Originally Posted By: ddivito
This post was automatically imported from our archived forum.



I saw a main service panel today that had a neutral/bare grounding wires on one busbar that was properly bonded to the enclosure. There was also a busbar on the enclosure that had a few bare grounding wires on it as well. Does a ground connecton made through the enclosure back through the bonding screw to the grounding electrode work well enough?


Originally Posted By: jpope
This post was automatically imported from our archived forum.



A bonding strap or bar should be used to bond bus bars.



Jeff Pope


JPI Home Inspection Service


“At JPI, we’ll help you look better”


(661) 212-0738

Originally Posted By: ddivito
This post was automatically imported from our archived forum.



there was proper bonding


Originally Posted By: jpope
This post was automatically imported from our archived forum.



Bus to bus, or bus to box?



Jeff Pope


JPI Home Inspection Service


“At JPI, we’ll help you look better”


(661) 212-0738

Originally Posted By: ddivito
This post was automatically imported from our archived forum.



proper bonding is bus to box which it was, but that is not the question


Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



jpope wrote:
Bus to bus, or bus to box?


Dennis, I must have also mis-interpreted your question because I thought as Jeff did. Can you decribe it again a bit differently?


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



ddivito wrote:
I saw a main service panel today that had a neutral/bare grounding wires on one busbar that was properly bonded to the enclosure. There was also a busbar on the enclosure that had a few bare grounding wires on it as well. Does a ground connecton made through the enclosure back through the bonding screw to the grounding electrode work well enough?



U/L says it works but I like a fat wire (250.66 size) between the bus with the grounded service connector and the ground bus for my main bonding jumper. I have even heard it said that the attaching screws can't be the only way you bond a grounding bus but the manufacturer says it is OK.
Bonding the neutral bus to the can is either going to be a strap or a green hex head screw.
If you also run a wire to the grounding bus you triple the contact points to the can.
This still has to be a suggestion, not "code"