At an inspection the other day, I noticed a galvanized elbow installed between 2 straight runs of black iron gas pipe. Is galvanized allowed as a general rule? Does it depend on local codes?

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [March 24, 2012, 4:37pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/2 "2012-03-24T16:37:50Z")

</div>

The issue with gavanized pipe is the possibility of the coating flaking and then plugging valves and orifices.

If drip/dirt legs are present the risk is low but I would note the non standard use of the galvanized fitting in the gas piping system.

---

<div class="post-metadata">

**Author:** ![wwilson3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wwilson3/32/58197_2.png) [@wwilson3](https://forum.nachi.org/u/wwilson3)\
**Post date:** [March 24, 2012, 8:20pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/3 "2012-03-24T20:20:38Z")

</div>

Well for once we agree Micheal. I would note it, it should be changed . It does depend on were you are the do not even ask for drip legs here .

---

<div class="post-metadata">

**Author:** ![canderson5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/canderson5/32/1814_2.png) [@canderson5](https://forum.nachi.org/u/canderson5)\
**Post date:** [March 24, 2012, 9:49pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/4 "2012-03-24T21:49:06Z")

</div>

Our local utility doesn’t recommend it either(for the reasons Mike gave).

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [March 24, 2012, 10:58pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/5 "2012-03-24T22:58:18Z")

</div>

Allowed by the UPC…

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [March 24, 2012, 11:07pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/6 "2012-03-24T23:07:07Z")

</div>

I was told not allowed here however if running underground to say a garage would you rather use Black or Galv ?

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [March 25, 2012, 1:56am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/7 "2012-03-25T01:56:43Z")

</div>

> [@jpope](#):
>
> Allowed by the UPC…

And the IRC. It’s a misconception that galvanized is prohibited for natural gas.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [March 25, 2012, 2:42am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/8 "2012-03-25T02:42:51Z")

</div>

> [@jfunderburk](#):
>
> And the IRC. It’s a misconception that galvanized is prohibited for natural gas.

It varies at where you live.

[From Ameren Illinois](http://www.ameren.com/sites/aiu/source/ILConstServ/Documents/PreparingForNewGasService.pdf), my local utility provider:

Fuel Line:  
Customer Requirements:

…… The customer’s fuel line is the pipe that connects  
to the outlet of the gas meter set and extends  
through the wall into the house. The fuel line  
should enter the house or structure within three  
(3) feet of the gas meter set.

…… \*\*The customer fuel line from the meter through  
the house wall \*\*must be **a minimum of one (1) inch  
IPS schedule 40 black iron pipe.** For Corrugated  
Stainless Steel Tubing (CSST) installations, a  
termination fitting mounted on the outside house  
wall is acceptable for the transition from black  
iron pipe.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [March 25, 2012, 2:54am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/9 "2012-03-25T02:54:49Z")

</div>

> [@ccurrins](#):
>
> It varies at where you live.
> 
> [From Ameren Illinois](http://www.ameren.com/sites/aiu/source/ILConstServ/Documents/PreparingForNewGasService.pdf), my local utility provider:
> 
> Fuel Line:  
> Customer Requirements:
> 
> …… The customer’s fuel line is the pipe that connects  
> to the outlet of the gas meter set and extends  
> through the wall into the house. The fuel line  
> should enter the house or structure within three  
> (3) feet of the gas meter set.
> 
> …… \*\*The customer fuel line from the meter through  
> the house wall \*\*must be **a minimum of one (1) inch  
> IPS schedule 40 black iron pipe.** For Corrugated  
> Stainless Steel Tubing (CSST) installations, a  
> termination fitting mounted on the outside house  
> wall is acceptable for the transition from black  
> iron pipe.

I said IRC. Local codes vary.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [March 25, 2012, 2:56am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/10 "2012-03-25T02:56:15Z")

</div>

2009 IRC G2414.4.2 (403.4.2) Steel. Steel and wrought-iron pipe shall  
be at least of standard weight (Schedule 40) and shall comply  
with one of the following:

1. ASME B 36.10, 10M;
2. ASTM A 53/A 53M; or
3. ASTM A 106.  
Commentary: Steel pipe must be Schedule 40 or heavier, must comply  
with one of the listed standards and can be black  
iron or galvanized. Contrary to popular belief, natural  
gas does not adversely react with the zinc coating on  
galvanized pipe."

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [March 25, 2012, 2:57am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/11 "2012-03-25T02:57:35Z")

</div>

> [@jfunderburk](#):
>
> I said IRC. Local codes vary.

You also said this

“It’s a misconception that galvanized is prohibited for natural gas.”

