# Bond wire needed at jetted tub?

**URL:** <https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850>\
**Category:** Electrical Inspections\
**Created:** [October 23, 2012, 5:27pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850 "2012-10-23T17:27:53Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![mpettitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mpettitt/32/57038_2.png) [@mpettitt](https://forum.nachi.org/u/mpettitt)\
**Post date:** [October 23, 2012, 5:27pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/1 "2012-10-23T17:27:53Z")

</div>

Jetted tub in master bath, all plastic piping except supply is copper. Should there be a bonding wire from copper supply to pump motor?  
Thanks

![121020 1504 N Manowar Dr, Her - Full, Wind 075.jpg](https://global.discourse-cdn.com/internachi/original/3X/0/2/0285c5dcea8d4b21477a101e7ce22f3d1a892c74.jpeg)

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [October 23, 2012, 5:47pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/2 "2012-10-23T17:47:52Z")

</div>

Good luck

IMHO yes

Looks like a ground terminal lug on that motor to me.

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [October 23, 2012, 5:55pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/3 "2012-10-23T17:55:59Z")

</div>

Bonding is only required if the piping is in contact with the circulating water.

---

<div class="post-metadata">

**Author:** ![mpettitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mpettitt/32/57038_2.png) [@mpettitt](https://forum.nachi.org/u/mpettitt)\
**Post date:** [October 23, 2012, 6:00pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/4 "2012-10-23T18:00:42Z")

</div>

Yes, I see what you mean but thanks, you gave me my answer (deferred)

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [October 23, 2012, 6:11pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/5 "2012-10-23T18:11:28Z")

</div>

Is that thing missing a motor mount ?

---

<div class="post-metadata">

**Author:** ![mpettitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mpettitt/32/57038_2.png) [@mpettitt](https://forum.nachi.org/u/mpettitt)\
**Post date:** [October 23, 2012, 6:16pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/6 "2012-10-23T18:16:57Z")

</div>

No, its there, just not visible

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [October 23, 2012, 6:32pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/7 "2012-10-23T18:32:11Z")

</div>

> [@Jim\_Port](#):
>
> Bonding is only required if the piping is in contact with the circulating water.

Never seen a hydro tub with metal piping.

Even if that was a double insulated pump the NEC still says to run a #8 to the area for any future replacement pump that may not be double insulated.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [October 23, 2012, 6:51pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/8 "2012-10-23T18:51:28Z")

</div>

> [@mlarson](#):
>
> Never seen a hydro tub with metal piping.
> 
> Even if that was a double insulated pump the NEC still says to run a #8 to the area for any future replacement pump that may not be double insulated.

680.74 Bonding  
_All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid_.

The motor should be grounded/bonded by the EGC with the branch-circuit feeding the tub.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [October 23, 2012, 7:19pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/9 "2012-10-23T19:19:10Z")

</div>

I understand that Chris. Jim seemed be disagreeing with bonding the motor with a #8. No?

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [October 23, 2012, 8:13pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/10 "2012-10-23T20:13:27Z")

</div>

Since the copper supply is not in contact with the circulating there is no code requirement for it to be bonded.

Could you also supply the code article that states a bond need to be installed in case the tub is changed?

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [October 23, 2012, 8:14pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/11 "2012-10-23T20:14:52Z")

</div>

Watch the Mike Holt link in post #2 Jim

680.74

![680.JPG](https://global.discourse-cdn.com/internachi/original/3X/d/f/dfd566213ccad874116d9be0d5a91c3cdc7836b3.jpeg)

![6802.JPG](https://global.discourse-cdn.com/internachi/original/3X/7/5/75c778cf4f8daef222a0cbe6665cae74a3a1d2b9.jpeg)

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [October 23, 2012, 8:33pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/12 "2012-10-23T20:33:29Z")

</div>

I agree with Jim, the recirculation piping is plastic therefore no bonding is required.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [October 23, 2012, 8:40pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/13 "2012-10-23T20:40:06Z")

</div>

> [@Robert\_Meier](#):
>
> I agree with Jim, the recirculation piping is plastic therefore no bonding is required.

Then why is the pump housing provided with a bonding lug?

If you watch the Mike Holt video the issue confuses Mike and the panel.

60.74 is so poorly written as to be silly in it’s real meaning.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [October 23, 2012, 8:53pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/14 "2012-10-23T20:53:11Z")

</div>

> [@mlarson](#):
>
> Then why is the pump housing provided with a bonding lug?
> 
> If you watch the Mike Holt video the issue confuses Mike and the panel.
> 
> 60.74 is so poorly written as to be silly in it’s real meaning.

I agree that it’s poorly written and that Mike’s guys are wrong on this one. Hopefully the 2014 NEC will clear this up a bit. Here’s a proposal that has so far been accepted.

