# Barriers in Service Panels

**URL:** <https://forum.nachi.org/t/barriers-in-service-panels/216565>\
**Category:** Electrical Inspections\
**Created:** [June 8, 2022, 3:35am UTC](https://forum.nachi.org/t/barriers-in-service-panels/216565 "2022-06-08T03:35:42Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![sdarden](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sdarden/32/249788_2.png) [@sdarden](https://forum.nachi.org/u/sdarden)\
**Post date:** [June 8, 2022, 3:35am UTC](https://forum.nachi.org/t/barriers-in-service-panels/216565/1 "2022-06-08T03:35:42Z")

</div>

Barriers are required on the main lugs on service panel boards. The NEC 230.62 discusses the protected lugs are on the load side. Does this mean the lugs on a sub panel board are not required to be protected by a barrier?

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [June 8, 2022, 11:51am UTC](https://forum.nachi.org/t/barriers-in-service-panels/216565/2 "2022-06-08T11:51:57Z")

</div>

That is correct because for a sub-panel the line side terminals can be de-energized by opening the OCPD on the feeder at it’s origin. So if you had a 100 amp circuit breaker in the service feeding a 100 amp sub-panel that breaker can be opened to completely de-energize the sub-panel.

---

<div class="post-metadata">

**Author:** ![sdarden](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sdarden/32/249788_2.png) [@sdarden](https://forum.nachi.org/u/sdarden)\
**Post date:** [June 8, 2022, 1:29pm UTC](https://forum.nachi.org/t/barriers-in-service-panels/216565/3 "2022-06-08T13:29:16Z")

</div>

Thank you.