Four point electrical
Doing a four point inspection, and came across this in a subpanel. Any ideas whats happening and how to write it up? (if you would)
Short answer it needs to be ripped out and done over correctly. There appears to be two copper SEU cables, one terminating on the lugs the other on the 80 amp breaker. You cannot tell which is the feeder from the photo. That would require that the 80 amp breaker be turned off and then testing to see where the power is coming in.
The neutral is bonded because the feeder lacks the required 4th wire which is the EGC. There are no SE cable connectors on the cable and missing KO seals on the enclosure.
For a 4-point, simply check “unsafe wiring”, and in the comments “in panel xyz.”
Good point.
The panel itself needs some attention!!
I see fireworks in it’s future!!
Yeah on the hack work installation scale of 1-10 this is a solid 9. :open_mouth:
As Dominic said, just mark it as unsafe. Don’t treat a Four-Point inspection the same as a pre-purchase home inspection. The more information you put in a Four-Point report, the more likely it is to delay the homeowner being able to get insurance, not be able to get insurance at all, or not get the most favorable rate. The people who review Four-point reports are not necessarily technically knowledgeable. They are mainly looking at checkboxes.
This might be one of those instances where denial of insurance is justified, lol. That panel is a disaster.
If this hack did any other electrical work in this place they should kill the power.
Yeah, I think inspectors who perform 4-point inspections have to realize that their objective is not to get their client cheap insurance, or even insurance at all. Glossing over significant defects to please the client and insurance seller is not going to be substainable.
Yes, I agree with you in this instance, but inspectors tend to put too much information in Four-Point reports. They need to understand the Citizens requirements and expectations. Homeowners often pay too much for insurance or are denied insurance even though the home is 100% Citizens compliant because the home inspector didn’t understand how to properly complete the Four-Point report.
I have had hundreds of conversations with insurance reps, home inspectors, and lawyers about Wind Mit and Four-Point reports. My WindSurance website is usually the first site that appears in searches, so I get lots of calls from insurance companies, home inspectors, and lawyers. I take the time to listen to their grievances and answer their questions. All too often, home inspectors muddy the waters with excessive commentary. The insurance companies mainly make their decisions based on the checkboxes. Additional commentary almost always hurts the homeowner.
Getting insurance and getting the best rate is precisely what the Four point report is all about. Insurance eligibility and rates are determined by which boxes are checked.
A homeowner can’t just walk into Citizens and buy a policy. They first have to go to traditional insurance companies to get quotes. They can only get the mandated discounts from traditional insurers if the right boxes are checked. If they cannot get what the state (Citizens) deems to be a favorable rate, only then can they get insurance coverage through Citizens.
Citizens has been overwhelmed with applications the past couple years. They will kick back reports or deny coverage for anything they don’t understand. Extraneous information greatly increases the likelihood of the reviewer not understanding and simply denying the application.
Four-Point and Wind Mit reports serve a very specific purpose. Inspectors who put on their Mighty Mouse cape, thinking that they are going to save the World, can easily cause their client to be denied coverage. That can, and does, have devastating consequences. Thousands of people have lost their homes because they can’t get insurance. The Mighty Mouse inspectors are one of the reasons for people losing their homes.
It’s going to get worse before it gets better. The new Wind Mit report is mandatory beginning April 1st. The Wind Mit update is the first in 14 years. The requirements are tougher. The 2025 Four-Point report was updated in 2025 and was a relatively minor update compared to the 2018 update, but it also made the requirements tougher. The 2018 Four-Point report update put a significant additional burden on homeowners and home inspectors alike.
I’ve only ever had 4 points come back from Citizens. It happened twice. Both times they complained about the pictures of the roof. These days I just take the pictures of the roof, from the roof. They nitpick the hell out of everything. One area was in shadow, they thought it was wet. So I took it a new picture at a different time of day. The other I was just further away than they wanted. It was a manufactured on a serious grade and the eaves were about 14 feet up, so I got a bit lazy and took the pictures from the eaves. Needless to say, a week later, I was on that roof.
I just answer what’s on the form. Nothing more, nothing less. I know some folks have had to change toilet and vanity supply lines if they looked the slightest bit used.
Is this a training issue?
Non-compliant reports benefit insurers. That’s why many times they don’t kick them back. If a report is not fully Citizens compliant, the insurance company can charge more for coverage. They don’t have to give the mandatory discounts. They are banking on homeowners not being well educated about how the system works. It is a homeowner’s responsibility to ensure that the house is Citizens compliant. If a homeowner later realizes that the home isn’t fully Citizens compliant and complains to the insurance company, the insurance company can tell them that the house doesn’t qualify for the best possible rate and that they need to make the necessary modifications to the home.
If a report gets as far as Citizens, the buck stops there. If the house isn’t Citizens compliant, it doesn’t get kicked back to the inspector. The homeowner doesn’t get coverage. The homeowner could go back to the inspector, but to what avail? If, for example, the inspector used the 2018 Four-Point in 2020, the homeowner would have a legitimate grievance against the inspector. That’s a long series of Ifs. If the inspector used the current Four-Point, he’s in the clear. If he used an outdated report, he has some explaining to do.
I still talk with inspectors often who weren’t using the 2018 Four-Point long after 2018, and still aren’t. Inspectors will call me to this day to ask if I know that there was a a 2018 update. They sometimes only realize that they are out of compliance after being contacted by an angry homeowner who can’t get insurance or learned that they were paying too much.
There was a seven year interval between the two most recent Four-Point updates and 14 years between the two most recent Wind Mit updates. There’s really no good reason for an inspector not to stay current with the requirements. But, the real burden is on the homeowner, not the inspector.
I don’t know. A lack of training is probably at least a part of the problem. Complacency is probably also likely part of the problem.
I suspect that people having a busy life is also an important factor. Think about it. Who has time to keep up with all the laws, rules, and regulations that affect our everyday lives. Homebuyers probably put too much faith and confidence in RE agent and insurance agents.
I only know what I know about the Florida insurance standards and requirements because I’ve been in the Florida insurance inspection report business for more than 25 years. I don’t consider myself to be an expert, but I know from talking to Florida inspectors, that a lot, probably the majority, of home inspectors don’t know how the system works any more than their clients do.
The only thing I’ll say about that is in the handful of situations where I am aware of the follow-up, they made the home owner do some repairs. Several times it was supply piping, once it was water stains on the HVAC base and the home owner just replaced all of it. He even had an invoice from the repair that fixed the condensate line, but just got new anyway instead of fighting it.
I also know two insurance companies that will pretty much write any home within reason. They aren’t in The Villages where I do most of my inspections. Compared to the rest of Florida, The Villages generally has good installations. When I do a 4 point in Leesburg, Fruitland Park, Oxford, etc, some of the homes are complete garbage and yet they get insurance not from Citizens. My sister found an insurance company in Lake City that I use personally. I have given them out to people so many times, they should put me on the payroll. Same coverage as Tower Hill, State Farm, etc and often times 25% less expensive and less picky about condition. They don’t have a million lawsuits over not paying claims either, they just deal with “old Florida” instead of new(er) construction.