# Furnace Vent Pipe Clearance

**URL:** <https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399>\
**Category:** Inspecting HVAC Systems\
**Created:** [November 28, 2022, 9:41pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399 "2022-11-28T21:41:12Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![ctemple1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ctemple1/32/242980_2.png) [@ctemple1](https://forum.nachi.org/u/ctemple1)\
**Post date:** [November 28, 2022, 9:41pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/1 "2022-11-28T21:41:12Z")

</div>

Anyone know if this is acceptable for a high efficiency furnace vent pipe clearance? (It is the lower house colored vent pipe)

 ![IMG_9573](https://global.discourse-cdn.com/internachi/original/4X/9/6/d/96db6f317a758351b5714f6dda8d5c21051ae230.jpeg)

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [November 28, 2022, 9:43pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/2 "2022-11-28T21:43:58Z")

</div>

What does the manufactures installation manual recommend?

---

<div class="post-metadata">

**Author:** ![dwigger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dwigger/32/58670_2.png) [@dwigger](https://forum.nachi.org/u/dwigger)\
**Post date:** [November 28, 2022, 10:10pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/3 "2022-11-28T22:10:44Z")

</div>

That is the only way to know the clearance needed.

---

<div class="post-metadata">

**Author:** ![ctemple1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ctemple1/32/242980_2.png) [@ctemple1](https://forum.nachi.org/u/ctemple1)\
**Post date:** [November 28, 2022, 10:11pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/4 "2022-11-28T22:11:54Z")

</div>

And if I cannot locate the manual online as its a 1999 American Standard, would writing it up as a potential safety hazard and referring to a qualified HVAC tech be appropriate?

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [November 28, 2022, 10:17pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/5 "2022-11-28T22:17:39Z")

</div>

Post the model number please. Sometimes we can dig up a manual.

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [November 28, 2022, 10:25pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/6 "2022-11-28T22:25:47Z")

</div>

Some info at link below:  
[https://inspectapedia.com/chimneys/Gas-Heater-Direct-Vent-Clearances.php](https://inspectapedia.com/chimneys/Gas-Heater-Direct-Vent-Clearances.php)

---

<div class="post-metadata">

**Author:** ![tglaze](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tglaze/32/362210_2.png) [@tglaze](https://forum.nachi.org/u/tglaze)\
**Post date:** [November 28, 2022, 10:29pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/7 "2022-11-28T22:29:10Z")

</div>

Looks like a Diversitech Hvent2. Here is a link to the installation manual.

> **[Diversitech HVent-2 Heater Accessories download instruction manual pdf](https://mans.io/item/diversitech/hvent-2)**
>
> Diversitech HVent-2 2 in PVC Horizontal Vent Kit for High Efficiency Fossil Fuel Appliances HVent 2301982912 download pdf instruction manual and user guide

If it is, seems that it should have a horizontal installation… 🤔

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [November 28, 2022, 11:43pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/8 "2022-11-28T23:43:27Z")

</div>

> [@tglaze](#):
>
> If it is, seems that it should have a horizontal installation…

It is a horizontal installation.

 ![guinness](https://global.discourse-cdn.com/internachi/original/4X/a/2/d/a2dd85d5e8920350af2dd4735b8102d5569d9dc4.jpeg)

---

<div class="post-metadata">

**Author:** ![lhenderson2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lhenderson2/32/58205_2.png) [@lhenderson2](https://forum.nachi.org/u/lhenderson2)\
**Post date:** [November 28, 2022, 11:51pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/9 "2022-11-28T23:51:36Z")

</div>

In general, clearances for flue terminations from condensing furnaces can be small, like 12", so that one looks too close to the soffitt. Flue gas temperatures are not a concern, but there could be excessive condensation on the soffit. So, without the manufacturer’s installation instructions, I would probably just comment that the termination appears closer than best practice to the soffit.

---

<div class="post-metadata">

**Author:** ![tglaze](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tglaze/32/362210_2.png) [@tglaze](https://forum.nachi.org/u/tglaze)\
**Post date:** [November 28, 2022, 11:56pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/10 "2022-11-28T23:56:57Z")

</div>

After Guinness and laying on your side looking at it.

Appears it could be installed either way, but I didn’t bother to check clearance. Something the OP needs to read and digest.

---

<div class="post-metadata">

**Author:** ![tlaplante](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tlaplante/32/184756_2.png) [@tlaplante](https://forum.nachi.org/u/tlaplante)\
**Post date:** [November 29, 2022, 4:22pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/11 "2022-11-29T16:22:47Z")

</div>

I would worry about moisture damage to the soffit also.

