Ok, I just finished one of my mock inspections and am a bit confused on if something is in need of correction. The service pa el has a 200amp main disconnect. It has 2 hot lines coming in and a neutral to the service panel. The first 4 breakers are 100 amp tied breakers for feeding distribution panels. There are a number of other breakers in the panel as well that add up to over 150amps. With two hot lines coming into the 200amp main disconnect that feeds two separate bus bars does that mean each bus bar has 200 amps or that each has 100amps? Also am I misremembering or arent the total amperage of the breakers in the box supposed to add up to (at most) the total amps coming into the panel?

The only way to know if a panel is overloaded is to perform a load calculation from Article 220 of the NEC. Adding up the amp ratings on the various circuit breaker handles is meaningless.

Can you post some photos of the panel in question? Maybe we can shed some light on what you’re looking at.

1 Like

Neither. Buss bars do not have or supply amperage.

The 200 amp breaker will allow up to 200 amps to be drawn from each leg of a 120/240 volt system. If either leg exceeds 200 amps, the breaker will trip and shut off power to both legs entirely.

I don’t think it’s "misremembering" as much as it is a misunderstanding of electrical theory. Amps do not come into a panel. Amperage is a measurement of the amount of current drawn by the loads connected to the panel.

Each breaker allows up to the breaker rating to be drawn off of the circuit. The 200 amp main breaker will allow up to 200 amps to be drawn off of the panel as a whole. The total of the breakers has nothing to do with the rating of the main breaker.

9 Likes

So what you’re calling four breakers is actually two circuit breakers. They are 2-pole circuit breakers. Each is a single unit. Even though it appears that they are separate they are not which is evident by the external handle-tie connecting each pole together. Here’s what it looks like out of the panel.

Each of those legs can provide 200 amps @120 volts or the two legs together can provide 200 amps @ 240 volts. Each of those bus bars would have a minimum rating of 200 amps.