Was performing an inspection. Was letting the oven heat up to check CO and turned on hot water. CO monitor started going off. Checked oven and it was fine. Hot water was registering anywhere from 10-110ppm, nothing with cold water. Checked multiple sinks all the same. House was vacant so I ran the hot water for 15 minutes, still reading CO… House was on a well and by the stains on the exterior appears to be pretty hard water. I use a Testo 317-3. I checked at my home and no readings at any sinks.
Possible false alarm causes…
Here are a few situations that may cause a carbon monoxide “false alarm:”
The carbon monoxide alarm needs to be relocated.
Carbon monoxide alarms should be located 15-20 feet away from all fossil fuel burning sources like furnaces and stoves.
Sounds to me like your oven is the issue. I assume you were testing ambient air, not undiluted oven flue CO.
For your personal CO alarm (edit), the first alarm level of ambient air CO is at 9ppm. 30ppm is the next level of alarm, requiring terminating the test. At 70ppm ambient air CO, exit the building.
I perform appliance undiluted CO testing during energy audits and test inside the throat of the oven at steady state. The first CO action level for an oven is 100ppm measured inside the oven throat (undiluted CO level). Recently I had an oven test at over 800ppm and still rising when I turned it off.
I think you misidentified the source of your CO; it’s probably the oven, not the water. In addition, was the water heater non electric and atmospherically vented? An atmospheric vented water heater could be another source of your CO.
No matter what, this is a serious issue that your client needs to know about and have fixed prior to occupancy. The risk of death is present in this home.