WTF - Really not sure what to say about this.
There’s a lot going on there.
Example:
A class-A metal chimney pipe was installed adjacent to and uphill of a large masonry chimney. This presents a maintenance problem against roof leakage as well as may create a drafting issue with the chimneys being so close together.
Recommend NFPA level 2 chimney inspections for consideration of safe operation before use.
Not sure if I agree there is a drafting issue. But, for sure that is a flashing nightmare.
Hi, William.
I hope you do not mind me observing and writing some defects and deficiencies.
This is what I would put in my report.
2 Chimneys. 1: Stone Masonry Chimney. 1: Insulated Metal, Stainless steel, chimney pipe.
A: Stone masonry chimney defects and deficiencies.
No roof deck chimney Apron, Step, Counter or Headwall flashings.
Cement crown too short. Crown does not appear sloped to disperse rain water and snow/ice melt liquid from the poured concrete crown.
B: Insulated Stainless steel chimney flue pipe defects and deficiencies.
Typically Metal chimneys more than 5’ tall above the roof require bracing. No diagonal brace.
Poor Stone masonry chimney clearance. The Insulated Stainless steel chimney flue pipe flashing is butted against the uphill portion of the Stone masonry chimney where a head wall flashing would be placed.
The storm collar is in direct contact with the uphill portion of the Stone masonry chimney stones.
Suspect: Poor drafting. Soot stains below the Metal chimney Cap.
Hope that helps.