> [@](#):
>
> * * *
> 
> 17-148 Log #2736 NEC-P17 Final Action: Accept  
> (680.74)
> 
> * * *
> 
> Submitter: Robert Meier  
> Recommendation: Revise text to read as follows:  
> 680.74 Bonding  
> Both metal piping system and all grounded metal parts in contact with the  
> circulating water shall be bonded together using a solid copper bonding jumper,  
> insulated, covered, or bare, not small than 8 AWG. The bonding jumper shall  
> be connected tot eh terminal on the circulating pump motor that is intended for  
> this purpose. The bonding jumper shall not be required to be connected to a  
> double insulated circulating pump motor. The 8 AWG or larger solid copper  
> bonding jumper shall be required for equipotential bonding in the area of the  
> hydromassage bathtub and shall not be required to be extended or attached to  
> the remote panelboard, service equipment, or any electrode. The 8 AWG or  
> larger solid copper bonding jumper shall be long enough to terminate on a  
> replacement non-double-insulated pump motor and shall be terminated to the  
> equipment grounding conductor of the branch circuit of the motor when a  
> double-insulated circulating pump motor is used.  
> Substantiation: There seems to be much confusion with the present wording  
> of this requirement. Inspectors and installers seem to believe that the two parts  
> of the first sentence, All metal piping systems and all grounded metal parts in  
> contact with the circulating water are two separate requirements. Because of  
> this they take the first part All metal piping systems out of context and require  
> the pump to be bonded to the hot and cold metallic water piping that feeds the  
> hydromassage tub faucet. If the intention of this section were to take the first  
> two parts of the sentence as two separate requirements then there would need  
> to be some additional wording that would say exactly where the All metal  
> piping systems that are required to be bonded are located within the structure.  
> When taken as two separate parts, it would mean that every metal piping  
> system within the structure would be required to be bonded to the pump motor.  
> This would include the hot and cold metallic water lines, metallic gas piping  
> systems and any other metallic piping system within the structure. changing the  
> first sentence will clarify that the requirement is solely for metal piping  
> systems and grounded metal parts that contact the circulating water and not the  
> piping used to fill the tub or any other metallic piping systems that may or may  
> not be in the vicinity of the hydromassage tub.  
> Panel Meeting Action: Accept  
> Panel Statement: The panel clarifies that the word “Both” replaces the  
> existing word “all” at the beginning of the first sentence. Otherwise, only the  
> changes shown in legislative text are intended.  
> Number Eligible to Vote: 10  
> Ballot Results: Affirmative: 10

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [October 23, 2012, 9:02pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/15 "2012-10-23T21:02:38Z")

</div>

OK but that is only a proposal. Wait, I see it was accepted by the panel but it still is not in effect.

What about the mfgs. installation instructions?

 ![Hydro Grounding.JPG](https://global.discourse-cdn.com/internachi/original/2X/b/b844fe4ad9f1cb77fc2b1089341161d49a7fc6bc.jpeg)

From here: (PDF page 11)

[http://www.jacuzzi.com/admin/files/files/4c12655c-e074-4e5d-8a6e-5e8643.pdf](http://www.jacuzzi.com/admin/files/files/4c12655c-e074-4e5d-8a6e-5e8643.pdf)

What I am saying is that if you see a grounding lug on the motor it’t there for a reason.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [October 23, 2012, 9:10pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/16 "2012-10-23T21:10:24Z")

</div>

I would guess that maybe sometimes the heater is added later so a bonding jumper can be installed between the motor housing and the heater. If the manufacturers instructions are part of the listing then they must be followed even if they exceed the requirements of the NEC.

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [October 23, 2012, 10:14pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/17 "2012-10-23T22:14:27Z")

</div>

I have seen instructions like those that created a code violation if they were followed. It seems that often times they were written by someone with limited knowledge of the NEC. As that is written it calls for grounding when the correct term would be bonding. The grounding is taken care of by the circuit EGC, not a #8.

The tub also does not require a bonding grid under it like a hot tub AFAIK. The lug would be used if a bond grid were in place.

Thanks for posting that section Mike. I see while reading it that this was a change to the 2011.

---

<div class="post-metadata">

**Author:** ![jwhitt](https://avatars.discourse-cdn.com/v4/letter/j/f4b2a3/32.png) [@jwhitt](https://forum.nachi.org/u/jwhitt)\
**Post date:** [October 26, 2012, 12:51pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/18 "2012-10-26T12:51:11Z")

</div>

How is the water getting into the tub? If you say by the pipes that supply the water to the tub then this must be in contact with the water that is being circulated would you not say.

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [October 26, 2012, 1:30pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/19 "2012-10-26T13:30:51Z")

</div>

The water that is circulating is already contained in the plastic piping of the tub. The water in the supply lines is not circulating.

---

<div class="post-metadata">

**Author:** ![jwhitt](https://avatars.discourse-cdn.com/v4/letter/j/f4b2a3/32.png) [@jwhitt](https://forum.nachi.org/u/jwhitt)\
**Post date:** [October 26, 2012, 1:53pm UTC](https://forum.nachi.org/t/bond-wire-needed-at-jetted-tub/72850/20 "2012-10-26T13:53:39Z")

</div>

Let’s look at what is being said;  
All metal piping systems  
and  
all grounded metal parts in contact with the circulating water shall be bonded together using a solid copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG.  
The water cannot get into the tub unless it comes out of the piping system and it is possible and probable that the water can fill while the tub is on therefore requiring the tub to be bonded to the supply piping.

The mixing valve is exposed to anyone in the tub at all times therefore the supply pipes needs to be bonded.

What we need to keep in mind is that this bond is installed to protect the person in the tub and to keep everything at the same potential. It is not a fault clearing bond.