Furnace and Water Heater Correctly Vented?

Hello there! InterNACHI student in training here.

I inspected my masonry chimney to see specifically how the water heater and furnace exhaust into it. Here are my questions for the experts out there:

  1. I discovered is that both exhaust vents are connected to one fitting before going into the chimney flue. Are there any concerns with this?
  2. I peeked through the flue stop and took a picture upward and noticed there was what appeared to be a flexible duct connection that runs up the chimney flue. Is this considered a chimney liner? Is this acceptable?

For more context, it’s a gas water heater and category 1 mid efficiency furnace (both Rheem installed new in 2024).

Thank you for the help!

Short answer…Yes.

Among other things, I would be looking to make sure the smaller BTU appliance (typically the water heater) is connected “downstream” of the larger BTU appliance. Make sure you realize the difference between downstream and upstream as it relates to the flow of flue gasses.

Was it a metallic liner? That is typically required when exhausting a gas-burning appliance into a masonry chimney flue. Typically the liner will be stainless steel, but there are some other acceptable metals.

1 Like