# Double Tap or Not?

**URL:** <https://forum.nachi.org/t/double-tap-or-not/99129>\
**Category:** Florida and SUNachi Inspectors\
**Created:** [August 12, 2015, 3:32am UTC](https://forum.nachi.org/t/double-tap-or-not/99129 "2015-08-12T03:32:52Z")\
**Posts on this page:** 20\
**Page:** 4

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [August 15, 2015, 1:06am UTC](https://forum.nachi.org/t/double-tap-or-not/99129/61 "2015-08-15T01:06:23Z")

</div>

> [@kjones5](#):
>
> By the way oh great Inspection Guru, I saw you have 31 years experience in construction .

[http://www.creativityinstitute.com/ProductImages/blocks/CF12inch14.jpg](http://www.creativityinstitute.com/ProductImages/blocks/CF12inch14.jpg)

---

<div class="post-metadata">

**Author:** ![evandeven](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/evandeven/32/373798_2.png) [@evandeven](https://forum.nachi.org/u/evandeven)\
**Post date:** [August 15, 2015, 2:26pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/62 "2015-08-15T14:26:13Z")

</div>

I go on vacation for a week in the Keys, and I see nothing has changed.

A simple question about double-lugging, has morphed into this…again.

To “help” those who wish to be helped, the first code issue is the paint in the panel. Although minor as seen in the picture, nowhere in the NEC does it state how much debris/paint/plaster is permitted in the panel.  
What it does say is the following:

> [@](#):
>
> - 110.12 Mechanical Execution of Work.
> - 
> - Electrical equipment shall be installed in a neat and workmanlike manner.
> 
> - 
> - 
> - (A) Unused Openings. Unused cable or raceway openings in boxes, raceways, auxiliary gutters, cabinets, cutout boxes, meter socket enclosures, equipment cases, or housings shall be effectively closed to afford protection substantially equivalent to the wall of the equipment. Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6 mm (¼ in.) from the outer surface of the enclosure.
> 
> - 
> - 
> - (B) Subsurface Enclosures. Conductors shall be racked to provide ready and safe access in underground and subsurface enclosures into which persons enter for installation and maintenance.
> 
> - 
> - 
> - (C) Integrity of Electrical Equipment and Connections. Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, **shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues.** There shall be no damaged parts that may adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; or deteriorated by corrosion, chemical action, or overheating.

It is up to each inspector to determine “how much” they are willing to accept. I know one inspector and a Seller that are going to “accept” the replacement of the panel in order to avoid a lawsuit. The Buyer of this particular property got a hold of my inspection report for my client who didn’t buy the home and after receiving permission to discuss the report with the new buyer, I informed them of what I found.

The next issue, the combustible material issue, is the fact that whoever installed this panel, did so prior to the drywall being installed and never accounted for the space of the drywall. Now, there is a gap between the cover and the panel box.

When this panel gets changed, at least if I were inspecting it, that would be the recommendation, both issues as well as the damaged label will be corrected.

EVERYONE IS FREE TO DO AS THEY LIKE…

And for those who claim to be doing a safety inspection and don’t mention these items,

The National Electrical Code (NEC), or NFPA 70, is a regionally adoptable standard for the \*\*safe installation of electrical wiring and equipment \*\*in the United States.

Now, back to your regular scheduled bickering…

---

<div class="post-metadata">

**Author:** ![wcollier](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcollier/32/180057_2.png) [@wcollier](https://forum.nachi.org/u/wcollier)\
**Post date:** [August 15, 2015, 3:49pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/63 "2015-08-15T15:49:26Z")

</div>

> [@ccurrins](#):
>
> [http://www.creativityinstitute.com/ProductImages/blocks/CF12inch14.jpg](http://www.creativityinstitute.com/ProductImages/blocks/CF12inch14.jpg)

