How serious do you treat double and triple tapped neutrals on the bus bar? If it is the only item on sub-panel wrong, is it just a minor or major concern?

 ![IMG_5310.jpg](https://global.discourse-cdn.com/internachi/original/3X/f/a/fabc8201145e351daeb843dd1d165062949f0949.jpeg)

---

<div class="post-metadata">

**Author:** ![mclark2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mclark2/32/170907_2.png) [@mclark2](https://forum.nachi.org/u/mclark2)\
**Post date:** [May 24, 2015, 7:31pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/2 "2015-05-24T19:31:09Z")

</div>

It’s only a concern if safety and fire are a concern.

It depends on if you consider electrocution or a possible fire, minor or major.

Your client probably has no clue, and is depending on your report to tell them.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [May 24, 2015, 7:59pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/3 "2015-05-24T19:59:54Z")

</div>

Major or minor is of no concern to me. It’s an improper installation and should be corrected.

---

<div class="post-metadata">

**Author:** ![mclark2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mclark2/32/170907_2.png) [@mclark2](https://forum.nachi.org/u/mclark2)\
**Post date:** [May 24, 2015, 8:13pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/4 "2015-05-24T20:13:23Z")

</div>

> [@jpope](#):
>
> Major or minor is of no concern to me. It’s an improper installation and should be corrected.

I struggle with these terms as well, and thinking about doing away with the summary because of it.

Every one’s concept of minor or major is not the same.

My wife is a prime example. It’s “major” to her if I walk through the house without taking off my shoes. It’s “minor” to her if she forgot to tell me she just sent my adult daughter $1000…again! 😉

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [May 24, 2015, 10:12pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/5 "2015-05-24T22:12:22Z")

</div>

> [@jpope](#):
>
> Major or minor is of no concern to me. It’s an improper installation and should be corrected.

I agree this is prohibited for a good reason.

---

<div class="post-metadata">

**Author:** ![rwells4](https://avatars.discourse-cdn.com/v4/letter/r/e274bd/32.png) [@rwells4](https://forum.nachi.org/u/rwells4)\
**Post date:** [May 24, 2015, 10:25pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/6 "2015-05-24T22:25:20Z")

</div>

> [@tgreenwade1](#):
>
> How serious do you treat double and triple tapped neutrals on the bus bar? If it is the only item on sub-panel wrong, is it just a minor or major concern?

Hard to say if something is minor or major.

But keep in mind a couple of things.

a) it is a code violation

b) you say we are not code inspectors - okay.. it is a safety issue and the panel manufactures will say so. Here is one from Square D. This also gives some reasoning so will not go into that.

[http://ecatalog.squared.com/pubs/Electrical%20Distribution/Panelboards/0100DB0705.pdf](http://ecatalog.squared.com/pubs/Electrical%20Distribution/Panelboards/0100DB0705.pdf)

c) since it is not allowed - no panel board is ever tested with multiple conductors under the terminals. Not designed to be used with multiples, not tested to be used with multiples, and rules say not to do so.

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [May 25, 2015, 12:02am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/7 "2015-05-25T00:02:21Z")

</div>

The terminals are many times listed for use with multiple grounding conductors.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [May 25, 2015, 12:06am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/8 "2015-05-25T00:06:30Z")

</div>

> [@Jim\_Port](#):
>
> The terminals are many times listed for use with multiple grounding conductors.

With specific restrictions.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [May 25, 2015, 12:26am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/9 "2015-05-25T00:26:23Z")

</div>

> [@jjonas](#):
>
> With specific restrictions.

Which include no grounded neutral conductor.

---

<div class="post-metadata">

**Author:** ![growden](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/growden/32/58544_2.png) [@growden](https://forum.nachi.org/u/growden)\
**Post date:** [May 25, 2015, 12:35am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/10 "2015-05-25T00:35:53Z")

</div>

Here are some doubled up neutrals I found the other day and one set was arcing.

