# Bonding of CSST.

**URL:** <https://forum.nachi.org/t/bonding-of-csst/73276>\
**Category:** Electrical Inspections\
**Created:** [November 8, 2012, 3:23pm UTC](https://forum.nachi.org/t/bonding-of-csst/73276 "2012-11-08T15:23:59Z")\
**Posts on this page:** 6\
**Page:** 2

<div class="post-metadata">

**Author:** ![jwhitt](https://avatars.discourse-cdn.com/v4/letter/j/f4b2a3/32.png) [@jwhitt](https://forum.nachi.org/u/jwhitt)\
**Post date:** [November 12, 2012, 7:14pm UTC](https://forum.nachi.org/t/bonding-of-csst/73276/21 "2012-11-12T19:14:57Z")

</div>

> [@canderson5](#):
>
> Mike, why not be helpful and post several sites you personally would reference regarding the dangers with CSST. I for one would not call it out as junk based on your opinion. You seem to have studied it, share your findings.

It is a little lengthy but it is good. Towards the end are some pictures.

[http://www.nfpa.org/assets/files/PDF/Research/CSST%20Gas%20Piping%20Ph.1%20Final%20Report.pdf](http://www.nfpa.org/assets/files/PDF/Research/CSST%20Gas%20Piping%20Ph.1%20Final%20Report.pdf)

edit to add this one  
[http://hawkeyehomeinspects.com/documents/CSST-DANGERS.pdf](http://hawkeyehomeinspects.com/documents/CSST-DANGERS.pdf)

A warning from the State Fire Marshall  
[http://www.nh.gov/safety/divisions/firesafety/news/20120730-gas-pipe-hazard.html](http://www.nh.gov/safety/divisions/firesafety/news/20120730-gas-pipe-hazard.html)

Am I getting enough or do we need more

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [November 12, 2012, 7:43pm UTC](https://forum.nachi.org/t/bonding-of-csst/73276/22 "2012-11-12T19:43:37Z")

</div>

It will be interesting to see if this is CSST related. It would have nothing to do with bonding/lighting…but.

[Owner: Furnace may be behind deadly Indiana blast](http://www.stltoday.com/news/national/owner-furnace-may-be-behind-deadly-indiana-blast/article_2e438575-58ef-560a-920c-eaf7786cb78d.html)

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [November 12, 2012, 11:06pm UTC](https://forum.nachi.org/t/bonding-of-csst/73276/23 "2012-11-12T23:06:27Z")

</div>

> [@ccurrins](#):
>
> [From Gastite](http://www.gastite.com/include/languages/english/downloads/pdfs/Gastite_LightningSafety_Inspector.pdf):
> 
> 4 NATIONAL ELECTRIC CODE  
> (NEC), Section 250.104b, states that “bonding all  
> piping and metal air ducts within the premises  
> will provide additional safety”. Gastite **recommends**  
> that all continuous metallic systems be  
> bonded and grounded. The owner should confirm  
> with an electrical or construction specialist that  
> each continuous metallic system in a structure  
> has been bonded and grounded by an electrical  
> professional in accordance with local building  
> codes. This should include, but is not limited to  
> metallic chimney liners, metallic appliance vents,  
> metallic ducting and piping,
> 
> [Direct Bonding of Standard (Yellow) CSST](http://www.csstsafety.com/Images/CSST-Direct-Bonding-Tech-Bulletin.pdf)
> 
> [Design and Installation Guide](http://www.ct.gov/dcs/lib/dcs/office_of_education_and_data_management_files/d&tr.-gastite_di_guide.pdf) Rather large pdf
> 
> CSST Safety Solution]([http://www.csstsafety.com/CSST-solution.html](http://www.csstsafety.com/CSST-solution.html)) - Bonding and Grounding

Gastite can recommend anything they want. That does not make it part of the NEC, nor is it part of the listing and labeling.

---

<div class="post-metadata">

**Author:** ![rjude](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rjude/32/168350_2.png) [@rjude](https://forum.nachi.org/u/rjude)\
**Post date:** [November 12, 2012, 11:52pm UTC](https://forum.nachi.org/t/bonding-of-csst/73276/24 "2012-11-12T23:52:39Z")

</div>

the local gas company told me “no, they do not require, nor recommend gas lines at all to be bonded”

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [November 13, 2012, 12:24am UTC](https://forum.nachi.org/t/bonding-of-csst/73276/25 "2012-11-13T00:24:19Z")

</div>

Well… The gas company governs SQUAT inside your house. If the gas line is likely to become energized then it gets bonded. If section 250.104 takes care of it then done.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [November 13, 2012, 1:33am UTC](https://forum.nachi.org/t/bonding-of-csst/73276/26 "2012-11-13T01:33:28Z")

</div>

> [@Jim\_Port](#):
>
> Gastite can recommend anything they want. That does not make it part of the NEC, nor is it part of the listing and labeling.

That’s why I like using the term Qualified “Person” in my reports.