Needs some help on the ground for the main panel, the ground is going into the white box to the bottom of the photo. Are bedrooms in new homes required to be 20 amp?
ccurrins
(Christopher Currins, CMI)
November 16, 2010, 4:17am
2
The ground (GEC) is in the gray PVC at right. The ground wire at white box is for something else, telephone, security, etc. The bedrooms circuits have been required to be protected by arc fault breakers since 2002. I do not believe there is a 20 amp requirement, not sure. What NEC code is being used where this home is located.
rmeier2
(Robert Meier)
November 16, 2010, 9:57am
3
That white box is called an Intersystem Bonding Terminal and is now required (2008 NEC) for the bonding of communication systems. You will usually see it right below the meter enclosure attached to a grounding electrode conductor or as in this case run as a separate conductor run out of the meter enclosure.
There is no NEC requirement for using 20 amp circuits for a bedroom in a dwelling.
250.94 Bonding for Other Systems.
An intersystem bonding termination for connecting intersystem bonding and grounding conductors required for other systems shall be provided external to enclosures at the service equipment and at the disconnecting means for any additional buildings or structures. The intersystem bonding termination shall be accessible for connection and inspection. The intersystem bonding termination shall have the capacity for connection of not less than three intersystem bonding conductors. The intersystem bonding termination device shall not interfere with opening a service or metering equipment enclosure. The intersystem bonding termination shall be one of the following:
(1) A set of terminals securely mounted to the meter enclosure and electrically connected to the meter enclosure. The terminals shall be listed as grounding and bonding equipment.
(2) A bonding bar near the service equipment enclosure, meter enclosure, or raceway for service conductors. The bonding bar shall be connected with a minimum 6 AWG copper conductor to an equipment grounding conductor(s) in the service equipment enclosure, meter enclosure, or exposed nonflexible metallic raceway.
(3) A bonding bar near the grounding electrode conductor. The bonding bar shall be connected to the grounding electrode conductor with a minimum 6 AWG copper conductor.
Exception: In existing buildings or structures where any of the intersystem bonding and grounding conductors required by 770.93, 800.100(B), 810.21(F), 820.100(B), 830.100(B) exist, installation of the intersystem bonding termination is not required. An accessible means external to enclosures for connecting intersystem bonding and grounding electrode conductors shall be permitted at the service equipment and at the disconnecting means for any additional buildings or structures by at least one of the following means:
(1) Exposed nonflexible metallic raceways
(2) An exposed grounding electrode conductor
(3) Approved means for the external connection of a copper or other corrosion-resistant bonding or grounding conductor to the grounded raceway or equipment
FPN No. 1: A 6 AWG copper conductor with one end bonded to the grounded nonflexible metallic raceway or equipment and with 150 mm (6 in.) or more of the other end made accessible on the outside wall is an example of the approved means covered in 250.94, Exception item (3).
FPN No. 2: See 800.100, 810.21, and 820.100 for bonding and grounding requirements for communications circuits, radio and television equipment, and CATV circuits.
dmacy
(David C. Macy, CMI)
November 16, 2010, 9:08pm
4
Here is a link.
I watched or read a post recently on this but I can not remember where.
Seems like a good idea.