Draft image: 200 Amp Panelboard (Without Main Disconnect) Supplied by a 4-Wire SER

I’ve attached a new draft image to preview, before finalizing. I’d like to hear any valuable feedback from the forum. Thanks for your help!

1 Like

You might want to note that for a panelboard without a main disconnect the common term used for the panel type is MLO or Main Lug Only. Same issue as the other graphic with the words “service conductors” not being correct for a feeder.

4 Likes

In my area for new construction or when service upgrades are performed, the disconnect is actually the “Emergency Disconnect” and is required to be labeled as such.

Here’s a picture of one I inspected recently.

1 Like

The use of “bonding strap” may be misleading. I think of a bonding strap as being the main bonding jumper in an Eaton panel.

3 Likes

Isn’t the “meter main with disconnect” the Primary panelboard and the panel to the right with 4 wire feed labeled “Primary” the Secondary panelboard? Asking for a Fren.

4 Likes

Yeah, what gives? My Fren wants to know as well :smiley:

I’ve been referring to the “Meter Main with Disconnect” as the service panel and this MLO I’ve been calling a distribution / sub panel.

1 Like

Yes, the service disconnect and a distribution panel is what I was thinking. :man_shrugging:

3 Likes

The meter main is is not showing a panelboard, it’s just the service disconnect.

Can you post a photo of the panel with the cover open? :wink: :laughing:

2 Likes

What should I being calling this, a service disconnect or is this a service panelboard? Its the service disconnect with additional breakers/slots. I see this setup often and want to make sure I’m naming it correctly. I’ve been calling it the service panel.

This was a townhome inspection 1979-build last week with a Sylvania sub in the unit. No label (also common) and the dead front was jammed to the breaker so I couldn’t remove it.

I would call that the service panelboard because it appears to have branch circuit breakers along with the service disconnect. What is shown in the graphic from the OP says nothing to indicate that the “Meter main with disconnect” has additional circuit breakers like in your photo.

Maybe Zak can clarify what the intent is for the graphic. From the graphic title it appears that they’re trying to show a 4-wire feeder to a MLO sub-panel without a main breaker. The other graphic that was posted today shows a panel with a main breaker.

1 Like

Well done, Zac.
Looks good to me.

According to the NEC there is no primary or secondary panelboards. I’m not sure if using those terms provide any clarity when describing the electrical system. The term service would apply to the “Meter main with disconnect”. It would be more accurate to say “Meter main with service disconnect”.

1 Like

Two comments

(A) move the green wire to the large terminal. It’s a much larger conductor than the big row of screws can handle.

(B) Add a representative bonding jumper. Many standard panel designs have a feature to connect ground and neutral, for when the panel is used as a main. This is usually a screw, and can be easy to miss. It’s bad if the screw is in the wrong position based on the use case, as this defeats the entire purpose of keeping ground bonded at only one place (the main).

Consider also highlighting that ground and neutral MUST be bonded the meter main
and ONLY at the meter main.

1 Like