# B-vent going through side of house

**URL:** <https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292>\
**Category:** Inspecting HVAC Systems\
**Created:** [July 27, 2021, 8:51pm UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292 "2021-07-27T20:51:03Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![sdale2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sdale2/32/89377_2.png) [@sdale2](https://forum.nachi.org/u/sdale2)\
**Post date:** [July 27, 2021, 8:51pm UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/1 "2021-07-27T20:51:03Z")

</div>

So there is a b-vent going through the basement wall for the furnace. Am I correct that this is only allowed if it’s a pvc vent for a high efficiency furnace?

 ![vent picture](https://global.discourse-cdn.com/internachi/original/3X/6/3/63bd24b57530dc0cf668ec6dba7dfb6676a30181.jpeg)

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [July 27, 2021, 9:12pm UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/2 "2021-07-27T21:12:10Z")

</div>

> [@sdale2](#):
>
> So there is a b-vent going through the basement wall for the furnace

Do you have any more information on the furnace such as the category?

---

<div class="post-metadata">

**Author:** ![jgilbert10](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgilbert10/32/201851_2.png) [@jgilbert10](https://forum.nachi.org/u/jgilbert10)\
**Post date:** [July 27, 2021, 9:31pm UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/3 "2021-07-27T21:31:52Z")

</div>

![image](https://global.discourse-cdn.com/internachi/original/3X/f/5/f540fbb86c90d7ea7de6cf2317ef49cdc545b4ce.png)

---

<div class="post-metadata">

**Author:** ![jgilbert10](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgilbert10/32/201851_2.png) [@jgilbert10](https://forum.nachi.org/u/jgilbert10)\
**Post date:** [July 27, 2021, 9:33pm UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/4 "2021-07-27T21:33:45Z")

</div>

As Martin had asked, any additional info or picture of the unit

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [July 27, 2021, 9:46pm UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/5 "2021-07-27T21:46:20Z")

</div>

That is correct a B vent is not allowed to terminate through a wall horizontally. I suspect there is more to this furnace and would like to know the model. Pictures of the furnace with flue connectors would help.

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [July 28, 2021, 1:12am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/6 "2021-07-28T01:12:24Z")

</div>

> [@sdale2](#):
>
> Am I correct that this is only allowed if it’s a pvc vent for a high efficiency furnace?

PVC is most common for homes. But up here in cold country (MN) we see many garage heaters with Z-vent stainless steel sidewall venting and horizontal termination, which is allowed. Of course we also see just as many unapproved b-vent horizontal terminations because of the cost of the Z-vent product, lol.

 ![zvent](https://global.discourse-cdn.com/internachi/original/3X/5/a/5af67f6f5e4fea52dfd0f4bc7e9d3b8d080b589f.png)

---

<div class="post-metadata">

**Author:** ![sdale2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sdale2/32/89377_2.png) [@sdale2](https://forum.nachi.org/u/sdale2)\
**Post date:** [July 28, 2021, 2:59am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/7 "2021-07-28T02:59:31Z")

</div>

Thanks for the information, guys. Here are some more pictures of the furnace.

 ![20210726_210932](https://global.discourse-cdn.com/internachi/original/3X/5/8/58d6b599c5ff496b746a04087bad8951068a86c9.jpeg)  
 ![20210726_211051](https://global.discourse-cdn.com/internachi/original/3X/d/9/d93b95b7174db9c8e275d9abeb419271838fb7aa.jpeg)  
 ![20210726_211020](https://global.discourse-cdn.com/internachi/original/3X/6/9/699d5aab39a0bcc2c2bbba32243dfb0dcef06ccf.jpeg)

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [July 28, 2021, 3:06am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/8 "2021-07-28T03:06:40Z")

</div>

That is an old gal, 25 years. Might be time to get that high efficiency and solve the problem 🙂

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [July 28, 2021, 3:08am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/9 "2021-07-28T03:08:02Z")

</div>

Just curious, what is this?  
 ![image](https://global.discourse-cdn.com/internachi/original/3X/d/6/d6a2fc75fdeaeee4d397cb189a2a7b70732b5170.jpeg)

---

<div class="post-metadata">

**Author:** ![sdale2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sdale2/32/89377_2.png) [@sdale2](https://forum.nachi.org/u/sdale2)\
**Post date:** [July 28, 2021, 3:08am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/10 "2021-07-28T03:08:51Z")

</div>

That’s the vent for the high efficiency water heater next to it.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [July 28, 2021, 3:09am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/11 "2021-07-28T03:09:30Z")

</div>

Intake or exhaust? Where is the intake?

---

<div class="post-metadata">

**Author:** ![sdale2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sdale2/32/89377_2.png) [@sdale2](https://forum.nachi.org/u/sdale2)\
**Post date:** [July 28, 2021, 3:14am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/12 "2021-07-28T03:14:21Z")

</div>

I just looked up the serial number. Manufactured in 1996. 25 years right on the money!

---

<div class="post-metadata">

**Author:** ![mfellman](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mfellman/32/369692_2.png) [@mfellman](https://forum.nachi.org/u/mfellman)\
**Post date:** [July 28, 2021, 4:04am UTC](https://forum.nachi.org/t/b-vent-going-through-side-of-house/201292/13 "2021-07-28T04:04:23Z")

</div>

The inducer fan cover on that furnace also looks to be cracked - a common issue on that age/type of furnace. I agree with the others that the installation if incorrect. Get it off your plate and get an HVAC tech out to clean up the mess.

 ![Inkedd93b95b7174db9c8e275d9abeb419271838fb7aa_LI](https://global.discourse-cdn.com/internachi/original/3X/9/6/96f7d481acbc7a9483bb7ec4ec10c7593e0b311a.jpeg)