Looks about right

---

<div class="post-metadata">

**Author:** ![Robert\_R.Sheppard](https://avatars.discourse-cdn.com/v4/letter/r/c6cbf5/32.png) [@Robert\_R.Sheppard](https://forum.nachi.org/u/Robert_R.Sheppard)\
**Post date:** [August 15, 2015, 4:47pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/64 "2015-08-15T16:47:11Z")

</div>

> [@evandeven](#):
>
> I go on vacation for a week in the Keys, and I see nothing has changed.
> 
> A simple question about double-lugging, has morphed into this…again.
> 
> To “help” those who wish to be helped, the first code issue is the paint in the panel. Although minor as seen in the picture, nowhere in the NEC does it state how much debris/paint/plaster is permitted in the panel.  
> What it does say is the following:
> 
> It is up to each inspector to determine “how much” they are willing to accept. I know one inspector and a Seller that are going to “accept” the replacement of the panel in order to avoid a lawsuit. The Buyer of this particular property got a hold of my inspection report for my client who didn’t buy the home and after receiving permission to discuss the report with the new buyer, I informed them of what I found.
> 
> The next issue, the combustible material issue, is the fact that whoever installed this panel, did so prior to the drywall being installed and never accounted for the space of the drywall. Now, there is a gap between the cover and the panel box.
> 
> When this panel gets changed, at least if I were inspecting it, that would be the recommendation, both issues as well as the damaged label will be corrected.
> 
> EVERYONE IS FREE TO DO AS THEY LIKE…
> 
> And for those who claim to be doing a safety inspection and don’t mention these items,
> 
> The National Electrical Code (NEC), or NFPA 70, is a regionally adoptable standard for the \*\*safe installation of electrical wiring and equipment \*\*in the United States.
> 
> Now, back to your regular scheduled bickering…

…he’s a smart man that Eric!

For the second issue:  
[size=4]\*\*\*312.3 Position in Wall. \*\*\*_In walls of concrete, tile, or other noncombustible material, cabinets shall be installed so that the front edge of the cabinet is not set back of the finished surface more than 6 mm (1⁄4 in.). In walls constructed of wood or other combustible material, cabinets shall be flush with the finished surface or project therefrom._[/size]

---

<div class="post-metadata">

**Author:** ![wsiegel](https://avatars.discourse-cdn.com/v4/letter/w/3d9bf3/32.png) [@wsiegel](https://forum.nachi.org/u/wsiegel)\
**Post date:** [August 15, 2015, 4:47pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/65 "2015-08-15T16:47:47Z")

</div>

Eric just told you everything that Robert told you. I think you guys owe him an apology. Just because he tried to make you think a little without actually giving you the answer was no reason for name calling.

---

<div class="post-metadata">

**Author:** ![wcollier](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcollier/32/180057_2.png) [@wcollier](https://forum.nachi.org/u/wcollier)\
**Post date:** [August 15, 2015, 6:15pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/66 "2015-08-15T18:15:46Z")

</div>

> [@wsiegel](#):
>
> Eric just told you everything that Robert told you. I think you guys owe him an apology. Just because he tried to make you think a little without actually giving you the answer was no reason for name calling.

Umm yeah I do not see that happening. You have it all backwards. I think RS owes everyone else an apology. There’s a difference in helping somebody learn something and being a D\*\*\* Head! He’s not the instructor of interNACHI last time I checked and not even a member. I bet you two talk on the phone like little girls thinking of your next move on the board. It is really sad when somebody comes on here starts an argument and then wants an apology. Sounds like ex wife syndrome.

---

<div class="post-metadata">

**Author:** ![Robert\_R.Sheppard](https://avatars.discourse-cdn.com/v4/letter/r/c6cbf5/32.png) [@Robert\_R.Sheppard](https://forum.nachi.org/u/Robert_R.Sheppard)\
**Post date:** [August 15, 2015, 6:27pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/67 "2015-08-15T18:27:35Z")

</div>

> [@wcollier](#):
>
> Umm yeah I do not see that happening. You have it all backwards. I think RS owes everyone else an apology. There’s a difference in helping somebody learn something and being a D\*\*\* Head! He’s not the instructor of interNACHI last time I checked and not even a member. I bet you two talk on the phone like little girls thinking of your next move on the board. It is really sad when somebody comes on here starts an argument and then wants an apology. Sounds like ex wife syndrome.

