# Double tap breaker question

**URL:** <https://forum.nachi.org/t/double-tap-breaker-question/254321>\
**Category:** Electrical Inspections\
**Created:** [March 28, 2025, 4:58pm UTC](https://forum.nachi.org/t/double-tap-breaker-question/254321 "2025-03-28T16:58:50Z")\
**Posts on this page:** 1\
**Page:** 2

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [April 7, 2025, 1:44pm UTC](https://forum.nachi.org/t/double-tap-breaker-question/254321/21 "2025-04-07T13:44:44Z")

</div>

> [@mroberts21](#):
>
> Sorta. NEC 300.14 says 6 inches of free conductor(Yes, I had to look up the cite, but I know it’s 6 inches). That seems a bit short. Also as long as it’s not a MWBC sharing a neutral that can be overloaded, it’d be ok too..

The 6" does not apply to a pigtail. Also 300.14 says nothing about be applicable to panel cabinets.