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [March 25, 2012, 3:00am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/12 "2012-03-25T03:00:11Z")

</div>

> [@ccurrins](#):
>
> It varies at where you live.
> 
> [From Ameren Illinois](http://www.ameren.com/sites/aiu/source/ILConstServ/Documents/PreparingForNewGasService.pdf), my local utility provider:
> 
> Fuel Line:  
> Customer Requirements:
> 
> …… The customer’s fuel line is the pipe that connects  
> to the outlet of the gas meter set and extends  
> through the wall into the house. The fuel line  
> should enter the house or structure within three  
> (3) feet of the gas meter set.
> 
> …… \*\*The customer fuel line from the meter through  
> the house wall \*\*must be **a minimum of one (1) inch  
> IPS schedule 40 black iron pipe.** For Corrugated  
> Stainless Steel Tubing (CSST) installations, a  
> termination fitting mounted on the outside house  
> wall is acceptable for the transition from black  
> iron pipe.

Is galvanized prohibited anywhere else by your utility? Or just the fuel line?

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [March 25, 2012, 3:08am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/13 "2012-03-25T03:08:02Z")

</div>

> [@jfunderburk](#):
>
> Is galvanized prohibited anywhere else by your utility? Or just the fuel line?

It’s not prohibited with water lines, if that’s what you mean.

Not sure if it still is with All of the fuel line. It used to be, at least by local AHJ.

But I believe the fuel mixture has changed, so maybe have the restrictions.

I rarely see galvanized on fuel lines, unless it’s a nipple, elbow, etc.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [March 25, 2012, 3:13am UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/14 "2012-03-25T03:13:10Z")

</div>

Here’s an example from a few days ago.

 ![HPIM6100.jpg](https://global.discourse-cdn.com/internachi/original/3X/1/7/178b96c672ed18cda890917ec6172ae80ee7d28b.jpeg)

---

<div class="post-metadata">

**Author:** ![paul\_dimaggio](https://avatars.discourse-cdn.com/v4/letter/p/a3d4f5/32.png) [@paul\_dimaggio](https://forum.nachi.org/u/paul_dimaggio)\
**Post date:** [September 8, 2014, 6:24pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/15 "2014-09-08T18:24:11Z")

</div>

As Joe Funderburk mentioned (which is the same requirement as 2013 California Plumbing Code, Fuel Gas Piping 1208.5.2.2), galvanized pipe may be used for natural gas piping.

2009 IRC G2414.4.2 (403.4.2) Steel. Steel and wrought-iron pipe shall  
be at least of standard weight (Schedule 40) and **shall comply  
with one of the following**: 1. ASME B 36.10, 10M;  
2. **ASTM A 53** /A 53M; or  
3. ASTM A 106.ASTM A53 specification. “Standard Specification for  
Pipe, Steel, Black and Hot-Dipped, **Zinc-Coated** , Welded and  
Seamless”, section 17, discusses Galvanized Pipe requirements:

1. Galvanized Pipe  
17.1 Galvanized pipe ordered under this specification shall  
be coated with zinc inside and outside by the hot-dip process.  
The zinc used for the coating shall be any grade of zinc  
conforming to Specification B6. …

---

<div class="post-metadata">

**Author:** ![eschmidt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/eschmidt/32/89375_2.png) [@eschmidt](https://forum.nachi.org/u/eschmidt)\
**Post date:** [September 8, 2014, 10:00pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/16 "2014-09-08T22:00:07Z")

</div>

> [@belliott](#):
>
> I was told not allowed here however if running underground to say a garage would you rather use Black or Galv ?

There is a plastic coated pipe for underground (not CCST, a black pipe with a yellow coating) or nowadays they use all plastic line, but it has to be plastic welded by a certified welder, not a home handyman job.

---

<div class="post-metadata">

**Author:** ![dspence3](https://avatars.discourse-cdn.com/v4/letter/d/ed655f/32.png) [@dspence3](https://forum.nachi.org/u/dspence3)\
**Post date:** [September 26, 2017, 4:23pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/17 "2017-09-26T16:23:06Z")

</div>

I thought that the whole deal with black iron was that they were seamless whereas galvanized have seams.

---

<div class="post-metadata">

**Author:** ![mrichards11](https://avatars.discourse-cdn.com/v4/letter/m/e9bcb4/32.png) [@mrichards11](https://forum.nachi.org/u/mrichards11)\
**Post date:** [October 13, 2020, 7:04pm UTC](https://forum.nachi.org/t/galvanized-natural-gas-pipe/67874/18 "2020-10-13T19:04:52Z")

</div>

It says a minimum, galvanized is over a minimum