Alot of homes have 200 amp service. What is the maximum amount of current being supplied from the overhead service lines ?
In theory it’s 200 amps but there are limiting factors like the size of the transformer on the pole and how many services are connected to that transformer. The utility company uses a fairly generous demand factor meaning that if there are 2-200 amp services connected it’s likely that they have calculated the maximum amount of current they can provide to quite a bit less than than that.
For example the transformer on the pole feeding my house is a 25 kva which is feeding two homes each with a 200 amp service. A 25 kva has a maximum normal output of 104 amps. (25000/240=104 amps)
A utility company will supply whatever a customer is willing to pay for.
BS! What “Theory” are you referring to?
A utility company will provide whatever a customer is willing to pay for. I have personally installed several 10mVA 3θ, 13.2 kV primary systems with the second current being approximately 12,000 amps and the primary current being approximately 437A. Consumers can purchase electricity at either primary or secondary Voltages. I have had customers buy electricity at primary Voltages and I‘ve had customers buy electricity at secondary Voltages. Most buy electricity at secondary Voltage, so the current supplied by the utility company in a 10mVA system would be approximately 12,000A.
I’ve worked on many systems larger than 10mVA with correspondingly higher current capacities.
The maximum overhead single phase service entrance capacity is 600 amps. Seen it several times in my neck of the woods. However, a utility may permit an 800 amp single phase underground service if certain conditions are met.
How often are the customer and the end user the same person? The customer would be the developer that built the home, and the end user is the homeowner. Most developers are only going to pay for the bare minimum, because in theory the user is going to have 200 amps.
for a residential electrical service - almost every time in my experience, limited as it may be to the last 20 odd years of visiting clients in homes. every now and then i have found a landlord was the customer when electricity was included in the rent, but not very often in a rented house, mostly apartments. the developer is not the customer as soon as the new owners take possession, or however long it takes the utilities to change over to the new owners.
Thanks,
This answers my question.
I saying the people buying the home are not the ones that typically order the original service. Robert’s & George’s examples are what I am referencing. Developers/builders are not going to spend extra money on something that will in theory work.
I spent 11 years designing and selling HVAC systems. Part of that was for new construction. I was told by multiple developers/builders to eliminate a fully ducted return and go with a wild return system, and they would undercut the doors. In theory, do both ways work? Yes. Would spending the extra money to do it correct be better? Yes.
Granite countertops, fixtures, & hardwood flooring sell homes. MEP systems do not. Where do you think the developer/builder is going to cut costs?
How often are the customer and the end user the same person? The customer would be the developer that built the home, and the end user is the homeowner. Most developers are only going to pay for the bare minimum, because in theory the user is going to have 200 amps.
There are two components in the question that Stephan asked in the OP. The first is the actual service size. The minimum service size is determined by a load calculation based on the size of the dwelling, etc. As you’ve mentioned around here for an average size house it’s likley 200 amps.
The second component is what the utility can provide in terms of current which is typcially limited by the size of the transformer on the pole. The POCO would normally not size the transformer based on the 200 amp service because they know that a 200 amp service is almost never going to draw anything near 200 amps.
Although not often, several times, I have inspected homes with low voltage dry cell transformer. At one property they installed 2.
How often are the customer and the end user the same person?
That depends on when and where a building was built. For example, in the early 2000s in the Las Vegas Valley, most homes and many commercial buildings were built on speculation.
Most of the projects I’ve been involved with were custom builds, so the customers were also the end users. I’ve been involved with only a few that were built on speculation.
What is the maximum amount of current being supplied from the overhead service lines ?
There are too many variables to be able to give you a definitive answer.
Contrary to what most home inspectors seem to believe, modern homes are using less electricity than in recent decades, so utility companies can use smaller transformers.
Service sizes are determined by demand calculations established using historical data from a long period of time and which have not appreciably changed in recent years, while actual demand is diminishing in homes. However, that trend could reverse if more people start buying electric cars and if natural gas appliances go away.
A common transformer size for residential electrical systems is 25kVA, which is a rating of approximately 104A on the secondary. The actual capacity, however will vary based on location. A 25kVA transformer in Anchorage Alaska will put out more current than a transformer in Puerto Rico. Transformer ratings are based on a fixed set of parameters. As with electrical conductors, they are not absolute numbers (which is also contrary to popular belief). Actual current capacity is a function of both time and temperature. So, the transformer in Alaska might safely supply 125A while the same transformer in Puerto Rico might only supply 90A.
