Looking for a solid answer rather than supposition. Today I ran into an aggregate of box vents toward the upper peak/ridge are on the back half of this hip roof. The roof was replaced in 2020 and was finaled by the AHJ in 2020. Do these box vents appear to be too high to the ridge line? Note, Yes, I am calling out the shingles overlapping the vents in areas, but I am more interested if someone can tell me that they are or are not, not too high on the roof. As always I thank you all for your input.
Looks like Lomanco 770-D roof vents from here.
In my area the common installation defects are improper attachment/sealing and improper roof sheathing hole fabrication.
Good luck with that.
Where are the photo’s from the interior attic space?
The attic was not accessible
I agree, so do they appear too high to the ridge?
I would not call that out, and the FBC states (typically) that upper ventilators shouldn’t be more than 3 feet below the ridge (with exceptions due to obstructions). It doesn’t spec out minimum distance.
They are NOT installed too high on the roof.
Please see Air Vent static roof vent installation instructions item #1.
And, others.
Thanks Dom
The 2 foot ridge board?
If it was a 5 foot ridge would you ask the same question?
They need to be as high as possible to exhaust the hot air.
If they don’t leak there should not be a problem.
If it was signed off by the ahj then it’s not a problem.
Nobody’s going to do anything about it anyways. Unless they are causing an issue.
I concur.
OP. Don’t chase down rabbit holes.
IMO not a problem, but I would want to see the attic structure just in case.
Regardless, I wouldn’t write up those vents based on them being installed to close to the ridge.
I would write them up that they are a tad bit to high as portions of the ridge line shingles overlap the vents which can lead to moisture issues. They should be slightly lower so the shingles do not lift up as they currently are.
I think the main question to ask, is there a defect observed? Is the aggregate of vents causing moisture intrusion? Are there any observable weak spots around the area? Having been a roofer for several years, I would not recommend installing them that closely, but as a home inspector, if you aren’t observing active water penetration, there does not seem to be a defect.
Exactly, this design of roof are very common in the North, and it is surprising how often those sections of the roofing (airflow) are blocked/restricted by framing details!
If one were to take the standards of practice into account or consider the purpose of a res home inspection, how would this non issue affect the value of the property or the safety of the occupants? I totally agree with the previous “rabbit hole” comment. Remember an HI is NOT a code compliance inspection. Just MHO. Cheers