** [December 1, 2022, 5:19pm UTC](https://forum.nachi.org/t/afci-test-button-hit-it-or-not/222459/21 "2022-12-01T17:19:58Z")

</div>

> [@mburfitt](#):
>
> Either way I doubt any homeowner will really care you flicked the power for a second: after all they are not surprised by your visit.

Oh grasshopper…Yes and double yes, at some point, some homeowner/seller will be dressing you down like a 3-year-old for interrupting the recording of their favorite soap opera, and the SoP will not protect you for a second. You can (and I have) proclaimed that “I am a home inspector and testing safety devices is what I do, but I can tell you the that sellers are unmoved by that defense.” And now, I have set up an acrimonious situation for my client in negotiating with the seller. And that is only for a soap opera. What if you mess up something important?

I typically test all GFCIs. But I recommend tripping them with the test button or at the GFCI outlet and then finding out what is de-energized downstream with your 3-light tester, instead of tripping them from a remote outlet and then searching for the controlling GFCI. But AFCI breakers are tested only on vacant homes, for me.

As others have said, we all operate as we see fit. I do many things that some other inspectors do not. We all find what works best for us, usually through a course at the school of hard knocks.