# Electrical Upgrade Uses old panel as a junction box

**URL:** <https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920>\
**Category:** Electrical Inspections\
**Created:** [December 7, 2021, 1:42am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920 "2021-12-07T01:42:02Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![wstowell](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wstowell/32/180961_2.png) [@wstowell](https://forum.nachi.org/u/wstowell)\
**Post date:** [December 7, 2021, 1:42am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/1 "2021-12-07T01:42:02Z")

</div>

I inspected a house that appeared to originally have a 100A Panel box in the basement. A 200A panel was installed in the garage and they just removed all the breakers in the 100A box and then connected the circuit wires to new wires that ran to the new panel box. Is this ok to do?

 ![IMG_3231](https://global.discourse-cdn.com/internachi/original/3X/2/8/281987ddc517536930ff6594b78483b54869d4bf.jpeg)

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [December 7, 2021, 1:58am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/2 "2021-12-07T01:58:22Z")

</div>

Yes, as long as all connections are inside the junction box, they didnt downsize any conductors, and the box needs to also be bonded (grounded)

Looks like it may not be bonded with those bare grounding conductors

The other concern is overcurrent protection. **Is there a disconnect at the exterior? Or is the first one at the new panel?** You cant have conductors with no overcurrent running across the home

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [December 7, 2021, 2:09am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/3 "2021-12-07T02:09:29Z")

</div>

No problem. Just recommend to secure the door, just like a junction box with a cover plate.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 7, 2021, 4:46am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/4 "2021-12-07T04:46:26Z")

</div>

What those guys said and…

> [@ccurrins](#):
>
> Just recommend to secure the door

…screwing the door shut works around here.

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [December 7, 2021, 6:34am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/5 "2021-12-07T06:34:29Z")

</div>

> [@lkage](#):
>
> …screwing the door shut works around here.

Screwing the door shut works. But, the box still needs to be “accessible” and the screw removable.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 7, 2021, 11:48am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/6 "2021-12-07T11:48:29Z")

</div>

> [@bnesbitt](#):
>
> Screwing the door shut works. But, the box still needs to be “accessible” and the screw removable

But, of course.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [December 7, 2021, 11:56am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/7 "2021-12-07T11:56:31Z")

</div>

Looks like the latch is still intact so screws would not be required. What are the large conductors feeding?

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 7, 2021, 12:04pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/8 "2021-12-07T12:04:30Z")

</div>

> [@rmeier2](#):
>
> Looks like the latch is still intact so screws would not be required.

Good point, Rob. Thanks. 👍

---

<div class="post-metadata">

**Author:** ![wstowell](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wstowell/32/180961_2.png) [@wstowell](https://forum.nachi.org/u/wstowell)\
**Post date:** [December 7, 2021, 2:06pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/9 "2021-12-07T14:06:05Z")

</div>

All the wires from this box appear run directly to the 200A panel located in the garage (inside) and connect to breakers. The main disconnect is in that Panel. The meter is located on the exterior wall directly behind the main panel.

---

<div class="post-metadata">

**Author:** ![wstowell](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wstowell/32/180961_2.png) [@wstowell](https://forum.nachi.org/u/wstowell)\
**Post date:** [December 7, 2021, 2:06pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/10 "2021-12-07T14:06:52Z")

</div>

Yes. Latch still works find

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [December 7, 2021, 3:57pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/11 "2021-12-07T15:57:18Z")

</div>

Hold on, not so fast. The latch on a breaker box leads to an electrically safe area with only switches.  
The latch on the pictured box leads to an area particularly bad for gefingerpoken und mittengrabben.

Carefully drilling a hole for a screw (avoiding metal debris) could raise the bar to entry in a helpful way.

> ACHTUNG! ALLES LOOKENSPEEPERS! Das computermachine ist nicht fuer gefingerpoken **und mittengrabben**. Ist easy schnappen der springenwerk, blowenfusen **und** poppencorken mit spitzensparken. Ist nicht fuer gewerken bei das dumpkopfen. Das rubbernecken sichtseeren keepen das cotten-pickenen hans in das pockets muss; relaxen **und** watchen das blinkenlichten.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 7, 2021, 3:59pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/12 "2021-12-07T15:59:35Z")

</div>

> [@bnesbitt](#):
>
> Hold on, not so fast. The latch on a breaker box leads to an electrically safe area with only switches.  
> The latch on the pictured box leads to an area particularly bad for gefingerpoken und mittengrabben.

I think Rob was referring to code but inspectors can recommend what they want for safety. 😃

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [December 7, 2021, 4:01pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/13 "2021-12-07T16:01:10Z")

</div>

> [@lkage](#):
>
> I think Rob was referring to code but inspectors can recommend what they want for safety. 😃

Sure, all good. Now regarding code, is it required to mark the box “no fuses, junction only”. Everyone around here does it.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [December 7, 2021, 4:03pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/14 "2021-12-07T16:03:04Z")

</div>

> [@bnesbitt](#):
>
> …is it required to mark the box “no fuses, junction only”.

Around here they want the box marked as a “junction box”.

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [December 7, 2021, 4:28pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/15 "2021-12-07T16:28:02Z")

</div>

> [@wstowell](#):
>
> All the wires from this box appear run directly to the 200A panel located in the garage (inside) and connect to breakers. The main disconnect is in that Panel. The meter is located on the exterior wall directly behind the main panel.

Ok. Because you had said this was the original panel, in the basement, so wanted to make sure that the service feeders didn’t go from here to the new panel, and then have a disconnect at that point.

---

<div class="post-metadata">

**Author:** ![mfellman](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mfellman/32/369692_2.png) [@mfellman](https://forum.nachi.org/u/mfellman)\
**Post date:** [December 7, 2021, 4:52pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/16 "2021-12-07T16:52:50Z")

</div>

In my area it’s standard to screw the panel closed, presumably to keep a kid or other curious folks from just pulling it open.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [December 7, 2021, 4:56pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/17 "2021-12-07T16:56:50Z")

</div>

> [@lkage](#):
>
> I think Rob was referring to code but inspectors can recommend what they want for safety

That’s correct. And there is no marking required by the NEC when the old panel cabinet is used as a junction box.

---

<div class="post-metadata">

**Author:** ![mgleeson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgleeson/32/59545_2.png) [@mgleeson](https://forum.nachi.org/u/mgleeson)\
**Post date:** [December 7, 2021, 5:09pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/18 "2021-12-07T17:09:44Z")

</div>

The way I am reading this is that 100A wiring is only protected by a 200A breaker?? Is the main in the new panel a 200A breaker with no other OCPD between it and the meter?

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [December 7, 2021, 8:04pm UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/19 "2021-12-07T20:04:35Z")

</div>

> [@mfellman](#):
>
> In my area it’s standard to screw the panel closed, presumably to keep a kid or other curious folks from just pulling it open.

Same here, similar to a J-box.

---

<div class="post-metadata">

**Author:** ![wstowell](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wstowell/32/180961_2.png) [@wstowell](https://forum.nachi.org/u/wstowell)\
**Post date:** [December 8, 2021, 12:59am UTC](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920/20 "2021-12-08T00:59:07Z")

</div>

New 200A panel has breakers protecting all circuits that were connected together in the old 100A box

[Next page](https://forum.nachi.org/t/electrical-upgrade-uses-old-panel-as-a-junction-box/207920.md?page=2)