Inspected a house today that had a flex gas line connected between two metal pipes in crawl space area. Stop valve was also present in crawl space. This was in the gas line supplying the range. Didn’t seem right to me. How would you right that up?

---

<div class="post-metadata">

**Author:** ![pkelley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pkelley/32/1635_2.png) [@pkelley](https://forum.nachi.org/u/pkelley)\
**Post date:** [February 16, 2006, 2:31pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/2 "2006-02-16T14:31:48Z")

</div>

Gas flex lines cannot pass through walls and or flooring. The Shut off valve needs to be with in reach of the appliance it is servicing.Recommending a qualified contractor repair

Was there a drip leg present?

---

<div class="post-metadata">

**Author:** ![Richard\_Seay](https://avatars.discourse-cdn.com/v4/letter/r/e9bcb4/32.png) [@Richard\_Seay](https://forum.nachi.org/u/Richard_Seay)\
**Post date:** [February 16, 2006, 11:32pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/3 "2006-02-16T23:32:46Z")

</div>

Thanks, you asked - Was there a drip leg present? No, I very seldom see them here. The flex line is connecting two gas pipes in the crawlspace area. It does not pass through a wall or floor. Didnt look right to me.  
Richard

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [February 17, 2006, 12:19am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/4 "2006-02-17T00:19:57Z")

</div>

\*Flex gas line? \*That doesn’t really tell us enough to give a proper response.

CSST is allowed in any location that other gas piping is allowed. If the _flex gas line_ you were referring to was in fact, CSST, there may be no problem with that application. Also, CSST **can** pass through walls floors etc.

If the _flex gas line_ was actually an appliance connector, it was probably improper. Appliance connectors are for connecting **appliances** , not piping.

---

<div class="post-metadata">

**Author:** ![Richard\_Seay](https://avatars.discourse-cdn.com/v4/letter/r/e9bcb4/32.png) [@Richard\_Seay](https://forum.nachi.org/u/Richard_Seay)\
**Post date:** [February 17, 2006, 3:56am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/5 "2006-02-17T03:56:42Z")

</div>

My mistake, the _flex gas line_ was actually an appliance connector. Thanks

---

<div class="post-metadata">

**Author:** ![JohnH515](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/johnh515/32/579_2.png) [@JohnH515](https://forum.nachi.org/u/JohnH515)\
**Post date:** [February 17, 2006, 3:57am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/6 "2006-02-17T03:57:11Z")

</div>

Jeff, is there a visable difference between CSST and appliance connector line?

John

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [February 17, 2006, 4:54am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/7 "2006-02-17T04:54:25Z")

</div>

Appliance connectors are typically smaller in diameter and three feet long. CSST can be quite long and sized as you would expect for building supply.

[http://www.gastite.com/flash.php](http://www.gastite.com/flash.php)

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [February 19, 2006, 3:41pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/8 "2006-02-19T15:41:51Z")

</div>

Here are some pictures of a fairly common set up. The CSST is run through the wall to rigid pipe, and then to an appliance connector.

The rigid piping wasn’t really necessary in this case, but there’s nothing wrong with the set up.

---

<div class="post-metadata">

**Author:** ![pbolliger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pbolliger/32/1150_2.png) [@pbolliger](https://forum.nachi.org/u/pbolliger)\
**Post date:** [February 20, 2006, 7:33pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/9 "2006-02-20T19:33:05Z")

</div>

Here is a picture of how NOT to install the flex gas connector.

This was in a basement, passing up through a wall up to a kitchen range.

The valve has to be in the same room preferably next to the appliance. Here is the rub … Most shut off valves for kitchen stoves are behind the appliance… Hmmm

 ![100_2254.JPG](https://global.discourse-cdn.com/internachi/original/3X/5/7/57b1cc1af9dacb4fcb9d6984fa0858d7e8c75b12.jpeg)

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [February 20, 2006, 11:01pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/10 "2006-02-20T23:01:17Z")

</div>

> [@pbolliger](#):
>
> The valve has to be in the same room preferably next to the appliance. Here is the rub … Most shut off valves for kitchen stoves are behind the appliance… Hmmm

Also, appliance connectors are absolutely **not** allowed to pass through walls, floors, etc.

