# Cutler Hammer panel double taps

**URL:** <https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144>\
**Category:** Electrical Inspections\
**Created:** [September 12, 2019, 9:57pm UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144 "2019-09-12T21:57:18Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![acox](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/acox/32/57038_2.png) [@acox](https://forum.nachi.org/u/acox)\
**Post date:** [September 12, 2019, 9:57pm UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/1 "2019-09-12T21:57:18Z")

</div>

Inspected a home built in 2003, the Cutler hammer panel had 2 circuits double-tapped. These are both CH 20 amp tandem breakers. In the pic, the top half of the tandem is doubled. It looks to me there is a “saddle” clamp that could hold 2 conductors, but the conductors are actually under the screw, not in the clamp. I can’t determine if this is rated for double conductors, if it’s installed correctly, or if I’m just seeing things.

 ![IMG_8604](https://global.discourse-cdn.com/internachi/original/3X/9/a/9a0641dd9c25cfe2ab8bb808aced1ec437b271ec.jpeg) ![IMG_8603](https://global.discourse-cdn.com/internachi/original/3X/3/1/3139f2e7b7c142551455c358a188d26060063ef2.jpeg)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [September 12, 2019, 10:06pm UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/2 "2019-09-12T22:06:17Z")

</div>

This is what it looks like, Andy:

 ![two%20wire%20breaker%20](https://global.discourse-cdn.com/internachi/original/3X/d/a/daf357ba1a25ba5ae4246ee854a1cc60049d4111.jpeg)

and

 ![Square-D-Breaker](https://global.discourse-cdn.com/internachi/original/3X/a/7/a744ae211f331585b5e05bd64387f8c066ddffc0.jpeg)

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [September 12, 2019, 11:06pm UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/3 "2019-09-12T23:06:36Z")

</div>

What’s the big deal?  
It’s a flippin’ double tapped breaker that ain’t designed for it… Yep!  
Man ! Well ! We will wait until next week for the same question.  
Write it up!  
Wow!

---

<div class="post-metadata">

**Author:** ![rkenney](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rkenney/32/405447_2.png) [@rkenney](https://forum.nachi.org/u/rkenney)\
**Post date:** [September 13, 2019, 12:01am UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/4 "2019-09-13T00:01:45Z")

</div>

So you called out the shared neutral above it. Don’t know that it is, but it certainly looks that way.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [September 13, 2019, 12:16am UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/5 "2019-09-13T00:16:41Z")

</div>

> [@acox](#):
>
> Inspected a home built in 2003, the Cutler hammer panel had 2 circuits double-tapped. These are both CH 20 amp tandem breakers. In the pic, the top half of the tandem is doubled. It looks to me there is a “saddle” clamp that could hold 2 conductors, but the conductors are actually under the screw, not in the clamp. I can’t determine if this is rated for double conductors, if it’s installed correctly, or if I’m just seeing things.

CB not listed for two conductors, write it up. 🕶

---

<div class="post-metadata">

**Author:** ![dmontgomery5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dmontgomery5/32/174610_2.png) [@dmontgomery5](https://forum.nachi.org/u/dmontgomery5)\
**Post date:** [September 13, 2019, 12:36am UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/6 "2019-09-13T00:36:14Z")

</div>

But it says 2 pole right on 😂

yes thats a joke

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [September 13, 2019, 1:21am UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/7 "2019-09-13T01:21:37Z")

</div>

With Cutler Hammer breakers the plastic foot breaker is listed for two conductors. The older metal feet breakers are not.

---

<div class="post-metadata">

**Author:** ![acox](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/acox/32/57038_2.png) [@acox](https://forum.nachi.org/u/acox)\
**Post date:** [September 13, 2019, 2:24am UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/8 "2019-09-13T02:24:22Z")

</div>

Thank you - That’s the answer I needed. I had not heard or read that about the CH breakers before.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [September 13, 2019, 9:15am UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/9 "2019-09-13T09:15:27Z")

</div>

According to CH the BD2020 is listed for one conductor:

> **[191b8376-721b-4039-9c30-c9871143f3f3.pdf](https://images.homedepot-static.com/catalog/pdfImages/19/191b8376-721b-4039-9c30-c9871143f3f3.pdf)**
>
> 82.56 KB

---

<div class="post-metadata">

**Author:** ![gwells](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gwells/32/417638_2.png) [@gwells](https://forum.nachi.org/u/gwells)\
**Post date:** [September 14, 2019, 2:51pm UTC](https://forum.nachi.org/t/cutler-hammer-panel-double-taps/156144/10 "2019-09-14T14:51:11Z")

</div>

Wait until next week? If is is late Saturday night maybe we will have to wait until next week.