I can find some info on electrical load calcs online, but I can’t find anything about when they are performed.

Are they performed when no upgrades are made anywhere in the home to determine if the service needs to be updated?

Or

Are they performed when making upgrades to the home to determine if the service needs to be updated and what it needs to be updated to?

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [September 26, 2013, 1:12pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/2 "2013-09-26T13:12:13Z")

</div>

I know we’ve been discussing this elsewhere, but here is my “two-cents.”

Load calculations are generally done during the **design phase** of the construction/renovation/addition(s) of a residence, to determine the necessary service capacity, and the size and quantity of branch circuits that will be necessary.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 1:17pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/3 "2013-09-26T13:17:43Z")

</div>

> [@jpope](#):
>
> I know we’ve been discussing this elsewhere, but here is my “two-cents.”
> 
> Load calculations are generally done during the **design phase** of the construction/renovation/addition(s) of a residence, to determine the necessary service capacity, and the size and quantity of branch circuits that will be necessary.

Ah that is contrary to what I was told in the other thread, but I trust the Pope:mrgreen:

Thanks Jeff!

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [September 26, 2013, 1:23pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/4 "2013-09-26T13:23:55Z")

</div>

> [@jjimenez](#):
>
> Ah that is contrary to what I was told in the other thread, but I trust the Pope:mrgreen:
> 
> Thanks Jeff!

Since you brought it up, a link should be offered… [Inspection Question - General Inspection Discussion - InterNACHI®️ Forum](http://www.nachi.org/forum/f11/inspection-question-85090/)

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 1:24pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/5 "2013-09-26T13:24:35Z")

</div>

> [@jjonas](#):
>
> Since you brought it up, a link should be offered… [Inspection Question - General Inspection Discussion - InterNACHI®️ Forum](http://www.nachi.org/forum/f11/inspection-question-85090/)

I don’t care

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [September 26, 2013, 1:25pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/6 "2013-09-26T13:25:34Z")

</div>

Wait for some of our resident experts to chime in before you take that to the bank. They will likely have much better information.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [September 26, 2013, 1:26pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/7 "2013-09-26T13:26:06Z")

</div>

> [@jjimenez](#):
>
> I don’t care

That’s the problem. You are closed minded to those you have issue with.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 1:27pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/8 "2013-09-26T13:27:53Z")

</div>

> [@jjonas](#):
>
> That’s the problem. You are closed minded to those you have issue with.

I don’t care about proper message board etiquette such as posting links to other threads. You can continue to pick up my slack though.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [September 26, 2013, 1:28pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/9 "2013-09-26T13:28:14Z")

</div>

> [@jpope](#):
>
> Wait for some of our resident experts to chime in before you take that to the bank. They will likely have much better information.

Thank you for that.

I found it interesting that Juan had to start another thread just to accept the opinion already offered in the other thread, without waiting for benefit of further input from others.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 1:28pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/10 "2013-09-26T13:28:27Z")

</div>

> [@jpope](#):
>
> Wait for some of our resident experts to chime in before you take that to the bank. They will likely have much better information.

Will do

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 1:31pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/11 "2013-09-26T13:31:56Z")

</div>

> [@jjonas](#):
>
> Thank you for that.
> 
> I found it interesting that Juan had to start another thread just to accept the opinion already offered in the other thread, without waiting for benefit of further input from others.

Dang. I guess I made another message board mistake. Thanks for keeping me honest Jeff.

---

<div class="post-metadata">

**Author:** ![tpappas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tpappas/32/1126_2.png) [@tpappas](https://forum.nachi.org/u/tpappas)\
**Post date:** [September 26, 2013, 2:31pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/12 "2013-09-26T14:31:47Z")

</div>

There is a good talk about Load Calculations in the book talked about in this thread 🙂

[http://www.nachi.org/forum/f2/electrical-inspection-code-check-85217/](http://www.nachi.org/forum/f2/electrical-inspection-code-check-85217/)

---

<div class="post-metadata">

**Author:** ![wblackmon](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wblackmon/32/1317_2.png) [@wblackmon](https://forum.nachi.org/u/wblackmon)\
**Post date:** [September 26, 2013, 2:47pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/13 "2013-09-26T14:47:36Z")

</div>

Normally, as Jeff has stated, it is done at the design phase before construction is begun. This is typical of both new construction and renovation projects.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 3:00pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/14 "2013-09-26T15:00:35Z")

</div>

> [@wblackmon](#):
>
> Normally, as Jeff has stated, it is done at the design phase before construction is begun. This is typical of both new construction and renovation projects.

Thanks Will.

---

<div class="post-metadata">

**Author:** ![canderson5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/canderson5/32/1814_2.png) [@canderson5](https://forum.nachi.org/u/canderson5)\
**Post date:** [September 26, 2013, 3:22pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/15 "2013-09-26T15:22:12Z")

</div>

> [@jjimenez](#):
>
> Dang. I guess I made another message board mistake. Thanks for keeping me honest Jeff.

Sometimes it’s good to start another thread just to get your question separated from all the useless and unrelated-to-the-topic posts.(Like my post in this thread for example) 😃

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 3:24pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/16 "2013-09-26T15:24:55Z")

</div>

> [@canderson5](#):
>
> Sometimes it’s good to start another thread just to get your question separated from all the useless and unrelated-to-the-topic posts.(Like my post in this thread for example) 😃

That is what I was thinking. Perhaps we just don’t know how to use the message board properly.

---

<div class="post-metadata">

**Author:** ![evandeven](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/evandeven/32/373798_2.png) [@evandeven](https://forum.nachi.org/u/evandeven)\
**Post date:** [September 26, 2013, 3:25pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/17 "2013-09-26T15:25:55Z")

</div>

I have a load calculation form in excel, if you wan tit.  
Just e mail me@ [ev@magnuminspections.com](mailto:ev@magnuminspections.com)

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2013, 3:45pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/18 "2013-09-26T15:45:15Z")

</div>

> [@evandeven](#):
>
> I have a load calculation form in excel, if you wan tit.  
> Just e mail me@ [ev@magnuminspections.com](mailto:ev@magnuminspections.com)

You do this on a home inspection?

---

<div class="post-metadata">

**Author:** ![mclark2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mclark2/32/170907_2.png) [@mclark2](https://forum.nachi.org/u/mclark2)\
**Post date:** [September 26, 2013, 4:43pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/19 "2013-09-26T16:43:08Z")

</div>

I only did load calculations when in the back up generator industry. Why would a Home Inspector ever need to do a load calculation anyway, except for the obvious.

I inspected a 1500 sq ft home not long ago, where the old fuse box had obviously been replaced by a breaker box. It contained 5 total circuits. No calculation necessary…

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [September 26, 2013, 4:47pm UTC](https://forum.nachi.org/t/electrical-load-calculation/81183/20 "2013-09-26T16:47:56Z")

</div>

> [@mclark2](#):
>
> I only did load calculations when in the back up generator industry.

That doesn’t sound like a **design** or **rehab/reno** event to me. Why the load calc when installing a generator back-up system?