# Double tapping question

**URL:** <https://forum.nachi.org/t/double-tapping-question/19537>\
**Category:** Electrical Inspections\
**Created:** [August 22, 2007, 1:38pm UTC](https://forum.nachi.org/t/double-tapping-question/19537 "2007-08-22T13:38:04Z")\
**Posts on this page:** 18\
**Page:** 1

<div class="post-metadata">

**Author:** ![mroe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mroe/32/2113_2.png) [@mroe](https://forum.nachi.org/u/mroe)\
**Post date:** [August 22, 2007, 1:38pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/1 "2007-08-22T13:38:04Z")

</div>

I called out a double tap on a square “D” 100 amp box last week. Today the electrician who was called in to correct it said that there was no problem with this because Square D was the only box allowed to have a double tap on a 40 amp cb for a range and a B/I Dutch oven. I can not find in any of my books where it says this, so before I open my mouth and insert my foot I thought I would ask here first? :mrgreen:

---

<div class="post-metadata">

**Author:** ![srowe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/srowe/32/613_2.png) [@srowe](https://forum.nachi.org/u/srowe)\
**Post date:** [August 22, 2007, 2:01pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/2 "2007-08-22T14:01:30Z")

</div>

He is correct. Did the breaker wire connection look like this (see image)?

---

<div class="post-metadata">

**Author:** ![dedwards](https://avatars.discourse-cdn.com/v4/letter/d/e95f7d/32.png) [@dedwards](https://forum.nachi.org/u/dedwards)\
**Post date:** [August 22, 2007, 2:07pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/3 "2007-08-22T14:07:45Z")

</div>

I like to go to Home Depot and Lowes on occasion just to walk through the various sections of the store just to see what is out there. There are constantly new items coming out that we as Home Inspectors need to know about. I get to pick them up and handle them without getting my yoyo knocked into my watchpocket unlike inside a live panel or system. Square D has had these brkrs around for years and you will run across them. You can get a real education just by hitting the Home Centers and pilfering thru their shelves. Plus it gets me out of the house and yard work.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [August 22, 2007, 2:22pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/4 "2007-08-22T14:22:56Z")

</div>

I have never seen a 40a breaker with the square plate termination, only the hole with the set screw and that type is only rated for one conductor.

---

<div class="post-metadata">

**Author:** ![mroe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mroe/32/2113_2.png) [@mroe](https://forum.nachi.org/u/mroe)\
**Post date:** [August 22, 2007, 2:27pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/5 "2007-08-22T14:27:09Z")

</div>

To answer your question, No… But I was able to contact a supplier of Square D and they did say they could do it if the right breaker was used. But when I describe the setup they said it didn’t sound right. They recommended that another breaker be added for the other wire. They did state that even if the correct breaker was used. The the for the range and the dutch oven setup, it would really be a strain on the breaker. Thanks for the help and the tips on this question…

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [August 23, 2007, 3:04am UTC](https://forum.nachi.org/t/double-tapping-question/19537/6 "2007-08-23T03:04:32Z")

</div>

“A strain on the breaker?”

That doesn’t even pass the laugh test.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 23, 2007, 3:23am UTC](https://forum.nachi.org/t/double-tapping-question/19537/7 "2007-08-23T03:23:28Z")

</div>

Square D breakers are not the **only** breakers rated for two conductors, but as Greg implied, I don’t think there is a 40 amp breaker with that listing. Generally, it’s only the 15 and 20 amp breakers that allow more than one conductor - when listed accordingly.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [August 23, 2007, 5:44am UTC](https://forum.nachi.org/t/double-tapping-question/19537/8 "2007-08-23T05:44:53Z")

</div>

SqD 30s can also have the square washer that takes 2 wires. They make both styles in a 30 so have an option when larger wire sizes are used.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [August 23, 2007, 12:23pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/9 "2007-08-23T12:23:41Z")

</div>

Quite possibly the fellow electrician is confused with 210.19(A)(3) Ex. 1 when he is talking taps…tehhehehe

No, a 40A Sq D breaker is not rated for (2) conductors and no he can’t use 210.19(A)(3) for this either…I was just throwing that one in for FUN

---

<div class="post-metadata">

**Author:** ![gromicko](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gromicko/32/58172_2.png) [@gromicko](https://forum.nachi.org/u/gromicko)\
**Post date:** [August 28, 2007, 7:56am UTC](https://forum.nachi.org/t/double-tapping-question/19537/10 "2007-08-28T07:56:31Z")

</div>

Jeff writes:

> [@](#):
>
> Square D breakers are not the **only** breakers rated for two conductors

I think Cutler Hammer CH circuit breakers are UL listed for 2 wires as well.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [August 28, 2007, 2:04pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/11 "2007-08-28T14:04:22Z")

</div>

Yes …Mr. G…you are correct as CH and QO are both listed for (2) conductors of the same size…😉 However, it is important to note that this applies up to 30A only…once you get above that then terminations on these brands do not allow multiple conductors unless the terminal is EXPRESSLY listed as such …and they wont in regards to breakers…😉

---

<div class="post-metadata">

**Author:** ![acox](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/acox/32/57038_2.png) [@acox](https://forum.nachi.org/u/acox)\
**Post date:** [August 29, 2007, 2:13am UTC](https://forum.nachi.org/t/double-tapping-question/19537/12 "2007-08-29T02:13:59Z")

</div>

That’s why I like this board so well - great questions, and great answers. I haven’t seen this yet, so now if I see it in the next 24 hours, I won’t have to ask! (More than 24 hours, I’ll forget I ever read it…:()

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [August 29, 2007, 4:03pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/13 "2007-08-29T16:03:10Z")

</div>

andrew thats why we answer the SAME questions…over…and over…and over…and over…and over…and over…and over…

---

<div class="post-metadata">

**Author:** ![kmiller1](https://avatars.discourse-cdn.com/v4/letter/k/4bbf92/32.png) [@kmiller1](https://forum.nachi.org/u/kmiller1)\
**Post date:** [August 29, 2007, 7:32pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/14 "2007-08-29T19:32:01Z")

</div>

What question? 😃

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [August 30, 2007, 2:39am UTC](https://forum.nachi.org/t/double-tapping-question/19537/15 "2007-08-30T02:39:08Z")

</div>

You boys need a FAQ page

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [August 30, 2007, 2:42am UTC](https://forum.nachi.org/t/double-tapping-question/19537/16 "2007-08-30T02:42:12Z")

</div>

lol…you ain’t SH\*TIN Greg…or they can use the SEARCH FEATURE built into this forum.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [August 30, 2007, 2:57am UTC](https://forum.nachi.org/t/double-tapping-question/19537/17 "2007-08-30T02:57:29Z")

</div>

Maybe Gerry can whip up a FAQ. It might even rise to the level of a “product” NACHI can sell or offer to members. You folks do cover a lot of ground here and I bet a fraction of a percent of NACHI members ever actually look in.

A compilation of things you have discussed might be worth some official scrutiny. I am sure NACHI owns anything we posted here.  
… certainly with my permission on my gibberish 😉

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [August 30, 2007, 12:32pm UTC](https://forum.nachi.org/t/double-tapping-question/19537/18 "2007-08-30T12:32:50Z")

</div>

Nah…I retain ownership of my content…lol…check is in the mail I am sure…lol…NOT