---

<div class="post-metadata">

**Author:** ![jcundiff](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jcundiff/32/1370_2.png) [@jcundiff](https://forum.nachi.org/u/jcundiff)\
**Post date:** [February 21, 2006, 2:27pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/11 "2006-02-21T14:27:03Z")

</div>

AGA website has alot of info on csst as well as appliance connectors which are a listed assembly. Also check the Fule Gas Code or IRC fule gas section.

---

<div class="post-metadata">

**Author:** ![hmiller](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/hmiller/32/57038_2.png) [@hmiller](https://forum.nachi.org/u/hmiller)\
**Post date:** [August 10, 2008, 4:27pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/12 "2008-08-10T16:27:54Z")

</div>

> [@pbolliger](#):
>
> The valve has to be in the same room preferably next to the appliance. Here is the rub … Most shut off valves for kitchen stoves are behind the appliance… Hmmm

However you can access gas range valve by removing the bottom drawer (in most cases)

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 10, 2008, 5:26pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/13 "2008-08-10T17:26:12Z")

</div>

> [@jpope](#):
>
> Also, appliance connectors are absolutely **not** allowed to pass through walls, floors, etc.

Nor through the cabinet of the appliance. About 1/2 of every furnace I see has the appliance connector going into the cabinet itself.

---

<div class="post-metadata">

**Author:** ![jgilleland](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgilleland/32/1326_2.png) [@jgilleland](https://forum.nachi.org/u/jgilleland)\
**Post date:** [August 12, 2008, 3:32am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/14 "2008-08-12T03:32:53Z")

</div>

Jeff what happened to the pictures in #8?

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 12, 2008, 4:07am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/15 "2008-08-12T04:07:14Z")

</div>

I have no idea. Maybe they expired after two and a half years. . .

---

<div class="post-metadata">

**Author:** ![rbritton](https://avatars.discourse-cdn.com/v4/letter/r/76d3ee/32.png) [@rbritton](https://forum.nachi.org/u/rbritton)\
**Post date:** [August 12, 2008, 5:42am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/16 "2008-08-12T05:42:07Z")

</div>

Jeff,  
Let me ask you about a inspection I did a couple of weeks ago. The flex gas line was run directly in front of attic stairs. If you crawled up attic stairs the  
the first thing that you would grab would be the flex

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 12, 2008, 3:20pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/17 "2008-08-12T15:20:00Z")

</div>

CSST can be run in the same manner as steel pipe. There are certain requirements for protection where CSST is run through walls or floors.

As long as it was properly supported, it can be run directly in front of an access point.

---

<div class="post-metadata">

**Author:** ![msylvester](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/msylvester/32/252729_2.png) [@msylvester](https://forum.nachi.org/u/msylvester)\
**Post date:** [August 12, 2008, 11:22pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/18 "2008-08-12T23:22:05Z")

</div>

Here’s an example.

![IMG.jpg](https://global.discourse-cdn.com/internachi/original/3X/b/9/b9caf2ea3d651d897cceea867ed9def480c23ac7.jpeg)

![IMG_9286.jpg](https://global.discourse-cdn.com/internachi/original/3X/6/1/611f486fa4cf654aa97bea6c9b15dfad40dff6f9.jpeg)

---

<div class="post-metadata">

**Author:** ![bkelly2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bkelly2/32/58257_2.png) [@bkelly2](https://forum.nachi.org/u/bkelly2)\
**Post date:** [August 12, 2008, 11:51pm UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/19 "2008-08-12T23:51:49Z")

</div>

> [@rbritton](#):
>
> Jeff,  
> Let me ask you about a inspection I did a couple of weeks ago. The flex gas line was run directly in front of attic stairs. If you crawled up attic stairs the  
> the first thing that you would grab would be the flex

I would reccomend that the tubing be protected from physical damage if you think someone might step on it.

[http://www.mtlfab.com/media/L1627.pdf](http://www.mtlfab.com/media/L1627.pdf)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [August 13, 2008, 12:12am UTC](https://forum.nachi.org/t/gas-flex-line-in-crawl-space/1536/20 "2008-08-13T00:12:24Z")

</div>

> [@bkelly2](#):
>
> I would reccomend that the tubing be protected from physical damage if you think someone might step on it.
> 
> [http://www.mtlfab.com/media/L1627.pdf](http://www.mtlfab.com/media/L1627.pdf)

…or use it for a grab bar/handrail.