Question, When running additional circuits, in the basement with a drop ceiling, can you just secure to bottom of floor joist. Or should you drill through joist. Thanks
– “I have not failed I have just found a thousand way’s that didn’t work” Thomas Edison.
Originally Posted By: dedwards This post was automatically imported from our archived forum.
Typically, we see most installed with electricians staples. (not to be confused with fencing staples, it makes a difference) Much easier to install and no drilling
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
Ok on running boards
334.15(C) In Unfinished Basements. Where the cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards.