I don’t recall that particular discussion Dave, however, there have been several discussions regarding “false-ground” readings with the SureTest.
Basically, the SureTest gives this indication when the resistance is to low between the ground (egc) and the neutral (grounded conductor).
It’s common to get this indication when the receptacle is close to the service equipment (where the grounds and neutrals are bonded) or near a distribution panel where the neutrals have been grounded (which we know to be improper).
The indicator is intended to help the inspector identify “bootleg” grounds, where the egc has been “grounded” to the circuit-neutral, rather than grounded at the panel.