LOL…

---

<div class="post-metadata">

**Author:** ![kjones5](https://avatars.discourse-cdn.com/v4/letter/k/cc9497/32.png) [@kjones5](https://forum.nachi.org/u/kjones5)\
**Post date:** [August 15, 2015, 7:05pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/68 "2015-08-15T19:05:56Z")

</div>

I saw the drywall and then I saw the paint line next to it. At first glance it looked like the dead front did not even reach the drywall but looking now the paint line is where the panel was masked off for painting. I wasn’t there to take off the dead front so…

All he had to do was say it not be a prick about it like he is. I don’t claim to know it all and I’m willing to learn so I asked what he saw. He replied with childish little games.

He is not on here to help anybody he just wants to belittle EVERYONE to make himself feel good. Pretty pathetic if you ask me.

Give an apology? Not a chance.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [August 15, 2015, 7:09pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/69 "2015-08-15T19:09:00Z")

</div>

> [@wsiegel](#):
>
> Eric just told you everything that Robert told you. I think you guys owe him an apology. Just because he tried to make you think a little without actually giving you the answer was no reason for name calling.

I disagree. I’m very confident most qualified electricians, that weren’t trying to make an extra buck, and home inspectors, would too. Recommending to change out a panel because of a little over spray and a half inch gap between cover and panel is ludicrous. Though both safety issues neither, in this case, warrant a brand new panel. There are much cheaper ways to solve both problems.

---

<div class="post-metadata">

**Author:** ![kjones5](https://avatars.discourse-cdn.com/v4/letter/k/cc9497/32.png) [@kjones5](https://forum.nachi.org/u/kjones5)\
**Post date:** [August 15, 2015, 7:09pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/70 "2015-08-15T19:09:41Z")

</div>

I saw the over spray in the panel and on the neutral conductor but if that is all there is are you really going to call it out?

So what are the other two problems or are we still playing the game?

---

<div class="post-metadata">

**Author:** ![Robert\_R.Sheppard](https://avatars.discourse-cdn.com/v4/letter/r/c6cbf5/32.png) [@Robert\_R.Sheppard](https://forum.nachi.org/u/Robert_R.Sheppard)\
**Post date:** [August 15, 2015, 7:18pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/71 "2015-08-15T19:18:15Z")

</div>

Go back to page one, you tell me who started with the smart comments and name-calling?

Little children complacent with doing the very least required…then blaming the person who pops their little bubble of comfort.

It’s partly my fault, I though we were all grown azz men here…I was sorely mistaken.

---

<div class="post-metadata">

**Author:** ![wcollier](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcollier/32/180057_2.png) [@wcollier](https://forum.nachi.org/u/wcollier)\
**Post date:** [August 15, 2015, 7:46pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/72 "2015-08-15T19:46:21Z")

</div>

> [@ccurrins](#):
>
> I disagree. I’m very confident most qualified electricians, that weren’t trying to make an extra buck, and home inspectors, would too. Recommending to change out a panel because of a little over spray and a half inch gap between cover and panel is ludicrous. Though both safety issues neither, in this case, warrant a brand new panel. There are much cheaper ways to solve both problems.

I agree. Good way to get run out of town on the silly wagon

---

<div class="post-metadata">

**Author:** ![evandeven](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/evandeven/32/373798_2.png) [@evandeven](https://forum.nachi.org/u/evandeven)\
**Post date:** [August 15, 2015, 8:09pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/73 "2015-08-15T20:09:15Z")

</div>

> [@ccurrins](#):
>
> I disagree. I’m very confident most qualified electricians, that weren’t trying to make an extra buck, and home inspectors, would too. Recommending to change out a panel because of a little over spray and a half inch gap between cover and panel is ludicrous. Though both safety issues neither, in this case, warrant a brand new panel. There are much cheaper ways to solve both problems.

