# Clearance?

**URL:** <https://forum.nachi.org/t/clearance/181197>\
**Category:** Public Archive\
**Created:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197 "2004-12-21T00:00:00Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/1 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: Matthew Metzger**  
**This post was automatically imported from our archived forum.**

* * *
  
Not enough clearance here, needs to be atleast an inch. How is it wrote up, state the improper clearance to combustibles and recommend repairs be licensed HVAC contractor?  
  
  
Thanks Matt  
  
[Image: [http://www.nachi.org/bbsystem/usrimages/I/IMG\_0156\_Small.JPG](http://www.nachi.org/bbsystem/usrimages/I/IMG_0156_Small.JPG) ]  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/2 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: jpeck**  
**This post was automatically imported from our archived forum.**

* * *
  

| **Matthew Metzger wrote:** |
| Not enough clearance here, needs to be atleast an inch. How is it wrote up, state the improper clearance to combustibles and recommend repairs be licensed HVAC contractor?  
  
Thanks Matt  
  
[Image: [http://www.nachi.org/bbsystem/usrimages/I/IMG\_0156\_Small.JPG](http://www.nachi.org/bbsystem/usrimages/I/IMG_0156_Small.JPG) ] |

   
   
Basically, yes, like you said.  

* * *
   

--  
Jerry Peck  
South Florida

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/3 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: cradan**  
**This post was automatically imported from our archived forum.**

* * *
  
Matthew, is that vent pipe single-wall, or B-type (multi-wall) vent pipe? Clearance-to-combustible requirements differ, depending on pipe installation.  

* * *
  

–  
Chris  
  
  
[http://www.inspect4me.com](http://www.inspect4me.com)  
  
  
Chicago Illinois Home Inspections

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/4 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: Matthew Metzger**  
**This post was automatically imported from our archived forum.**

* * *
  
Chris it’s B Vent.  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/5 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: tallen**  
**This post was automatically imported from our archived forum.**

* * *
  
B-vent requires 1" of clearence, Single wall is 6"  
  
  
  
Wright it up!  

* * *
  

--  
I have put the past behind me,  
where , however, it now sits, making rude remarks.  
  
[www.whiteglovehomeinspections.net](http://www.whiteglovehomeinspections.net)  
  
30 Oct 2003-- 29 Nov2005

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/6 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: jonofrey**  
**This post was automatically imported from our archived forum.**

* * *
  
The idiot that installed that vent stack should have cut that rafter and left the ends hangin’. That would cure his clearance problem! ![icon_wink.gif](https://global.discourse-cdn.com/internachi/original/3X/c/7/c780e395059a8e0dcd430a029eb634655c8f86e8.gif)  
  
  
That's the way I see 'em done down here.   

* * *
  

--  
Inspection Nirvana!  
  
We're NACHI. Get over it.

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/7 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: phinsperger**  
**This post was automatically imported from our archived forum.**

* * *
  
Earthquake shifted vent over 1". Recommend refraining from having earthquakes. ![icon_lol.gif](https://global.discourse-cdn.com/internachi/original/3X/f/9/f9d92d0317184e74bf4af4a8b30106d80406969c.gif)  

* * *
  

–  
.

  
  
Paul Hinsperger  
Hinsperger Inspection Services  
Chairman - NACHI Awards Committee  
[Place your Award Nominations  
here !](http://www.nachi.org/awards-nomination.htm)

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 21, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/8 "2004-12-21T00:00:00Z")

</div>

**Originally Posted By: tallen**  
**This post was automatically imported from our archived forum.**

* * *
  
I see this problem all the time. B vent up against combustible material. They all complain, but I win. ![icon_biggrin.gif](https://global.discourse-cdn.com/internachi/original/3X/8/3/83717c74df9b0ce202453063bc4f11baf0ee6b8a.gif)  

* * *
  

–  
I have put the past behind me,  
  
  
where , however, it now sits, making rude remarks.

  
[www.whiteglovehomeinspections.net](http://www.whiteglovehomeinspections.net)  
  
30 Oct 2003-- 29 Nov2005

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 22, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/9 "2004-12-22T00:00:00Z")

</div>

**Originally Posted By: Blaine Wiley**  
**This post was automatically imported from our archived forum.**

* * *
  

| **Matthew Metzger wrote:** |
| How is it wrote up |

   
   
Hopefully with proper English! ![icon\_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon\_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 22, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/10 "2004-12-22T00:00:00Z")

</div>

**Originally Posted By: dbowers**  
**This post was automatically imported from our archived forum.**

* * *
  
because of writing up things like this, you get called a “NITPICKER” by realtors AND every year for 25 years I’ve seen less and less realtors REFER you to their buyer AND refer the “Good Little Home Inspectors” that don’t write this type of thing up.  
  
  
Oh well, too late in the game to change now.  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [December 22, 2004, 12:00am UTC](https://forum.nachi.org/t/clearance/181197/11 "2004-12-22T00:00:00Z")

</div>

**Originally Posted By: Blaine Wiley**  
**This post was automatically imported from our archived forum.**

* * *
  

| **dbowers wrote:** |
| I've seen it for 25 years. I 've wrote it up for 25 years. I've never seen it get repaired in 25 years. I've never seen it be a problem in 25 years.  
  
AND because of writing up things like this, you get called a "NITPICKER" by realtors AND every year for 25 years I've seen less and less realtors REFER you to their buyer AND refer the   
  
Oh well, too late in the game to change now. |

   
   
I guess my next 15 years are just going to be downhill then. I've been writing things up like that for my first ten years, and have never been called a nit picker, and have no problem with referrals. I've written them up, write them up now, and will write them in the future. The guys I've been aware of who are called picky are the ones who write up things like paint missing on the tops of doors, squeaky hinges, peeling wallpaper, bathroom cabinet drawers that are a little sticky, etc.  
   
Must just be your glowing personality, Dan ![icon\_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon\_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon\_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon\_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)  

* * *