---

<div class="post-metadata">

**Author:** ![dandersen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dandersen/32/59398_2.png) [@dandersen](https://forum.nachi.org/u/dandersen)\
**Post date:** [November 29, 2022, 6:46pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/12 "2022-11-29T18:46:30Z")

</div>

> [@ctemple1](#):
>
> would writing it up as a potential safety hazard and referring to a qualified HVAC tech be appropriate?

Because you don’t know? I don’t think so.

What is the safety hazard your thinking about?

---

<div class="post-metadata">

**Author:** ![dandersen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dandersen/32/59398_2.png) [@dandersen](https://forum.nachi.org/u/dandersen)\
**Post date:** [November 29, 2022, 6:49pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/13 "2022-11-29T18:49:38Z")

</div>

The soffit is located outdoors. All the water from the roof cascades just over it.  
Moisture damage? How’s that?  
Do you see moisture damage in the pic?

Is that not a condensing furnace? What does it condense?

---

<div class="post-metadata">

**Author:** ![ctemple1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ctemple1/32/242980_2.png) [@ctemple1](https://forum.nachi.org/u/ctemple1)\
**Post date:** [November 29, 2022, 7:00pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/14 "2022-11-29T19:00:06Z")

</div>

Could the hazardous carbon monoxide gases vented by the furnace not potentially draft into the window or door next to it? Seems like a safety hazard to me.

---

<div class="post-metadata">

**Author:** ![tlaplante](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tlaplante/32/184756_2.png) [@tlaplante](https://forum.nachi.org/u/tlaplante)\
**Post date:** [November 29, 2022, 7:04pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/15 "2022-11-29T19:04:20Z")

</div>

I know the soffit is on the exterior!

Hot and cold create condensation which will cause moisture on the soffit. (Think winter). This also happens with a radon mitigation exhaust located under a soffit.

---

<div class="post-metadata">

**Author:** ![dandersen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dandersen/32/59398_2.png) [@dandersen](https://forum.nachi.org/u/dandersen)\
**Post date:** [November 29, 2022, 7:05pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/16 "2022-11-29T19:05:03Z")

</div>

Have you ever measured CO from a high efficiency furnace?  
Did you look up the distances required anywhere as suggested by others?  
If air is **Drafting** into the house in the winter with windows and doors closed, you have another real serious problem aside from this.

---

<div class="post-metadata">

**Author:** ![ctemple1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ctemple1/32/242980_2.png) [@ctemple1](https://forum.nachi.org/u/ctemple1)\
**Post date:** [November 29, 2022, 7:07pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/17 "2022-11-29T19:07:15Z")

</div>

Cool thanks

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [November 29, 2022, 7:08pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/18 "2022-11-29T19:08:16Z")

</div>

![image](https://global.discourse-cdn.com/internachi/original/4X/8/a/b/8abc49aa152f820e29d1ffe3476312a552565c4b.gif)

---

<div class="post-metadata">

**Author:** ![dandersen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dandersen/32/59398_2.png) [@dandersen](https://forum.nachi.org/u/dandersen)\
**Post date:** [November 29, 2022, 7:14pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/19 "2022-11-29T19:14:41Z")

</div>

Yes, that is correct.  
So based on the OP’s picture, what material is subject to damage?

I’m not saying condensation doesn’t happen, I want to know why it is a significant issue that home inspectors report on. We don’t just make stuff up to report. There has to be something actually there.

Again, is this not a condensing furnace? Just how much moisture is left in the combustion gas discharge vs. how much went down the drain.

Speaking of drains, will that drain discharging on the concrete cause an issue?

(6) General Exclusions  
(b) Home inspectors are not required to  
8. Predict future condition, including but not limited to failure of components

I looked again, and I still don’t see moisture damage in that pic.

---

<div class="post-metadata">

**Author:** ![jdeoliveira2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jdeoliveira2/32/57038_2.png) [@jdeoliveira2](https://forum.nachi.org/u/jdeoliveira2)\
**Post date:** [December 3, 2022, 2:13pm UTC](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399/20 "2022-12-03T14:13:26Z")

</div>

If the manufacturer specs are not followed, then it should be called out.  
Whether there is or is not any currently visible deficiencies is irrelevant.

[Next page](https://forum.nachi.org/t/furnace-vent-pipe-clearance/222399.md?page=2)