Unfortunately, the manufacturer disagrees with you:

> [@](#):
>
> Good Afternoon, Mr. Van De Ven,
> 
> If any contaminant has entered the panel that cannot be removed by  
> simply vacuuming or wiping with a clean lint-free cloth, then we would  
> recommend replacing the interior of the panel. If paint, or some other  
> contaminant, has left labeling that is affixed to the panel unreadable,  
> then we would recommend replacing the complete panel. We comment in our  
> current design of panel:  
> “Allowing petroleum based paint, solvents or spray to contact the  
> non-metallic parts of this product may adversely affect user safety and  
> impair reliability”.  
> This is due to the chemical reaction of the petroleum base paint or  
> solvent to the insulating bases used in the panel.
> 
> I am not familiar with the “Groomers Goop”. However, our stance would  
> remain the same as stated above. If a consumer were to utilize this pet  
> grooming product, it would be without the Square D Company’s consent or  
> approval.
> 
> I hope that this will help with your issues. Please let me know if you  
> would need anything further.
> 
> Regards,  
> Rick Snapp  
> Product Technical Support Group  
> Square D Company - Lexington Plant  
> E-Mail: [rick.snapp@us.schneider-electric.com](mailto:rick.snapp@us.schneider-electric.com)"

I emailed several manufacturers to get the correct answer. They were all consistent in the fact that the paint/debris wouldn’t be there in the first place if the electrician who installed the panel used the perforated cut out found on the back of the package the load center came in, and, that modifying their panels in any way violates their warranty and technically renders it non-UL compliant.

As I said, everyone is free to do what they like.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [August 15, 2015, 8:17pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/74 "2015-08-15T20:17:12Z")

</div>

Good grief fellas.

If you think a little overspray in a panel is cause for concern…

It’s a judgment call.

Please use your own judgement.

---

<div class="post-metadata">

**Author:** ![Robert\_R.Sheppard](https://avatars.discourse-cdn.com/v4/letter/r/c6cbf5/32.png) [@Robert\_R.Sheppard](https://forum.nachi.org/u/Robert_R.Sheppard)\
**Post date:** [August 15, 2015, 8:40pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/75 "2015-08-15T20:40:35Z")

</div>

Two different approaches…same result. Denial and refusal to see the truth.

After kissing realtors butts for so long, it just gets impossible to see anything that doesn’t resemble the northern side of a south bound camel. Start reporting these issues and watch the referrals go away…

---

<div class="post-metadata">

**Author:** ![wsiegel](https://avatars.discourse-cdn.com/v4/letter/w/3d9bf3/32.png) [@wsiegel](https://forum.nachi.org/u/wsiegel)\
**Post date:** [August 15, 2015, 8:56pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/76 "2015-08-15T20:56:41Z")

</div>

> [@wcollier](#):
>
> Again, you don’t know what you are talking about skippy. My website is the same. Look at the trademark dates and stop grasping at straws.

Actually Wayne, you did change your web site. You used to have a septic certification listed, It is no longer there.

---

<div class="post-metadata">

**Author:** ![wsiegel](https://avatars.discourse-cdn.com/v4/letter/w/3d9bf3/32.png) [@wsiegel](https://forum.nachi.org/u/wsiegel)\
**Post date:** [August 15, 2015, 9:11pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/77 "2015-08-15T21:11:32Z")

</div>

> [@mlarson](#):
>
> Good grief fellas.
> 
> If you think a little overspray in a panel is cause for concern…
> 
> It’s a judgment call.
> 
> Please use your own judgement.

