# Electrician says this is OK

**URL:** <https://forum.nachi.org/t/electrician-says-this-is-ok/68810>\
**Category:** Electrical Inspections\
**Created:** [April 30, 2012, 6:36pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810 "2012-04-30T18:36:50Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [April 30, 2012, 6:36pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/1 "2012-04-30T18:36:50Z")

</div>

The electrician that installed these panels says the wiring is OK, even though the neutrals and grounds are bonded at “sub-panel” at left.

Sorry about clarity of photos.

 ![2012-04-28 14.50.05.jpg](https://global.discourse-cdn.com/internachi/original/3X/7/1/7164ab805ef47dbc95269584ea5ef2e8df407b3b.jpeg)

 ![2012-04-28 14.53.13.jpg](https://global.discourse-cdn.com/internachi/original/3X/d/4/d4eca1a22fb4c084c7bf36d22621a1af538e9d41.jpeg)

 ![2012-04-28 14.52.47.jpg](https://global.discourse-cdn.com/internachi/original/3X/0/5/05476f7818c53b9bf9674283087eebd42cf2a777.jpeg)

---

<div class="post-metadata">

**Author:** ![dedwards](https://avatars.discourse-cdn.com/v4/letter/d/e95f7d/32.png) [@dedwards](https://forum.nachi.org/u/dedwards)\
**Post date:** [April 30, 2012, 7:53pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/2 "2012-04-30T19:53:13Z")

</div>

Well, of course he did.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [April 30, 2012, 8:52pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/3 "2012-04-30T20:52:41Z")

</div>

Customer needs to hire a better electrician. :roll:

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [April 30, 2012, 9:10pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/4 "2012-04-30T21:10:20Z")

</div>

Not only do the neutrals need to be isolated from the panel and grounding conductors, but the egc’s must be bonded to the panel enclosure.

As Robert suggested, tell them to get a new electrician.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [April 30, 2012, 9:51pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/5 "2012-04-30T21:51:52Z")

</div>

> [@jpope](#):
>
> Not only do the neutrals need to be isolated from the panel and grounding conductors, but the egc’s must be bonded to the panel encloser.

Correct. I guess you noticed the bars are isolated from the panel.

Funnier part is a previous home inspector left his card in the panel, with nothing mentioned in his report.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [April 30, 2012, 9:56pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/6 "2012-04-30T21:56:34Z")

</div>

Aren’t there two EGC bars in this panel bonded to the enclosure with no conductors connected to them?

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [April 30, 2012, 10:18pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/7 "2012-04-30T22:18:30Z")

</div>

> [@Robert\_Meier](#):
>
> Aren’t there two EGC bars in this panel bonded to the enclosure with no conductors connected to them?

Yes, the ground bars.:D. He must have overlooked those.

The person that installed these left his installed by sticker on each panel.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [May 1, 2012, 12:09am UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/8 "2012-05-01T00:09:35Z")

</div>

> [@Robert\_Meier](#):
>
> Aren’t there two EGC bars in this panel bonded to the enclosure with no conductors connected to them?

Yes, he must have overlooked those. 😁

---

<div class="post-metadata">

**Author:** ![rdemott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rdemott/32/179490_2.png) [@rdemott](https://forum.nachi.org/u/rdemott)\
**Post date:** [May 5, 2012, 5:30pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/9 "2012-05-05T17:30:53Z")

</div>

It was nice of the last home inspector to leave a flammable item in the service panel

---

<div class="post-metadata">

**Author:** ![dandersen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dandersen/32/59398_2.png) [@dandersen](https://forum.nachi.org/u/dandersen)\
**Post date:** [May 5, 2012, 6:43pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/10 "2012-05-05T18:43:36Z")

</div>

Interesting how many inspectors “recommend further evaluation by a licensed electrician (and others)” and then there is stuff like this…

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [May 5, 2012, 7:22pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/11 "2012-05-05T19:22:22Z")

</div>

> [@dandersen](#):
>
> Interesting how many inspectors “recommend further evaluation by a licensed electrician (and others)” and then there is stuff like this…

Such as this from yesterday…

Note the date on the ‘tag’. The homeowner/seller purchased the townhome in 2004, and yes, he had an inspection performed. He told me of many of the corrections he made himself, but knew of no issues in the panel!!! :shock:

 ![DSCI0058.jpg](https://global.discourse-cdn.com/internachi/original/3X/9/d/9dd2b51f77c79e4c22df6779097df4786a348446.jpeg)

 ![DSCI0064.jpg](https://global.discourse-cdn.com/internachi/original/3X/5/1/5134eeae664e8a454474f353035f6c3d96951cc9.jpeg)

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [May 5, 2012, 9:16pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/12 "2012-05-05T21:16:19Z")

</div>

Hard to tell from the photo’s so what’s wrong with the panel?

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [May 6, 2012, 1:58pm UTC](https://forum.nachi.org/t/electrician-says-this-is-ok/68810/13 "2012-05-06T13:58:45Z")

</div>

I do see conduit fitting being used on the NM cables.