All the info I have seen on csst just shows a bond where the csst connects to the black pipe. is that one bond good for all of these connections or should there be jumpers at all the breaks? Excuse my ignorance.

 ![DSCN0054](https://global.discourse-cdn.com/internachi/original/3X/0/a/0aeee9f034bb27da437339cd46e02819ddcc25f4.jpeg)

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [December 28, 2019, 2:09am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/2 "2019-12-28T02:09:32Z")

</div>

It needs to be bonded in accordance with the manufacturer’s specification. Typically it’s directly bonded to the iron pipe.

---

<div class="post-metadata">

**Author:** ![esantiago5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/esantiago5/32/181562_2.png) [@esantiago5](https://forum.nachi.org/u/esantiago5)\
**Post date:** [December 28, 2019, 4:38am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/3 "2019-12-28T04:38:01Z")

</div>

It breaks ground, could be bonded 5 feet from berried water main, with continued conduit. Picture seem to show it breaks continuity. But then again, that is a weird source of ground their should be a GEC clamp closer to the panel to provide the carry the ground over. I think I just confused my self, please correct me if I am wrong.

On the other hand, I think that type of clamp would only bond a low voltage. (Telephone, satellites dish/cable etc.)

---

<div class="post-metadata">

**Author:** ![jmilby](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmilby/32/57038_2.png) [@jmilby](https://forum.nachi.org/u/jmilby)\
**Post date:** [December 28, 2019, 4:39am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/4 "2019-12-28T04:39:41Z")

</div>

The bond is to the black iron piping, not directly on the CSST.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [December 28, 2019, 3:37pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/5 "2019-12-28T15:37:37Z")

</div>

Looks to me like those short nipples, tee’s and couplings were just used to connect several runs of CSST together. The bonding is typically done where it enters the structure.

---

<div class="post-metadata">

**Author:** ![sfrakes](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sfrakes/32/59523_2.png) [@sfrakes](https://forum.nachi.org/u/sfrakes)\
**Post date:** [December 28, 2019, 3:44pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/6 "2019-12-28T15:44:16Z")

</div>

[Technical\_Bulletin\_WF2008 Wardflex.pdf](https://forum.nachi.org/uploads/short-url/cVoXJFWto0Vfr2OLdhJSdxfJ95S.pdf) (274.1 KB)

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [December 28, 2019, 3:47pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/7 "2019-12-28T15:47:03Z")

</div>

Someone please show me where it is bonded at? I can’t seem to see it? 😁

 ![DSCN0054](https://global.discourse-cdn.com/internachi/original/3X/0/a/0aeee9f034bb27da437339cd46e02819ddcc25f4.jpeg)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 28, 2019, 4:47pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/8 "2019-12-28T16:47:25Z")

</div>

> [@rlewis5](#):
>
> Someone please show me where it is bonded at? I can’t seem to see it? 😁

Isn’t that plumber’s strap good enough, Roy? 🙄😳🤨

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [December 28, 2019, 4:48pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/9 "2019-12-28T16:48:56Z")

</div>

> [@lkage](#):
>
> Isn’t that plumber’s strap good enough, Roy?

I suppose so! NOT!

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [December 28, 2019, 5:31pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/10 "2019-12-28T17:31:35Z")

</div>

There’s no bonding in the picture.

---

<div class="post-metadata">

**Author:** ![dwigger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dwigger/32/58670_2.png) [@dwigger](https://forum.nachi.org/u/dwigger)\
**Post date:** [December 28, 2019, 5:37pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/11 "2019-12-28T17:37:47Z")

</div>

I don’t know about Texas, but in Oklahoma, bonding is only required for CSST with yellow vinyl sleeve.

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [December 28, 2019, 5:39pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/12 "2019-12-28T17:39:32Z")

</div>

Bonding is required for all metallic piping systems.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [December 28, 2019, 5:40pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/13 "2019-12-28T17:40:20Z")

</div>

> [@cevans](#):
>
> There’s no bonding in the picture

I know …LOL!

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 28, 2019, 7:59pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/14 "2019-12-28T19:59:34Z")

</div>

> [@cevans](#):
>
> There’s no bonding in the picture.

> [@rlewis5](#):
>
> I know …LOL!

I know, too. LOL! …just joking with Roy.

---

<div class="post-metadata">

**Author:** ![sfrakes](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sfrakes/32/59523_2.png) [@sfrakes](https://forum.nachi.org/u/sfrakes)\
**Post date:** [December 28, 2019, 9:48pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/15 "2019-12-28T21:48:46Z")

</div>

David is correct. Only yellow vinyl coated pipe has to be bonded.  
Most newer black “Flashshield” does not.

---

<div class="post-metadata">

**Author:** ![mparks2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks2/32/172915_2.png) [@mparks2](https://forum.nachi.org/u/mparks2)\
**Post date:** [December 28, 2019, 11:48pm UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/16 "2019-12-28T23:48:13Z")

</div>

FALSE!

Read what the manufacturer says:

 ![Screenshot_20191228-184532](https://global.discourse-cdn.com/internachi/original/3X/0/2/0252ec68a9842c8a79581aa14b92a2e48fd3f2fc.jpeg)

---

<div class="post-metadata">

**Author:** ![sfrakes](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sfrakes/32/59523_2.png) [@sfrakes](https://forum.nachi.org/u/sfrakes)\
**Post date:** [December 29, 2019, 12:12am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/17 "2019-12-29T00:12:19Z")

</div>

Um, true.  
The manufacturers instructions indicate no additional bonding required.  
The AHJ appears to have the final say and have found several that don’t even require it with the yellow coated pipe which is a separate discussion altogether.

---

<div class="post-metadata">

**Author:** ![mparks2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks2/32/172915_2.png) [@mparks2](https://forum.nachi.org/u/mparks2)\
**Post date:** [December 29, 2019, 12:48am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/18 "2019-12-29T00:48:00Z")

</div>

> [@sfrakes](#):
>
> Um, true

FALSE

“is to be bonded in accordance with the National Electrical Code NFPA 70 Article 250.104, Canadian Electrical Code, CSA-C22.1, in the same manner as the minimum requirements for rigid metal piping”

 ![Screenshot_20191228-194708](https://global.discourse-cdn.com/internachi/original/3X/a/0/a0dc05e5832e3815a8a65db291e9cb6b7e67d305.jpeg)

---

<div class="post-metadata">

**Author:** ![dhawley1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhawley1/32/59611_2.png) [@dhawley1](https://forum.nachi.org/u/dhawley1)\
**Post date:** [December 29, 2019, 12:48am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/19 "2019-12-29T00:48:48Z")

</div>

Beat me to it.

---

<div class="post-metadata">

**Author:** ![mparks2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks2/32/172915_2.png) [@mparks2](https://forum.nachi.org/u/mparks2)\
**Post date:** [December 29, 2019, 12:50am UTC](https://forum.nachi.org/t/csst-bonding-question-2/159457/20 "2019-12-29T00:50:03Z")

</div>

> [@dhawley1](#):
>
> Beat me to it

I’ll slow down!