A typical oil-filled transformer can have its capacity increased by adding cooling fins. The amount of the increase can be substantial, but the actual transformer is exactly the same.
There is also a huge difference between a sustained (continuous) load and an instantaneous load. Everything I’ve said thus far assumes long duration loads. The maximum current for an instantaneous load is determined by the transformer’s internal impedance (which is expressed as a percentage). In the US, the standard is a minimum of 10,000A for a short duration load. That is also known as the Available Fault Current (AFC). Here gain, it is important to remember that actual current capacity is a function of both time and temperature.
Also, as I explained elsewhere in this discussion, a consumer of electricity can buy almost any capacity they want or need. As an electrical contractor and as a project manager, I routinely worked with utility companies to determine what the supply capacity would be. Different customers have different needs. Electric utility companies do their own calculations based on their knowledge of the local area to determine their standard transformer sizes.
If you are looking for a gross generalization, 104A is about the best answer you’ll get based on 25kVA being the most common transformer size used to supply residential electrical systems. However, I would caution anyone from going around citing that number for any practical applications.
[qquote=“Stephen Salisbury, post:1, topic:250588, username:ssalisbury3”]
What is the maximum amount of current being supplied from the overhead service lines ?
[/quote]
There are too many variables to be able to give you a definitive answer.
Contrary to what most home inspectors seem to believe, modern homes are using less electricity than in recent decades, so utility companies can use smaller transformers.
Service sizes are determined by demand calculations established using historical data from a long period of time and which have not appreciably changed in recent years, while actual demand is diminishing in homes.
A common transformer size for residential electrical systems is 25kVA, which is a rating of approximately 104A on the secondary. The actual capacity, however will vary based on location. A 25kVA transformer in Anchorage Alaska will put out more current than a transformer in Puerto Rico. Transformer ratings are based on a fixed set of parameters. As with electrical conductors, they are not absolute numbers. Actual current capacity is a function of both time and temperature. So, the transformer in Alaska might safely supply 125A while the same transformer in Puerto Rico might only supply 90A.
A typical oil-filled transformer can have its capacity increased by adding cooling fins. The amount of the increase can be substantial, but the actual transformer is exactly the same.
There is also a huge difference between a sustained (continuous) load and an instantaneous load. Everything I’ve said thus far assumes long duration loads. The maximum current for an instantaneous load is determined by the transformer’s internal impedance (which is expressed as a percentage). In the US, the standard is a minimum of 10,000A for a short duration load. That is also known as the Available Fault Current (AFC). Here gain, it is important to remember that actual current capacity is a function of both time and temperature.
Also, as I explained elsewhere in this discussion, a consumer of electricity can buy almost any capacity they want or need. As an electrical contractor and as a project manager, I routinely worked with utility companies to determine what the supply capacity would be. Different customers have different needs. Electric utility companies do their own calculations based on their knowledge of the local area to determine their standard transformer sizes.
If you are looking for a gross generalization, 104A is about the best answer you’ll get based on 25kVA being the most common transformer size used to supply residential electrical systems. However, I would caution anyone from going around citing that number for any practical applications.
George,
Thanks for the information, it is interesting how heat degrades the performance of a transformer
Steve.
S
St
| George Wells, CMI gwells Certified Master Inspector
December 21 |
- | - |
[qquote=“Stephen Salisbury, post:1, topic:250588, username:ssalisbury3”]
What is the maximum amount of current being supplied from the overhead service lines ?
[/quote]
There are too many variables to be able to give you a definitive answer.
Contrary to what most home inspectors seem to believe, modern homes are using less electricity than in recent decades, so utility companies can use smaller transformers.
Service sizes are determined by demand calculations established using historical data from a long period of time and which have not appreciably changed in recent years, while actual demand is diminishing in homes.
A common transformer size for residential electrical systems is 25kVA, which is a rating of approximately 104A on the secondary. The actual capacity, however will vary based on location. A 25kVA transformer in Anchorage Alaska will put out more current than a transformer in Puerto Rico. Transformer ratings are based on a fixed set of parameters. As with electrical conductors, they are not absolute numbers. Actual current capacity is a function of both time and temperature. So, the transformer in Alaska might safely supply 125A while the same transformer in Puerto Rico might only supply 90A.
A typical oil-filled transformer can have its capacity increased by adding cooling fins. The amount of the increase can be substantial, but the actual transformer is exactly the same.