[FONT=Comic Sans MS][size=3]

 ![Douled up neutrals.jpg](https://global.discourse-cdn.com/internachi/original/3X/8/a/8a11c3f2ea850f8c17acefa991d6da6580358ffb.jpeg) [/size][/FONT]

---

<div class="post-metadata">

**Author:** ![dhays](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhays/32/58202_2.png) [@dhays](https://forum.nachi.org/u/dhays)\
**Post date:** [May 25, 2015, 1:37am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/11 "2015-05-25T01:37:54Z")

</div>

> [@rwells4](#):
>
> Hard to say if something is minor or major.
> 
> But keep in mind a couple of things.
> 
> a) it is a code violation
> 
> b) you say we are not code inspectors - okay… it is a safety issue and the panel manufactures will say so. Here is one from Square D. This also gives some reasoning so will not go into that.
> 
> [http://ecatalog.squared.com/pubs/Electrical%20Distribution/Panelboards/0100DB0705.pdf](http://ecatalog.squared.com/pubs/Electrical%20Distribution/Panelboards/0100DB0705.pdf)
> 
> **c) since it is not allowed - no panel board is ever tested with multiple conductors under the terminals. Not designed to be used with multiples, not tested to be used with multiples, and rules say not to do so.**

How do you know that they are never tested with multiple conductors?

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [May 25, 2015, 2:26am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/12 "2015-05-25T02:26:34Z")

</div>

The highest temperature that I have ever recorded in a panel (over 900°F) was on a grounded conductor. I always recommend repair.

---

<div class="post-metadata">

**Author:** ![mbrooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mbrooke/32/57038_2.png) [@mbrooke](https://forum.nachi.org/u/mbrooke)\
**Post date:** [May 25, 2015, 7:57am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/13 "2015-05-25T07:57:41Z")

</div>

That can easily overheat and start a fire. Call out and defer to electrician.

---

<div class="post-metadata">

**Author:** ![jbuckley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jbuckley/32/172460_2.png) [@jbuckley](https://forum.nachi.org/u/jbuckley)\
**Post date:** [May 25, 2015, 11:11am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/14 "2015-05-25T11:11:38Z")

</div>

Doesn’t Square D allow up to 2 neutrals under the same screw? Are there any other manufacturers that allow multiple neutrals under the same screw?

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [May 25, 2015, 11:48am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/15 "2015-05-25T11:48:25Z")

</div>

No panel allows multiple neutrals, aka grounded, in a hole. The code specifies one per hole.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [May 25, 2015, 12:35pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/16 "2015-05-25T12:35:46Z")

</div>

> [@jbuckley](#):
>
> Doesn’t Square D allow up to 2 neutrals under the same screw?

No, Square D does not allow more the one neutral per terminal hole.  
.

> [@jbuckley](#):
>
> ```
> Are there any other manufacturers that allow multiple neutrals under the same screw?
> 
> ```

No.

---

<div class="post-metadata">

**Author:** ![cwallace1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cwallace1/32/60126_2.png) [@cwallace1](https://forum.nachi.org/u/cwallace1)\
**Post date:** [May 27, 2015, 2:19pm UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/17 "2015-05-27T14:19:28Z")

</div>

It would be red in my report.

---

<div class="post-metadata">

**Author:** ![twitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/twitt/32/58462_2.png) [@twitt](https://forum.nachi.org/u/twitt)\
**Post date:** [May 28, 2015, 2:35am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/18 "2015-05-28T02:35:55Z")

</div>

> [@tgreenwade1](#):
>
> How serious do you treat double and triple tapped neutrals on the bus bar? If it is the only item on sub-panel wrong, is it just a minor or major concern?

I don’t do major/minor.  
In this case it’s just noted as a condition in the panel that needs correction by a licensed electrician.

While I’m standing there with the client behind me I also tell them I see it in virtually every panel I inspect, even panels signed off on by municipal code inspectors.

---

<div class="post-metadata">

**Author:** ![kramm](https://avatars.discourse-cdn.com/v4/letter/k/96bed5/32.png) [@kramm](https://forum.nachi.org/u/kramm)\
**Post date:** [May 28, 2015, 2:58am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/19 "2015-05-28T02:58:46Z")

</div>

> [@twitt](#):
>
> I see it in virtually every panel I inspect, even panels signed off on by municipal code inspectors.

Same here and why is that?

---

<div class="post-metadata">

**Author:** ![kshepard](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kshepard/32/59504_2.png) [@kshepard](https://forum.nachi.org/u/kshepard)\
**Post date:** [May 28, 2015, 4:14am UTC](https://forum.nachi.org/t/double-tapped-neutrals/96882/20 "2015-05-28T04:14:51Z")

</div>

> [@tgreenwade1](#):
>
> How serious do you treat double and triple tapped neutrals on the bus bar? If it is the only item on sub-panel wrong, is it just a minor or major concern?

My understanding is that isolating the circuits becomes a problem and that’s why it’s not allowed. It should be identified as needing correction.