# Double tapped minis

**URL:** <https://forum.nachi.org/t/double-tapped-minis/196015>\
**Category:** Misc. Discussion\
**Created:** [March 31, 2021, 9:57pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015 "2021-03-31T21:57:58Z")\
**Posts on this page:** 16\
**Page:** 1

<div class="post-metadata">

**Author:** ![jwood22](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jwood22/32/179475_2.png) [@jwood22](https://forum.nachi.org/u/jwood22)\
**Post date:** [March 31, 2021, 9:57pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/1 "2021-03-31T21:57:58Z")

</div>

I did a quick Google search but was unable to find a definitive answer. Can mini split breakers be double-tapped? It seems to me, they shouldn’t be. These breakers did not appear to be designed to except two wires. Any input is greatly appreciated. Thanks guys!

 ![image](https://global.discourse-cdn.com/internachi/original/3X/1/4/14763f7da7bd7ffa65f0560a2cec69794d052762.jpeg) ![image](https://global.discourse-cdn.com/internachi/original/3X/0/e/0eff417de183783e4b1f382e403b371d58c9c60e.jpeg)

---

<div class="post-metadata">

**Author:** ![dhodges](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhodges/32/167435_2.png) [@dhodges](https://forum.nachi.org/u/dhodges)\
**Post date:** [March 31, 2021, 10:37pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/2 "2021-03-31T22:37:11Z")

</div>

Looks like a Cutler Hammer load center , Cutler Hammer does have Circuit Breakers that can accept two wires but you have to know which ones. There is not enough information on the picture to determine the answer to your 'question. You have to get the breaker type and load info from the tags and printing on the component.

---

<div class="post-metadata">

**Author:** ![jwood22](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jwood22/32/179475_2.png) [@jwood22](https://forum.nachi.org/u/jwood22)\
**Post date:** [March 31, 2021, 10:40pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/3 "2021-03-31T22:40:07Z")

</div>

![image](https://global.discourse-cdn.com/internachi/original/3X/4/f/4f009810141f07b8c2bdd383b088c17d3674f91f.jpeg)

Can you tell from this?

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [March 31, 2021, 10:44pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/4 "2021-03-31T22:44:27Z")

</div>

Wrong OCPD to terminate 2 conductors on.  
Refer for correction.

Have a shot of the AFCI conductor terminations?

---

<div class="post-metadata">

**Author:** ![jwood22](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jwood22/32/179475_2.png) [@jwood22](https://forum.nachi.org/u/jwood22)\
**Post date:** [March 31, 2021, 10:48pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/5 "2021-03-31T22:48:33Z")

</div>

Thanks! That’s what I was thinking. How can you determine that this is the wrong breaker for two conductors?

I believe this to be a GFCI

 ![image](https://global.discourse-cdn.com/internachi/original/3X/8/7/87919d73318d8a3e00e34f139060d7c97925f11e.jpeg)

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [March 31, 2021, 10:54pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/6 "2021-03-31T22:54:10Z")

</div>

2 conductors under one lug.  
Breaker label identifies how many conductors can terminate.  
AFCI are 1 conductor only.  
 ![double tap Squard D breaker](https://global.discourse-cdn.com/internachi/original/3X/1/9/19274b7969e7d1b20f33bf0596be096e3fd36c13.jpeg)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 31, 2021, 11:39pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/7 "2021-03-31T23:39:27Z")

</div>

No, I don’t believe that “mini split” breakers can have two ungrounded wires attached.

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [March 31, 2021, 11:50pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/8 "2021-03-31T23:50:11Z")

</div>

Looks like AL wiring above the GFCI breakers.

---

<div class="post-metadata">

**Author:** ![jmilby](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmilby/32/57038_2.png) [@jmilby](https://forum.nachi.org/u/jmilby)\
**Post date:** [March 31, 2021, 11:51pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/9 "2021-03-31T23:51:42Z")

</div>

Stranded aluminum conductors should not an issue.

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [March 31, 2021, 11:55pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/10 "2021-03-31T23:55:39Z")

</div>

It looked like single strand but you’re right after having another look.

---

<div class="post-metadata">

**Author:** ![jwood22](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jwood22/32/179475_2.png) [@jwood22](https://forum.nachi.org/u/jwood22)\
**Post date:** [March 31, 2021, 11:57pm UTC](https://forum.nachi.org/t/double-tapped-minis/196015/11 "2021-03-31T23:57:34Z")

</div>

Does it always state on the breaker when it accepts two grounded conductors? I feel like I should have learned this already.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [April 1, 2021, 12:00am UTC](https://forum.nachi.org/t/double-tapped-minis/196015/12 "2021-04-01T00:00:18Z")

</div>

I think the split breaker is Cutler’s answer for two conductors, one for each side. So, the breaker takes up less space and you get two (not 4) conductors. The label says two 1 pole units.

---

<div class="post-metadata">

**Author:** ![asinger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/asinger/32/100152_2.png) [@asinger](https://forum.nachi.org/u/asinger)\
**Post date:** [April 1, 2021, 12:34am UTC](https://forum.nachi.org/t/double-tapped-minis/196015/13 "2021-04-01T00:34:46Z")

</div>

Those don’t take two conductors and be careful - the panel may not be designed for the twin breakers in all locations or at all. You have to check the legend on the panel for how it was designed.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [April 1, 2021, 5:31am UTC](https://forum.nachi.org/t/double-tapped-minis/196015/14 "2021-04-01T05:31:33Z")

</div>

[In addition, the presence of single- _strand aluminum wiring_ may void a home’s](https://www.nachi.org/aluminum-wiring.htm)

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [April 1, 2021, 5:39am UTC](https://forum.nachi.org/t/double-tapped-minis/196015/15 "2021-04-01T05:39:51Z")

</div>

> [@jwood22](#):
>
> Does it always state on the breaker when it accepts two grounded conductors? I feel like I should have learned this already.

To answer your questions.  
1: Yes. OCPD Label indicates the conductor AWG and terminations. Square D & Cutter Hammer.

2: 🤔 Not to worry. I only recently learned to hit the water in the bowl, and that’s after decades.  
Just be happy. You learned something new. 😀

---

<div class="post-metadata">

**Author:** ![jwood22](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jwood22/32/179475_2.png) [@jwood22](https://forum.nachi.org/u/jwood22)\
**Post date:** [April 1, 2021, 8:56am UTC](https://forum.nachi.org/t/double-tapped-minis/196015/16 "2021-04-01T08:56:51Z")

</div>

Thanks for all of the help guys!