Had a furnace today with no indication of who the manufacturer is.
Also all the instruction labels were in both English and French!
Please take a look at the pictures and let me know if you have any idea of who the manufacturer is. Thanks!
Had a furnace today with no indication of who the manufacturer is.
Also all the instruction labels were in both English and French!
Please take a look at the pictures and let me know if you have any idea of who the manufacturer is. Thanks!
Google says…
**Luxaire furnaces that start with the model numbers: PAKU, PBKM, and PBKD
Or also might be York.
**
Hmmm
A Flex connector entering the housing to the metering valve… A no no around here…
It comes back as Brand: FRASER JOHNSTON (Also Luxaire) , Power or Power Vent / Noncondensing, Nonweatherproof
Up [flow](http://www.furnacecompare.com/faq/definitions/air_flow_configuration.html)
Natural Gas
We’re on the same page Patrick…I saw it too. Here is what I put in the report…
• Improve: The flexible appliance fuel (gas) connector should terminate prior to entering the furnace appliance cabinet wall. Only rigid gas pipe should pass through the cabinet wall. As is, this represents a potential gas leak condition.