why is safety glazing not required at window above landing at stairs but it is required at the bottom?

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 24, 2024, 9:08pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/2 "2024-03-24T21:08:23Z")

</div>

Welcome back to the forum, Ross.

 ![Screenshot 2024-03-24 at 5.08.03 PM](https://global.discourse-cdn.com/internachi/original/4X/3/b/e/3be67f65a4f061cbeddad0d6df32c6d5d3e2a09c.jpeg)

---

<div class="post-metadata">

**Author:** ![rlorimer](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlorimer/32/295448_2.png) [@rlorimer](https://forum.nachi.org/u/rlorimer)\
**Post date:** [March 24, 2024, 9:17pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/3 "2024-03-24T21:17:30Z")

</div>

Is the top of the stairs not considered a landing? Thus as long as it’s greater than 18” from the floor then safety glazing is not required.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 24, 2024, 9:22pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/4 "2024-03-24T21:22:19Z")

</div>

> [@rlorimer](#):
>
> Is the top of the stairs not considered a landing? Thus as long as it’s greater than 18” from the floor then safety glazing is not required

Do you have a picture to share?

---

<div class="post-metadata">

**Author:** ![rlorimer](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlorimer/32/295448_2.png) [@rlorimer](https://forum.nachi.org/u/rlorimer)\
**Post date:** [March 24, 2024, 9:26pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/5 "2024-03-24T21:26:06Z")

</div>

See diagram attached

 ![IMG_0420](https://global.discourse-cdn.com/internachi/original/4X/1/a/2/1a2e4a14e20e398c2c7ca625c66b780070865f85.jpeg)

---

<div class="post-metadata">

**Author:** ![dwigger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dwigger/32/58670_2.png) [@dwigger](https://forum.nachi.org/u/dwigger)\
**Post date:** [March 24, 2024, 9:29pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/6 "2024-03-24T21:29:12Z")

</div>

> [@rlorimer](#):
>
> Thus as long as it’s greater than 18” from the floor then safety glazing is not required

If the top of the stairs is \>6’ above grade, the window must be 24" from floor.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 24, 2024, 9:36pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/7 "2024-03-24T21:36:51Z")

</div>

> [@rlorimer](#):
>
> Is the top of the stairs not considered a landing?

Yeah, the wording is somewhat confusing maybe…

Aside from what David posted, landings **between flights of stairs** …shall be considered a hazardous location.

 ![Screenshot 2024-03-24 at 5.30.15 PM](https://global.discourse-cdn.com/internachi/original/4X/e/5/8/e589c1d0edac3b6fcfc54b547e1844868c9b787b.jpeg)

---

<div class="post-metadata">

**Author:** ![rkenney](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rkenney/32/405447_2.png) [@rkenney](https://forum.nachi.org/u/rkenney)\
**Post date:** [March 24, 2024, 11:10pm UTC](https://forum.nachi.org/t/glazing-at-stairs/240527/8 "2024-03-24T23:10:05Z")

</div>

Simply put your illustration is wrong. Larry posted the correct code. The important words are: “adjacent walking surface.” That includes landings at the top and bottom of stairs as well as between flights of stairs.

So, why did you buy a book of illustrations created by an ASHI member?

From their page, " Our home inspection illustrations library includes over 400 illustrations. It also includes a PDF copy of [_Everybody’s Building Code_](https://dreamhomeconsultants.com/everybodys-building-code/). **Bruce A. Barker, a former chair of the ASHI Standards Committee and former ASHI President,** developed this library."

Be interested to see what other errors it includes.