can you have the bathroom GFCI on the same circuit as the garage and exterior outlets. The home was built about 9 years ago.

---

<div class="post-metadata">

**Author:** ![rromoser](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rromoser/32/1832_2.png) [@rromoser](https://forum.nachi.org/u/rromoser)\
**Post date:** [March 23, 2007, 8:04pm UTC](https://forum.nachi.org/t/gfci/14474/2 "2007-03-23T20:04:36Z")

</div>

Yes, NEC 2002 states they need GFCI protection, it doesn’t state anything on circuiting. It appears in 2005 I believe. I’ve seen Million dollar homes with all GFCI receptacles except kitchens on the same circuit. They had 4-5 bathrooms. Mom and daughter can’t dry their hair at the same time:mad: Might be worth noting if just for that reason.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [March 23, 2007, 8:19pm UTC](https://forum.nachi.org/t/gfci/14474/3 "2007-03-23T20:19:17Z")

</div>

The requirement for a dedicated 20a circuit in the bathroom showed up in the 96 code.