Had this today. All branch wiring copper except for AC condenser and Oven. Both appeared to have AL strand (picture shows 40A breaker for oven). First time I’ve seen this. Any concerns? Thx.

![Wire.jpg](https://global.discourse-cdn.com/internachi/original/3X/e/1/e10831c3488a6ca41411a88dd1c2f9558baaa02e.jpeg)

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [April 8, 2009, 8:28pm UTC](https://forum.nachi.org/t/aluminum-wiring/37811/2 "2009-04-08T20:28:41Z")

</div>

Multi-strand AL wiring does not have the same problems associated with solid AL conductors. No issues to be concerned about. . .

---

<div class="post-metadata">

**Author:** ![rnewland](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rnewland/32/59431_2.png) [@rnewland](https://forum.nachi.org/u/rnewland)\
**Post date:** [April 8, 2009, 8:41pm UTC](https://forum.nachi.org/t/aluminum-wiring/37811/3 "2009-04-08T20:41:55Z")

</div>

> [@jpope](#):
>
> Multi-strand AL wiring does not have the same problems associated with solid AL conductors. No issues to be concerned about. . .

I kneel to the Pope:D

Thanks Jeff!

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [April 9, 2009, 2:17am UTC](https://forum.nachi.org/t/aluminum-wiring/37811/4 "2009-04-09T02:17:51Z")

</div>

The AL conductor appears to be 8 gauge protected by a 40 Amps breakers, shouldn’t it be 6 gauge?

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [April 9, 2009, 2:27am UTC](https://forum.nachi.org/t/aluminum-wiring/37811/5 "2009-04-09T02:27:15Z")

</div>

> [@mgratton](#):
>
> The AL conductor appears to be 8 gauge protected by a 40 Amps breakers, shouldn’t it be 6 gauge?

Condenser circuits are generally wired that way. . .

---

<div class="post-metadata">

**Author:** ![fnewman](https://avatars.discourse-cdn.com/v4/letter/f/90db22/32.png) [@fnewman](https://forum.nachi.org/u/fnewman)\
**Post date:** [April 9, 2009, 3:09am UTC](https://forum.nachi.org/t/aluminum-wiring/37811/6 "2009-04-09T03:09:46Z")

</div>

I assume you also observed/wrote up the doubled neutral connections.

---

<div class="post-metadata">

**Author:** ![bkelly2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bkelly2/32/58257_2.png) [@bkelly2](https://forum.nachi.org/u/bkelly2)\
**Post date:** [April 9, 2009, 10:30pm UTC](https://forum.nachi.org/t/aluminum-wiring/37811/7 "2009-04-09T22:30:19Z")

</div>

:D:D:D