# Federal Pacific Electrical Panel in 1979 condo

**URL:** <https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253>\
**Category:** Florida and SUNachi Inspectors\
**Created:** [May 26, 2023, 11:25am UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253 "2023-05-26T11:25:01Z")\
**Posts on this page:** 12\
**Page:** 1

<div class="post-metadata">

**Author:** ![czhang5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/czhang5/32/268942_2.png) [@czhang5](https://forum.nachi.org/u/czhang5)\
**Post date:** [May 26, 2023, 11:25am UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/1 "2023-05-26T11:25:01Z")

</div>

Morning All

I am the first time find out this big guy in a 1979 condo. The InterNACHI class mention this guy many time. I think I should just report it to call professional license electrical contractor to make an inspection？

 ![20230525_110705](https://global.discourse-cdn.com/internachi/original/4X/5/f/d/5fd35c4026fe7fc7beba85cecb760f505c2d9bf9.jpeg)  
 ![20230525_110714](https://global.discourse-cdn.com/internachi/original/4X/d/1/e/d1ef1e4065ac7deb34f8c4a28c0c9167551980f2.jpeg)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [May 26, 2023, 11:42am UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/2 "2023-05-26T11:42:41Z")

</div>

> [@czhang5](#):
>
> I think I should just report it to call professional license electrical contractor to make an inspection？

Yes…I would.

---

<div class="post-metadata">

**Author:** ![rkenney](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rkenney/32/405447_2.png) [@rkenney](https://forum.nachi.org/u/rkenney)\
**Post date:** [May 26, 2023, 11:44am UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/3 "2023-05-26T11:44:31Z")

</div>

CYA Report it as a defect: “Obsolete panel, no longer serviceable” Report the fact that FPE cheated on breaker testing and that many FPE breakers do not work when needed, leaving critical circuits that can be overloaded and cause fires.

Add a reference:

> **[Why should I replace my obsolete and dangerous Federal Pacific Panel? |...](https://www.wirechiefelectric.com/replace-dangerous-federal-pacific-panel)**
>
> Should I Replace My Federal Pacific Panel? Your home may still have a type of electrical circuit breaker that has been the subject of a long-running debate over safety concerns. These worries centre on whether the Federal Pacific panel and its...

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [May 26, 2023, 11:45am UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/4 "2023-05-26T11:45:56Z")

</div>

Being that you are in Florida, insurance will likely require replacement on federal pacific and zynsco/sylvania.  
There are a few that may still insure, but not many.

Just report that they are known for having issues, and could be fire hazards, and that replacement may be necessary.

---

<div class="post-metadata">

**Author:** ![mgoldenberg](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgoldenberg/32/89265_2.png) [@mgoldenberg](https://forum.nachi.org/u/mgoldenberg)\
**Post date:** [May 26, 2023, 12:33pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/5 "2023-05-26T12:33:34Z")

</div>

Please click the following link to go to:  
[http://www.inspectapedia.com/fpe/FPESummary.htm](http://www.inspectapedia.com/fpe/FPESummary.htm)  
for further information  
Due to FPE’s fraudulent testing and falsified UL labeling, defective FPE Stab-Lok circuit  
breakers were installed in millions of residences throughout the United States. Recent tests on  
more than 500 Stab-Lok breakers from homes across the country show defective performance  
for about 1/3 of the two-pole FPE Stab-Lok circuit breakers and about 1/5 of the single-pole  
FPE Stab-Lok circuit breakers.  
Because of the proven high defect rate, the FPE Stab-Lok breakers that are presently  
installed in homes do not provide the circuit protection that is required by applicable codes  
and standards (NEC and UL).  
This constitutes an increased risk of fire and injury.  
Homeowners and renovators who encounter these panels should consider replacing them with  
new equipment. Panel replacement, can involve significant expense, depending on service size  
and other factors.  
But identifying one of these defects can lead to an argument in some cases.  
For example, a knowledgeable inspector or contractor observes one of these panels and  
recommends replacement. An owner or another inspector, unaware of the background,  
refuses to cooperate, and insists there is “no problem.” Who’s right?  
There is indeed “a problem.” FPE panels and circuit breakers are a “safety-related defect.”  
In some conditions the equipment may not provide the safety protection (against fire) that  
was intended.  
\*\*\* Safety Warning\*\*\*  
I have observed a Federal Pacific Electric “Stab-Lok” service panel in the house.  
This panel is a latent fire hazard: it’s circuit breakers may fail to trip in response to an  
over current or a short circuit. Failure of a circuit breaker to trip can result in a fire,  
property damage, or personal injury. A circuit breaker that may not trip does not afford  
the protection that is intended and required.  
Simply replacing the circuit breakers is not a reliable repair. The panel should be replaced,  
and significant expense may be involved.

---

<div class="post-metadata">

**Author:** ![kleonard](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kleonard/32/170953_2.png) [@kleonard](https://forum.nachi.org/u/kleonard)\
**Post date:** [May 26, 2023, 12:35pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/6 "2023-05-26T12:35:49Z")

</div>

I report them as a potential fire and shock hazard with documented failures and recommend replacement.

---

<div class="post-metadata">

**Author:** ![czhang5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/czhang5/32/268942_2.png) [@czhang5](https://forum.nachi.org/u/czhang5)\
**Post date:** [May 26, 2023, 1:22pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/7 "2023-05-26T13:22:21Z")

</div>

If I see this brand panel in the 4 points inspection, are we also will report it is a Hazards present, right?

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [May 26, 2023, 2:41pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/8 "2023-05-26T14:41:12Z")

</div>

Thank for sharing. Never seen on in my neckof the woods.

---

<div class="post-metadata">

**Author:** ![mgoldenberg](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgoldenberg/32/89265_2.png) [@mgoldenberg](https://forum.nachi.org/u/mgoldenberg)\
**Post date:** [May 26, 2023, 4:16pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/9 "2023-05-26T16:16:07Z")

</div>

> [@czhang5](#):
>
> If I see this brand panel in the 4 points inspection, are we also will report it is a Hazards present, right?

The 4 point asks what brand is the panel.  
Just enter FPE Stab-Lok. The rest is totally up to the insurance carrier.

---

<div class="post-metadata">

**Author:** ![ringalls](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ringalls/32/59732_2.png) [@ringalls](https://forum.nachi.org/u/ringalls)\
**Post date:** [May 26, 2023, 4:21pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/10 "2023-05-26T16:21:28Z")

</div>

On just a 4-Point Insurance inspection, just document what you found about the electrical panel (i.e. main or subpanel, total amps, panel age, and brand/model)  
No need to add additional info about FPE. The insurance company will handle it from there.  
On a regular detailed home inspection, that is where you would provide in your report additional information about the potentially hazard panel.

---

<div class="post-metadata">

**Author:** ![czhang5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/czhang5/32/268942_2.png) [@czhang5](https://forum.nachi.org/u/czhang5)\
**Post date:** [May 26, 2023, 4:44pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/11 "2023-05-26T16:44:49Z")

</div>

Get it. Thanks a lot

---

<div class="post-metadata">

**Author:** ![szakharchenko](https://avatars.discourse-cdn.com/v4/letter/s/8e8cbc/32.png) [@szakharchenko](https://forum.nachi.org/u/szakharchenko)\
**Post date:** [June 6, 2024, 9:46pm UTC](https://forum.nachi.org/t/federal-pacific-electrical-panel-in-1979-condo/229253/12 "2024-06-06T21:46:56Z")

</div>

Thank you for posting through explanation!