Good advice Jeff. BTW, I enjoy reading your posts and feel fortunate that you were kind enough to reply to mine today. Are you working on Memorial Day? I have two inspections.
Originally Posted By: bbadger This post was automatically imported from our archived forum.
I am glad you went on to point out that this is a sub panel, as I noticed the missing MBJ (main bonding jumper)
![](upload://z9Mxy8AHGXcdF5jgZsBf6kWlkic.jpeg)
If this was the service panel the bonding screw would be installed in the open hole on this neutral bar.
Strictly speaking we are supposed to use the grounding bar listed on the panel cover and mount it where it is made to go.
That said as long as it is a grounding bar and it is securely mounted electrical inspectors in my area will accept it.
The 125 amp breaker at the meter determines the size feeder to this unit, the 150 amp main breaker in the unit is simply being used as a switch for a local disconnecting means.
-- Bob Badger