There is also a huge difference between a sustained (continuous) load and an instantaneous load. Everything I’ve said thus far assumes long duration loads. The maximum current for an instantaneous load is determined by the transformer’s internal impedance (which is expressed as a percentage). In the US, the standard is a minimum of 10,000A for a short duration load. That is also known as the Available Fault Current (AFC). Here gain, it is important to remember that actual current capacity is a function of both time and temperature.
Also, as I explained elsewhere in this discussion, a consumer of electricity can buy almost any capacity they want or need. As an electrical contractor and as a project manager, I routinely worked with utility companies to determine what the supply capacity would be. Different customers have different needs. Electric utility companies do their own calculations based on their knowledge of the local area to determine their standard transformer sizes.
If you are looking for a gross generalization, 104A is about the best answer you’ll get based on 25kVA being the most common transformer size used to supply residential electrical systems. However, I would caution anyone from going around citing that number for any practical applications.
That makes sense.
I saying the people buying the home are not the ones that typically order the original service. Robert’s & George’s examples are what I am referencing. Developers/builders are not going to spend extra money on something that will in theory work.
Residential customers almost exclusively buy electricity at secondary Voltages. That means that the utility company owns the transformation and transmission equipment. It is the utility company, not the builder or developer who makes decisions related to the capacity of transformation and transmission equipment.
Utility companies are not bound by the NEC or other codes that the average person is familiar with. They do demand calculations based on their knowledge of the energy consumption of their customer base and other variables and factors.
A residential developer could purchase electricity secondary and specify the secondary current capacity, but that never happens in the residential world.
Instead, a developer will design a residential community with residences that have similar design characteristics such as all houses have certain minimum requirements that would result in all the houses in a development each a having 200A service. The service size is not determined by the developer. They are determined by using industry standard demand calculations.
The utility company, in turn, will do their own demand calculations to determine the capacity needs of their equipment.
Alternatively, as I’ve said, a developer could specify a minimum delivery capacity, but that just doesn’t happen in the residential world.
The most common pole-mounted transformer is a basic oil-filled can style transformer rated at 25kVA. The real question, therefore, is how many homes will each transformer serve. A single 25kVA transformer will typically serve from one to three homes. The transformer capacity is the same whether it serves one home or three homes.
Demand varies throughout a typical day. There are times during which the load is very light and times during which the loads are heavy.
In the commercial world, rates are typically based on a customer’s peak demand. That method isn’t usually used in the residential world. Instead, it is the reverse. Utility companies will sometimes offer discounts for, or even require, load management. In most cases those programs are voluntary, but in some areas, load management may be required.
As a former engineering manager, energy management was an important part of my job. For example, in an industrial facility where energy cost can be a large cost component, it is important to level usage as much as possible. Allowing demand to peak well above average usage for as little as 15 minutes can cost hundreds of thousands of dollars in a single billing period.
In residential settings the numbers are small to individual customers, but are large in aggregate, to the utility company.
A single 25kVA transformer could easily satisfy the demand of five or six houses during most of the day, but would be insufficient at other times. Utility companies can predict energy consumption with a high degree of accuracy. They may offer energy management programs to consumers that limit certain loads during certain times as a way to reduce peak demand.
It’s important to understand that there can be a big difference between connected load and demand load. Residential service size demand calculations are very conservative. Most homes will very rarely come anywhere close to the demand being equal to the service size. A home’s service size may be 200A but could have almost any connected load. The connected load could be a thousand Amperes, but that number is largely irrelevant.
The same is true on the utility company’s end. There may be four homes each with a 200A service, but to the utility company they may only represent a load of 40A each. They too are much more concerned with demand load than connected load.
The relationship between electrical equipment capacity and cost is not linear. It is more exponential. Utility companies, and large energy consumers, therefore have a strong incentive to use the smallest possible equipment.
The typical residential developer doesn’t concern himself in the slightest with how the utility company determines what it does. They will tell the utility company that there will be Xn houses of Yn size and that’s it. The utility company will take it from there.
it is interesting how heat degrades the performance of a transformer
All electrical components are rated for current carrying capacity based on a range of operating temperatures. As ambient temperature rises, current carrying capacity goes down. Conversely, current carrying capacity goes up as temperature goes down. For example, we normally think of #14AWG copper as having a capacity of 15 Amperes but that is based on a specific temperature range. At 0°K, it would be able to carry many millions of Amperes, near infinity, infinitely. There is no such thing as any electrical component having a fixed current carrying capacity.