How can it be a judgement call when the manufactures issued a letter saying tht it is not. They take precedence. That being said you guys need to go back and read this thread, You are the ones that started the name calling. Robert was right in everything he said. He just did not want to give you the answer right away. He thought maybe you would research it a little. But unfortunately no one wants to do a little work. Everyone wants instant gratification and have everything handed to them. As far as attiudes, I used to be a member. The day i did not renew and started posting the same things as I always did, the name calling began. I am glad you guys stict together. But just because someone is not a member of your organiztion does not mean that they do not care about the industry or is unwililng to help. I can bet you that if Robert paid the dues he would be treated differently.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 15, 2015, 9:30pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/78 "2015-08-15T21:30:14Z")

</div>

> [@evandeven](#):
>
> Unfortunately, the manufacturer disagrees with you:
> 
> > [@](#):
> >
> > Good Afternoon, Mr. Van De Ven,
> > 
> > If any contaminant has entered the panel that cannot be removed by  
> > simply vacuuming or wiping with a clean lint-free cloth, then we would  
> > recommend replacing the interior of the panel. If paint, or some other  
> > contaminant, has left labeling that is affixed to the panel unreadable,  
> > then we would recommend replacing the complete panel. We comment in our  
> > current design of panel:  
> > “Allowing petroleum based paint, solvents or spray to contact the  
> > **non-metallic parts** of this product may adversely affect user safety and  
> > impair reliability”.  
> > This is due to the chemical reaction of the petroleum base paint or  
> > solvent to the insulating bases used in the panel.
> > 
> > I am not familiar with the “Groomers Goop”. However, our stance would  
> > remain the same as stated above. If a consumer were to utilize this pet  
> > grooming product, it would be without the Square D Company’s consent or  
> > approval.
> > 
> > I hope that this will help with your issues. Please let me know if you  
> > would need anything further.
> > 
> > Regards,  
> > Rick Snapp  
> > Product Technical Support Group  
> > Square D Company - Lexington Plant  
> > E-Mail: [rick.snapp@us.schneider-electric.com](mailto:rick.snapp@us.schneider-electric.com)"
> 
> I emailed several manufacturers to get the correct answer. They were all consistent in the fact that the paint/debris wouldn’t be there in the first place if the electrician who installed the panel used the perforated cut out found on the back of the package the load center came in, and, that modifying their panels in any way violates their warranty and technically renders it non-UL compliant.
> 
> As I said, everyone is free to do what they like.

Red **BOLD** highlighted above is a KEY ELEMENT to the statement!!! The INTENT of the restriction is to protect the WORKING COMPONENTS of the assembly. Obviously a damaged label replacement is required if not easily readable… for SAFETY!

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [August 15, 2015, 10:28pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/79 "2015-08-15T22:28:03Z")

</div>

> [@wsiegel](#):
>
> How can it be a judgement call when the manufactures issued a letter saying tht it is not. They take precedence. That being said you guys need to go back and read this thread, You are the ones that started the name calling. Robert was right in everything he said. He just did not want to give you the answer right away. He thought maybe you would research it a little. But unfortunately no one wants to do a little work. Everyone wants instant gratification and have everything handed to them. As far as attiudes, I used to be a member. The day i did not renew and started posting the same things as I always did, the name calling began. I am glad you guys stict together. But just because someone is not a member of your organiztion does not mean that they do not care about the industry or is unwililng to help. I can bet you that if Robert paid the dues he would be treated differently.

So you would would call out minor overspray. Really?

Like I said its a judgment call.

---

<div class="post-metadata">

**Author:** ![wcollier](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcollier/32/180057_2.png) [@wcollier](https://forum.nachi.org/u/wcollier)\
**Post date:** [August 15, 2015, 10:37pm UTC](https://forum.nachi.org/t/double-tap-or-not/99129/80 "2015-08-15T22:37:07Z")

</div>

> [@wsiegel](#):
>
> Actually Wayne, you did change your web site. You used to have a septic certification listed, It is no longer there.

It is still there. It’s in the Video…not that it should matter