# Flush mounted electrical meter

**URL:** <https://forum.nachi.org/t/flush-mounted-electrical-meter/218501>\
**Category:** Electrical Inspections\
**Created:** [August 4, 2022, 1:03pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501 "2022-08-04T13:03:25Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [August 4, 2022, 1:03pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/1 "2022-08-04T13:03:25Z")

</div>

Hi guys, this one was a first for me. I’m hoping someone has more information on this. I came across this underground service and meter panel, the panel was recessed into the masonry veneer and the service entrance cable was hidden, I’m assuming behind the veneer. Also, I didn’t see any type of proper grounding which I am noting in the report separately. Thank you for taking a look at this for me, any help would be greatly appreciated.

 ![IMG_0706](https://global.discourse-cdn.com/internachi/original/4X/4/1/9/419eb967b36a41dc8fd7b01b63facc39bf3c64d9.jpeg)  
 ![IMG_0703](https://global.discourse-cdn.com/internachi/original/4X/3/4/1/341b656a9c344842f5f8e4ef4900bbc62ec14336.jpeg)

---

<div class="post-metadata">

**Author:** ![gneff](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gneff/32/59427_2.png) [@gneff](https://forum.nachi.org/u/gneff)\
**Post date:** [August 4, 2022, 1:26pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/2 "2022-08-04T13:26:25Z")

</div>

Likely that the stone was layed around it.  
Did you open the disconnect cover? That should give you an idea if it is grounded, as well in the main panel. Newer construction does not always have a visible exterior ground.  
The service entrance is likely in conduit, but not confirmable.  
Just report what you see.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [August 4, 2022, 1:43pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/3 "2022-08-04T13:43:04Z")

</div>

What is this?

 ![nachi](https://global.discourse-cdn.com/internachi/original/4X/1/a/c/1ac3fa22be00845e96899c422096aa381d4650df.jpeg)

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 4, 2022, 1:43pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/4 "2022-08-04T13:43:14Z")

</div>

> [@dvandermeulen](#):
>
> Hi guys, this one was a first for me. I’m hoping someone has more information on this. I came across this underground service and meter panel, the panel was recessed into the masonry veneer and the service entrance cable was hidden, I’m assuming behind the veneer. Also, I didn’t see any type of proper grounding which I am noting in the report separately. Thank you for taking a look at this for me, any help would be greatly appreciated

Is there a question in there somewhere?

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 4, 2022, 1:44pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/5 "2022-08-04T13:44:30Z")

</div>

> [@rlewis5](#):
>
> What is this

Looks like a stick to me.

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [August 4, 2022, 1:48pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/6 "2022-08-04T13:48:52Z")

</div>

Its a branch

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [August 4, 2022, 1:51pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/7 "2022-08-04T13:51:14Z")

</div>

Good morning Jeffrey. Yes my question was regarding the complete installation of this meter pan as it was buried in the wall. This is the first time anyone at my company has come across an installation like this. Have you seen an install like this before where you live? And would you have anything to say about it?

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [August 4, 2022, 2:00pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/8 "2022-08-04T14:00:23Z")

</div>

Looked like a ground wire to me.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [August 4, 2022, 2:05pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/9 "2022-08-04T14:05:25Z")

</div>

Not much to report until you open the cover. In general service entrance conductors need to be on the outside of the building.

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [August 4, 2022, 2:06pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/10 "2022-08-04T14:06:59Z")

</div>

Thanks Rob, I guess that was pretty much what I was asking about not being able to physically see the conductors

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 4, 2022, 2:18pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/11 "2022-08-04T14:18:12Z")

</div>

> [@rmeier2](#):
>
> In general service entrance conductors **need** to be on the outside of the building.

‘ **Need** ’ is such an ‘_opinionated_’ word… Are they “ **required** ” to be?  
For overhead systems, they are 50/50 exposed. On underground systems, they are always in conduit, and 50/50 exposed… but the conductors are still not visible without disassembly of some component.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [August 4, 2022, 2:27pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/12 "2022-08-04T14:27:22Z")

</div>

Need or required pick the word.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 4, 2022, 2:32pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/13 "2022-08-04T14:32:42Z")

</div>

> [@rmeier2](#):
>
> pick the word.

Use the word ‘need’ in a courtroom, and a sharp judge will make your life miserable!

In a previous life, my boss went to court, used that word, and the judge demanded that he explain who the hell he thought he was for telling a client “what HE needed”!!  
Yes… my boss lost the case by using that one word.

I have never forgot that example and have never used that word in any similar context.

Need is an opinion.  
Required is authoritative.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [August 4, 2022, 2:53pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/14 "2022-08-04T14:53:17Z")

</div>

> [@rmeier2](#):
>
> In general service entrance conductors need to be on the outside of the building.

Even when in conduit?

---

<div class="post-metadata">

**Author:** ![rkenney](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rkenney/32/405447_2.png) [@rkenney](https://forum.nachi.org/u/rkenney)\
**Post date:** [August 4, 2022, 3:09pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/15 "2022-08-04T15:09:53Z")

</div>

> [@rmeier2](#):
>
> In general service entrance conductors need to be on the outside of the building.

Is that “be on the outside of the building.” or **BE accessible** from the outside of the building? or both?

---

<div class="post-metadata">

**Author:** ![jfrederick](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfrederick/32/58314_2.png) [@jfrederick](https://forum.nachi.org/u/jfrederick)\
**Post date:** [August 4, 2022, 5:52pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/16 "2022-08-04T17:52:59Z")

</div>

So did you open the panel or not?

---

<div class="post-metadata">

**Author:** ![gwells](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gwells/32/417638_2.png) [@gwells](https://forum.nachi.org/u/gwells)\
**Post date:** [August 4, 2022, 7:10pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/17 "2022-08-04T19:10:38Z")

</div>

> [@rlewis5](#):
>
> Even when in conduit?

Service entrance conductors are usually on the exterior, even when they are in conduit.

---

<div class="post-metadata">

**Author:** ![mfellman](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mfellman/32/369692_2.png) [@mfellman](https://forum.nachi.org/u/mfellman)\
**Post date:** [August 4, 2022, 7:20pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/18 "2022-08-04T19:20:44Z")

</div>

If I made a comment I’d probably just say it’s an uncommon installation and replacement of the equipment will be difficult and involve removing some of the stone veneer. The power company or an electrician may be able to provide additional information.

---

<div class="post-metadata">

**Author:** ![lhenderson2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lhenderson2/32/58205_2.png) [@lhenderson2](https://forum.nachi.org/u/lhenderson2)\
**Post date:** [August 5, 2022, 1:19pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/19 "2022-08-05T13:19:36Z")

</div>

I don’t see anything in the photo worthy of any comment. I’ve haven’t seen boxes flush with the masonry either, but I’ve seen siding added that covers near the surface of the panel.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 5, 2022, 2:14pm UTC](https://forum.nachi.org/t/flush-mounted-electrical-meter/218501/20 "2022-08-05T14:14:06Z")

</div>

> [@rkenney](#):
>
> Is that “be on the outside of the building.” or **BE accessible** from the outside of the building?

And what about those instances where the SEC enters the home near the soffit when the meter is in the basement?